Thread: Lochinvar Solution Temperature Settings

  1. #1
    DIY Junior Member rpowli's Avatar
    Join Date
    Dec 2011
    Location
    Michigan
    Posts
    1

    Default Lochinvar Solution Temperature Settings

    We have a Lochinvar Solution running three zones with the following settings
    Set Point = 180
    Differential =15
    High-Fire Offset =7

    When the boiler first starts up, it goes on Lo-Fire for 120 seconds, then Hi-Fire until it gets to around 173 and then goes to Low-Fire. So far so good.

    If only one or two zones are calling for heat, Lo-Fire will continue on until 180 is reached, then burners shut off until temperature drops to 160-165 and the the burner comes back on at Lo-Fire (not High-Fire even though it is well below the 7 degree High Fire Offset setting) ... maybe no big deal since this reduces short cycling. This continues until the zone(s) shut down and then system shuts down.

    If all three zones call for heat at the same time (e.g. first thing in the morning) Lo-Fire again kicks in at 173, but Lo-Fire is unable to increase the temperature and in fact the water temperature drifts down until it stabilizes around 160-165 degrees. It stays this way for quite awhile until one or two of the zones shuts down, then Lo-Fire will eventually increase the temperature to 180. It then proceeds as outlined above.

    Just wondering why the system will never turn on High-Fire during a cycle once it goes to Lo-Fire. I would think that once the temperature drops below the High-Fire Offset value, High-Fire would come back on.

    Does anyone know how it is supposed to work?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    Do you know what the return water temperatures are?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member tray's Avatar
    Join Date
    Dec 2011
    Location
    west henrietta, ny
    Posts
    10

    Default

    Is your boiler a high eff with an outdoor sensor. With some boilers, water temp and outdoor temp figure into where the boiler fires and if high is even need for efficiency. For the boiler, it maybe more eff to run on lo fire for 10min than on hi for 5-8min

Similar Threads

  1. Lochinvar Water Heaters
    By feltdog in forum Water Heater Forum, Tanks
    Replies: 17
    Last Post: 12-07-2011, 04:12 AM
  2. Temperature Settings on Moen Single Handle Tub/Shower Faucet
    By shelleyevans in forum Shower & bathtub Forum & Blog
    Replies: 12
    Last Post: 11-28-2011, 05:20 PM
  3. New Lochinvar Knight install
    By DEA in forum Boiler Forum
    Replies: 3
    Last Post: 10-13-2011, 11:59 AM
  4. water boiler temperature settings and circulator
    By jsherk in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 12-10-2009, 01:03 PM
  5. Recommended oil furnace temperature settings?
    By spicyjeff in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 05-02-2008, 05:19 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •