    Default Flow control valve stuck closed??

    It seems most times flo control valves get stuck open and then you have the zone too hot due to runaway heat. I am wondering if mine is stuck closed cause the radiant heat in that zone never reaches temperature (70 degrees) and thus the cirulator is always running. The other 4 zones upstairs with baseboards are working fine, pressure is at about 17lb. and boiler temp is at 180 degrees.

    It seems that the hot water pipe going into this flow control valve is hot but the pipe out of it is not. I am very worried to try to open it manually since the valve is original 1961? If in fact its stuck closed, if I try to bleed this zone, would nothing come out of the purge valve located on the return since the flow control valve is closed?? Any input is greatly appreciated!!

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Most zone valves have a manual override...it should be safe to open it. The valve could be open, and not circulating in that loop because of an air lock, though, and purging might solve the problem...the valve could be okay. But, I think I'd try to manually open it to see if that does anything before I tried to purge it.

    Depending on the brand and type, it might just be the motor head, which is replaceable without changing the valve.

    To purge, the valve would have to be open, either manually, or, it's possible it is already open if the thermostat is calling for heat, but not flowing because of an airlock. Some have an indicator that shows whether it is closed or open.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member greekguy7's Avatar
    Join Date
    Jul 2005
    Location
    Illinois
    Posts
    29

    Default

    Actually, I think you are referring to a zone valve... not a flow control valve? I dont have any zone valves, but instead have a dedicated circulator pump and flow control valve for each zone.

    http://www.pexsupply.com/Bell-Gosset...trol-5595000-p

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Take a hammer and give it a whack...see what happens.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,936

    Default

    You got no heat because that zone has air in it and it ain't circulating. Get rid of the air and Presto....problem solved
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    DIY Junior Member greekguy7's Avatar
    Join Date
    Jul 2005
    Location
    Illinois
    Posts
    29

    Default

    If it was truly stuck closed or nearly closed, wouldn't any attempt to bleed the zone cause very little to come out of the purge valve since the water wouldn't go thru the flo control valve?

Similar Threads

  1. Flow control Ball valve, hot water baseboard
    By Vinijm in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 04-23-2009, 02:27 PM
  2. Mixette Shower Control- low flow
    By shall in forum Shower & bathtub Forum & Blog
    Replies: 5
    Last Post: 07-19-2007, 02:58 PM
  3. Shower Control Knob Stuck
    By John24689 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-20-2006, 06:00 AM
  4. Shower Control Knob Stuck
    By John24689 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-19-2006, 02:50 PM
  5. Control flow and temp?
    By Bex in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 12-09-2005, 04:09 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •