Thread: Soft copper for shower line?

  1. #1
    DIY Junior Member Bob.W's Avatar
    Join Date
    May 2011
    Location
    Dallas, TX
    Posts
    4

    Default Soft copper for shower line?

    Hello,

    I'm plumbing an American Standard R520 shower valve and adding a twin ell for a tub connection. Since the outlet for the valve is pointing up, I need to make a U-turn, go down below the valve to hook to the twin ell for the tub, then back up for a shower head. I've considered pex, but the cost of the fittings and/or crimpers is high. I was curious if it's OK to use soft copper tubing from the shower valve to the twin-ell and back up to the shower head? Then I could sweat the connections and it would allow me to manipulate the pipe around the supply.

    Thanks,

    Bob

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    On some of those valves, you can flip them, then just rotate the cartridge to get it to work. Do NOT use pex, as the ID restrictions will give you all sorts of grief, usually causing water to go out the showerhead while filling the tub. Are you sure that there isn't just a plug in the valve that could be removed? As to soft copper, I don't know if it would be allowed, and there's got to be a better way!
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member Bob.W's Avatar
    Join Date
    May 2011
    Location
    Dallas, TX
    Posts
    4

    Default

    Nope. That's how they designed it. Install instructions here. Kind of strange, but I guess it will work if I can get all that pipe tucked in the wall. I checked into mounting it upside down, but then the writing on the trim kit would be upside down.

    Bob
    Last edited by Bob.W; 11-14-2011 at 12:45 PM.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    You can flip it, just swap the hot and cold check stops. Not sure what the trim would look like, but it would work.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    It appears that the number you show has a temperature control and a separate volume control above it. That type of valve CANNOT be inverted and still look correct. Use hard copper and sweat elbows to make the turn. Soft copper would require a "lot of room" to make the "U" bend, and would have NO benefits over hard copper, especially TO the twin elbow.
    Licensed residential and commercial plumber

Similar Threads

  1. Water tests soft but doesn't feel soft.
    By ninefall in forum Water Softener Forum, problems, installation and reviews
    Replies: 9
    Last Post: 10-06-2010, 07:54 PM
  2. 5/8 in Soft Copper
    By Livi in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-13-2009, 08:50 AM
  3. soldering soft copper
    By scott99 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 02-07-2007, 03:13 PM
  4. PEX or Soft Copper
    By RRG75 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 11-26-2006, 05:51 AM
  5. Water flow? How long for a branch? Also about soft copper?
    By Clem in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-13-2005, 05:03 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •