Please look at my washing machine/utility sink drain setup...need advice.

Users who are viewing this thread

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
Previous homeowner was victim of watching too many DIY reality shows, nothing has been done correctly or works like it should. If this IS correct, then I will eat crow.

Tall pipe on the left is where the washing machine drains into. There is a utility sink on the right side fitting. No venting. I don't know if the 2" running up the wall runs to a main vent, if it is its own vent, or if it's used as a drain from something upstairs. I will check and find out.

When the washer drains, the sink fills up near to the top. I don't know if I have an obstruction or if it's due to lack of vent; or a combination of both. I'm going to try and clean everything out just in case.

I'm doing a small remodel on this laundry room (mainly just painting the concrete walls, replacing the sink, installing a cheap floor...ripped out black-molded carpet that was used in the laundry room...WTH???)




Left supply lines are for the washer. Right is for the sink.
P1150463a.JPG




Old drain. Won't work with the new sink. Old sink was raised 1" off the floor just so they had clearance.
2011-11-25_18-06-39_461.jpg



Thinking the drain T needs to be moved to the right a bit, and then done correctly, with the correct fitting.
P1150469.JPG
 

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
OK I looked at the pipe a bit closer.

I turned on the upstairs sink, and it's draining down the pipe labeled below. The pipe that the washing machine is draining into is the one that's a couple feet closer to us.

P1150473.jpg




In this picture, you see the drain pipe for the upstairs sink on the left. The pipe on the right is the one that's hooked to the laundry machine drain. I would ASSume that this is also the vent for the sink? I looked in the attic, and there is a pipe coming up in this same area tied over into another pipe (vent) going up through the roof. This leads me to believe this pipe is purely vent (no drain coming from above).

With that said, what is the proper way to set up the washer and sink traps/vents? Thank you!

P1150475.JPG
 
Last edited:

MTcummins

In the Trades
Messages
389
Reaction score
1
Points
18
Location
Pittsburgh PA
is there a bathroom above the kitchen on a 2nd floor? if not, then most likely this is a properly vented system. if there is, you likely have a lav/tub draining down through this line and you have a wet vent on your laundry. this is not ideal or legal, but does give some venting as opposed to none.

have you opened up that cleanout wye and snaked out the drain? this sounds like a clogged up underground, and thankfully you were left with a cleanout, albeit an awkwardly placed one, that you can use. you'll want to rent a good sized power snake for this, as these lines can go a long way and those old cast iron lines tend to get all corroded and need a little power to break through some of the gunk.

As for the trap, its not horrible, but you'll want to cut off the elbow on the sink trap and glue on an adapter and fit a standard P trap to the sink. This should give you the side to side flexibility to get it to line up properly to the sink. a new tailpiece wouldn't hurt either, with all plastic parts rather than that mix and match of plastic and metal.

it looks like you're darn near level on that drain line from the washer to the drain, you might want to lift it up and resupport it about an inch or so higher to get proper fall.
 

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
At HD now, mobile.
Nothing above the kitchen. Haven't snaked yet, but am buying one.
No ABS here I can see. Think I am going to cut it all off, couple a Fernco to the stub, and redo it in PVC.
...I'll check back in a bit, low batt.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
The washer will need to be a 2" p-trap and standpipe interior dimension. The vent can be 1-1/2"
It will need a vent between the washer p-trap and the waste standpipe.

The laundry tray drain, (sink drain) will need 2" until the vent, and then you can use a 1-1/2" trap arm and vent.

It's easier to have the sink drain located above the washer piping, and then the washer vent and the sink vent can tie together at 42" above the floor.

The original pictures are not correct. It should be torn out and be redone.

Helpful Plumbing Hints for Residential Construction by Bert Polk Plumbing Inspector Lincoln County
 
Last edited:

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
I'm not entirely sure what you mean...I was going to have the sink and washer on the same drain line. Please forgive me, I don't know all the terminology. :(

Also, I did not see black ABS at Home Depot. Should I look elsewhere and use all ABS? Or, should I redo it in PVC, with a Fernco type rubber connector near the waste stack connecting the ABS to new PVC? That still leaves me needing something up top. Unless I used a PVC Sanitary-T with 2x PVC "stubs" sticking out up/down, with a Fernco rubber connector on each end of it.

Please forgive my hack-up Visio job here (feel free to draw on it!). I thought this was the solution you are suggesting, but looking closer at your post, I don't think it is.

Thank you very much.

Laundry_Plumbing.jpg
 
Last edited:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
The sanitary tee on it's side is a problem.

The extra pipe you added, does nothing.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
I was going off of the popular diagram that Terry uses on this site. Is it incorrect?

A sanitary tee can only be placed on it's back for a dry vent take-off, never a drain attachment. Terry's fitting is a combo, which is the equivalent of a wye and 1/8 bend.
Terry's is correct in this regard.
 
Last edited:

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
You will have to move the clean out to a position ABOVE the 2 new sanitary tees so the drain lines can be run lower.
 

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
A sanitary tee can only be placed on it's back for a dry vent take-off, never a drain attachment. Terry's fitting is a combo, which is the equivalent of a wye and 1/8 bend.
Terry's is correct in this regard.
I misunderstood dlarrivee's post about being on it's side, I thought that meant side as in the vertical pipe. I was thinking of the bottom one as more 'on its back', but nevertheless, I would still be in the wrong!

Must be a pretty common mistake that people make huh...I'm looking at that guide that Terry posted above.

drain_san-t.jpg
 
Last edited:

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
No you weren't, your drawing says "sanitary tee pointing straight out for sink drain"... That is what I was referring to.
Actually, I see you replied as I was creating this post, I wasn't even thinking about that one. Thank you.

You will have to move the clean out to a position ABOVE the 2 new sanitary tees so the drain lines can be run lower.
Here is a closer view of that area. Not a big deal I don't think. For a lack of better term, that rubber ring the vent stack is connected into, is that simply a press/friction fit?

So what I am wanting to do here is have the sink on its own drain and the washer on its own drain, correct?

I really appreciate all the help, and, sorry for so many questions. I bought a book tonight hoping I could read up on it and get a better understanding, but it's useless. Might have to return it.

P1150476.JPG
 
Last edited:

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
OK if I have correctly followed your advice, this is what I need?

The last question is ABS or PVC...

Laundry_Plumbing2.jpg
 
Last edited:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
You're on the right track now.

Yes you need to have 2 drain lines, unless you wanted to dump your washing machine into the sink?
 

Dave88LX

Network Engineer
Messages
22
Reaction score
0
Points
1
Location
York, PA
I would really prefer not to. I know it's just a laundry/utility room, but I'd like it to have its own drain and maybe even keep the sink from filling up with water!

Is my best option to just replace the drain/waste stack with all PVC from the top below the 90* down to the rubber gasket in the floor there?
 
Last edited:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
If I was you, I would replace almost everything in the picture, what is in the slab cast iron?

You can keep the abs vent portion...
 