    Default Whole house filter with jet pump and pressure tank

    Hello everyone,

    I need a little advice. I apologize if this subject has already been addressed. I have 1.0HP Myers jet pump and I believe a 14 gallon pressure tank. My pressure switch was originally 40/60. Anyway, about 7 months ago I installed a whole house filter (AP907) after the pressure tank. I think it is starting to clog up because I can no longer have two draws on the system at the same time. If I am taking a shower, no one can run the kitchen sink. I initially tried increasing pressure from the switch, its set at about 45/63 now but still the same problem. I can replace the filter but its supposed to last a year. I am thinking of raising the pressure switch again to 50/65 but wonder what other options I may have.

    Does anybody have any advice to increase my pressure? thanks in advance.

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    Change the filter and/or install two in parallel.

  3. #3
    DIY Senior Member Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,174

    Default

    I hate whole house filters but if you must, you must also maintain them. Change the element and presto......life is better, for awhile anyway
    No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!

  4. #4
    DIY Junior Member mbinetti's Avatar
    Join Date
    Nov 2011
    Location
    BDA, NJ
    Posts
    2

    Default

    I know what you mean about the WHF, but it is necessary. I rather not change the filter so soon. So would a CSV be of any use? Any other constant pressure solution out there? Should I be worried about the 65-70 pressure setting? I should also note it is a 3/4 HP not a 1 HP jet pump. Any more advice would be helpful.

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    A CSV would do nothing for loss of volume which is what the WHF is causing. Either get a bigger filter that can provide more GPM or twin two in parallel.

  6. #6
    DIY Senior Member Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,174

    Default

    No, change the damn filter, it's plugged up. Would you leave a plugged oil or fuel filter in your car?
    No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!

Similar Threads

  1. 3M recommends pressure tank size for their CBF100 carbon filter
    By hcw3 in forum Water Softener Forum, problems, installation and reviews
    Replies: 58
    Last Post: 04-16-2012, 08:55 PM
  2. Use Chlorine (Charcoal) filter in Whole House Sediment Filter Housing ??
    By kstuart in forum Plumbing Forum Discussion & Blog
    Replies: 0
    Last Post: 03-03-2011, 02:04 PM
  3. Well gpm/pressure/tanks/softner/filter/distance from house questions.
    By maxfischersweet in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 10-11-2010, 10:41 PM
  4. Water Pressure Booter Pump w/softener and whole house filter
    By dsteph3 in forum Plumbing Forum Discussion & Blog
    Replies: 3
    Last Post: 05-13-2010, 06:12 AM
  5. Pressure at tank is great, in house is low unless pump is running
    By greghughes in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 07-16-2008, 09:06 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •