    Default 6 AWG to 100 amp subpanel?

    I'm installing a sub-panel for a new addition. My load calc suggests a 50amp load for the sub-panel. So, I'm planning a 50amp feeder breaker in the main panel with #6 feeder wire to the sub-panel. But, the local retail stores don't carry (Siemens) panels smaller than 100amp. I checked with the local inspector (Seattle) and he said that it's common practice to feed a larger sub-panel (e.g., 100amp) from a smaller main feeder breaker/wire (e.g. 50amp, #6 wire).

    The problem is that the 100amp main breaker in the sub-panel I bought lists a wire gauge range of "4 - 3/0". I assume this means I cannot connect #6 wire to it? I don't want to size up the feeder wire/breaker, so what are my options? Are there 100amp sub-panels that will accept smaller wire? BTW, the inspector mentioned that I might run into this issue, but I didn't really follow his recommended solution. Best I could tell, he was suggesting shimming the wire somehow at the 100amp breaker/connecter. That doesn't seem right to me... Is there some sort of adapter available for this situation?

    Thanks.

  2. #2
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    i just wired the same panel in my garage with 6/3 using the 100a siemens panel. worked for me.
    Last edited by Chad Schloss; 11-13-2011 at 11:56 AM.

  3. #3
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    I just wired the same panel in my garage with 6/3 using the 100a siemens panel. worked for me.
    Just because it works does not make it ok or a code compliant installation.

    You should splice a short piece of #4 onto the #6 and terminate the #4 on the breaker lugs.

  4. #4
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Quote Originally Posted by Jim Port View Post
    You should splice a short piece of #4 onto the #6 and terminate the #4 on the breaker lugs.
    Thanks Jim. By "splice" do you mean simply twist-with-wire-nut as you would with smaller gauge splices?

    Steve

  5. #5
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,259

    Default

    I think you need a panel without a main and infeed thru a 50 amp breaker.

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    Quote Originally Posted by ballvalve View Post
    I think you need a panel without a main and infeed thru a 50 amp breaker.
    That would be good, but as long as the wire feeding the subpanel is protected to the size of the wire, it doesn't really matter.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by seattle_steve View Post
    Thanks Jim. By "splice" do you mean simply twist-with-wire-nut as you would with smaller gauge splices? Steve
    Use a split bolt or a Polaris


    Quote Originally Posted by ballvalve View Post
    I think you need a panel without a main and infeed thru a 50 amp breaker.
    That would be backfed and that is what is being done with the 100 amp breaker
    What Jim said

Similar Threads

  1. Question about subpanel
    By wjones4 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 07-02-2009, 04:53 PM
  2. New subpanel?
    By Zenman in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 04-12-2009, 09:58 AM
  3. subpanel
    By HockeyFan in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 02-18-2008, 11:08 AM
  4. Subpanel
    By benr in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 09-07-2007, 07:07 PM
  5. 2nd floor subpanel
    By Jed54 in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 08-10-2007, 09:25 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •