Thread: Rheem 04EAUSR. Igniter doesn't glow.

  1. #1
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default Rheem 04EAUSR. Igniter doesn't glow.

    I have a Rheem 04EAUSR and when I turn it on and set it to call for heat, the unit starts up and blows air, but it's not hot. When I went to the garage to look at it, the flame wasn't on. I went through the quick check guide on under the panel and after following the steps I've found out that my igniter doesn't glow at all. What is the next step I should take to diagnose the problem?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    That could be a symptom of the control board, or the ignitor, or a wiring failure (assuming it had worked). Look for obvious things like a loose or corroded, or broken wire to the ignitor. Watch the thing through a full cycle to verify it never gets hot. It doesn't stay hot once the system determines it has actually lit the burner. On some, the ignitor is also the flame detector. If it does get hot, when the gas should then come on, if it doesn't detect that it actually got hot because of the flame, rather than applying electricity to make it glow, it will shut the gas off. So, if it does come on, it could be the gas valve is not opening. This again, could be the valve or the controller. If you are comfortable with a meter, you can verify that the parts are getting their proper voltages at the proper time. Also, if this is a closed combustion device, the fan may not have come on and the vacuum switch interlock may be preventing it from going through the proper cycle since it is sensing some problem with the flue.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    I ended up replacing the ignitor based on what a local HVAC guy said. It still didn't glow, but when I turned it on this time, the gas started going and didn't shut off. I ended up turning off and unplugging the unit, because the whole house started to smell like gas.

  4. #4
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,645

    Default

    Quote Originally Posted by Rickcusaf View Post
    I ended up replacing the ignitor based on what a local HVAC guy said. It still didn't glow, but when I turned it on this time, the gas started going and didn't shut off. I ended up turning off and unplugging the unit, because the whole house started to smell like gas.
    That is not good at All, I would check the CAD eye.

    Gas is no playing mater...
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #5
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    Where would that be located so I can check it? I did some searching and only found stuff about Oil burners?

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    Different makes use different methods to determine if the flame has actually ignited. Sometimes it's a little probe, sometimes it's the dual purpose ignitor/sensor, sometimes it's a photo sensor. Somewhere in your documentation it will have a theory of operation, and describe what you have. Then, either in that manual or on the block diagram often on an inside panel, it will show the interlock, and operational wiring diagram. Unless you deal with wiring diagrams often, they can be confusing, but if you take your time, you can usually figure it out. Whatever your system uses, it must either be in the flame or be able to see the flame.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    Would that cause the hot surface ignitor to not glow though? Right now the ignitor is still not glowing.

  8. #8
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,645

    Default

    Quote Originally Posted by Rickcusaf View Post
    Would that cause the hot surface ignitor to not glow though? Right now the ignitor is still not glowing.
    Are You able to read an error code, Looking at the LEDs on the control board ?
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  9. #9
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Quote Originally Posted by Rickcusaf View Post
    I ended up replacing the ignitor based on what a local HVAC guy said. It still didn't glow, but when I turned it on this time, the gas started going and didn't shut off. I ended up turning off and unplugging the unit, because the whole house started to smell like gas.
    You are definitely going to spring for the HVAC guy, or up your homeowners insurance and take a long vacation.

  10. #10
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,645

    Default

    Quote Originally Posted by ballvalve View Post
    You are definitely going to spring for the HVAC guy.
    That may not be a bad Idea.

    After looking at the service manual for that unit, It looks like it could be a Air Flow sensor, Shutting it down.

    If the old ignitor was bad, and broke and shorted to ground, It may have blown the fuse.

    The three LEDs on the control board should help to troubleshoot the simple problems.

    A service tech may be worth the cost, For safety reasons.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  11. #11
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    a bad air flow sensor will NEVER let gas flow. Just changed a few. Probably the main board. VERY rare for gas to flow with a igniter hot and the exhaust inducer running. Only chance would be a out of alignment hot igniter, and bad flame sensor.

  12. #12
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,645

    Default

    Quote Originally Posted by ballvalve View Post
    a bad air flow sensor will NEVER let gas flow. Just changed a few. Probably the main board. VERY rare for gas to flow with a igniter hot and the exhaust inducer running. Only chance would be a out of alignment hot igniter, and bad flame sensor.
    That is True, The gas valve should never open.

    Not sure why there would be a gas smell. That made no sense.

    If the air does not flow the igniter SHOULD never come on either, according to the manual.

    Could be the control board is bad.
    Last edited by DonL; 12-19-2011 at 02:57 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #13
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    Sorry for the delay in replying. The main board has three lights. The Power and Ok lights are on, but the Flame light isn't. Nothing flashes nor do I see any noticeable warning. I'd love to spring for the HVAC guy, but my wife lost her job early December and money is super tight right now. It sucks, because it's starting to dip into the 20s where I live.

  14. #14
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Hate to sound like the grim reaper, but money will be tighter if you have to pay for a funeral. This is just not the type of problem that can be fixed by poking around and changing parts on a whim. If filling the house with a gas smell did not scare the crap out of you, well...I see a new reality show in your future.

  15. #15
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    It did, but there is no money for an HVAC guy right now. They charge $75 an hour here with a minimum of one hour charged. It hasn't smelled like gas since though. When it happened the first time it was right after I had changed the ignitor and the slow-blow fuse. How much are the control boards and where would I be able to find one if it does happen to be that?

Similar Threads

  1. Takagi tk3 flash igniter woes
    By HANK WHITE in forum Tankless Water Heater Forum
    Replies: 1
    Last Post: 03-10-2010, 01:58 PM
  2. Ruud vs Rheem
    By S30trbo in forum Water Heater Forum, Tanks
    Replies: 3
    Last Post: 01-27-2010, 08:04 AM
  3. RIP 21 y.o. Rheem. What's next?
    By pmoe in forum Water Heater Forum, Tanks
    Replies: 9
    Last Post: 09-16-2009, 01:33 PM
  4. Rheem
    By cwhyu2 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 12-11-2007, 07:23 PM
  5. Rheem Richmond Toilet
    By opalomarez in forum Toilet Forum discussions
    Replies: 2
    Last Post: 12-04-2006, 10:37 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •