Thread: 50 amp breaker for camper supply outlet

  1. #1

    Default 50 amp breaker for camper supply outlet

    I want to run a 50 amp , 120 volt service for a camper hook-up. There are 200 amps available at the box by the meter.
    there is already a mobile home running from there using 100 amps. i have only been able to find 2-pole 50 amp breakers
    designed for 220v. Can i use one pole of this breaker , removing the bracket between the 2 poles that locks them togethor,
    and run my 120 volts that way? Is it still rated for 50 amps that way, or is it now 25 amps?
    The service will run thru pvc conduit underground, using #6 guage copper wire 35 feet to an outdoor receptacle, where
    the 15 ft cord from the camper will plug in. Any suggestions appreciated.

  2. #2
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,247

    Default

    You could use the breaker, and only connect one pole. I don't know about cutting.

    I guess these do not fit:
    http://www.homedepot.com/p/GE-Q-Line...P150/100171999
    http://www.homedepot.com/p/Square-D-...50CP/100153251

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Each pole of a two pole 50 amp breaker is rated at 50 amps.

    If the vehicle has a 50 amp cord then it is a 120/240 volt system and would need to have a four wire system wired to it.

    They do have 120 volt 30 amp cords with some vehicles.

    Whatever the cord is on the vehicle is what that needs to be installed for that vehicle. In other words if the vehicle has a 30 amp 120 volt cord then don’t install anything but a 30 amp 120 volt system to supply it and so on.

    I have seen vehicles that have a 120 volt 30 amp cord and adapters be used to plug it into a 50 amp receptacle that caused damage to the vehicle due to over amperage of the supply.

  4. #4

    Default

    Yes, those breakers would work, must have missed them. It is a strictly 120 volt service, i'll have to look into
    the rating and size of the cord, but the inside service panel calls it a 45 amp service(the breakers add up to that)
    so i assumed the cord would support that- not good to assume? i will rate the breaker to the cord , as you say-thanks

  5. #5
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,247

    Default

    I suspect that they intended that the vehicle be fed with a 30 amp service. It is common to have the sum of breakers to be significantly greater than the feed amps.

    Can you provide a picture of the external connector at the vehicle?

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    Does the panel in the trailer have a main shutoff? Adding up individual breakers is not usually an accurate way to size the main unless each branch is regularly loaded (not a common situation in a home, maybe in a factory).
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by jnrwood View Post
    Yes, those breakers would work, must have missed them. It is a strictly 120 volt service, i'll have to look into
    the rating and size of the cord, but the inside service panel calls it a 45 amp service(the breakers add up to that)
    so i assumed the cord would support that- not good to assume? i will rate the breaker to the cord , as you say-thanks
    If and I use if loosely it is truly a 120 volt service then I will not be larger than 30 amps.

    The cord end cap should fit one of these types of receptacles. Size the circuit and receptacle as well as the breaker based on the configuration of the cord end cap. Donít use an adaptor unless you are just desiring to have problems and with the interior of a RV the problems ainít cheap
    Attached Images Attached Images  

Similar Threads

  1. HELP: gerber 21-374 floor mount back outlet bowl waste outlet thickness
    By munkyboi in forum Toilet Forum discussions
    Replies: 2
    Last Post: 01-29-2013, 02:22 PM
  2. Replies: 9
    Last Post: 12-11-2012, 12:01 PM
  3. aluminum supply to sub panel - breaker tripping/wire heating
    By completelyhis in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 10-11-2010, 11:14 AM
  4. Replies: 9
    Last Post: 07-18-2008, 07:16 PM
  5. GFCI outlet AND breaker?
    By hans_idle in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 12-17-2007, 01:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •