Thread: Generac XG7000E and Interlock Kit

  1. #1
    DIY Junior Member Ted M's Avatar
    Join Date
    Dec 2011
    Location
    Northern New Hampshire
    Posts
    12

    Default Generac XG7000E and Interlock Kit

    There is much confusion regarding connecting a portable generator to a service panel. Iíd like some expert advice on doing this safely and legally.

    I ordered a Generac XG7000E from Home Depot. It will not be here until January 18.
    I tried to get an ownerís manual from Generac, but that requires knowing the exact serial number, which I do not have yet.

    My service panel is a 200 amp, 40-circuit Square D, QO type.

    I have a K-5210 Generator Interlock Kit to use. (www.interlockkit.com)

    The Generac XG7000E will run outside in the yard, connected with a standard 120/240V, 30 amp four-wire flexible cable with twist lock connectors to a Reliance PB30 power inlet box.

    From the box, attached to the outside of the house, will run 10/3 +G to a back-fed 30 amp CB.


    Iíve read the NEC sections about generators being an SDS now.
    I also read Mike Holtís book on Grounding vs. Bonding.

    Some on this forum say that an SDS means the neutral is switched.
    Others say itís an SDS if the neutral and ground is bonded.

    Which is it?

    And, specifically, does anyone know if the Generac XG7000E has a bonded Neutral-Ground?

    If bonded, can it be disconnected, so only one neutral path exists?

    If it IS bonded, then there will be two paths for neutral current.

    How does this comply with code?

    Is it impossible to use a Generator Interlock Kit now?

    Or must we now use a Reliance type ďXĒ transfer switch, which switches neutrals also.

    I guess thousands of people buy generators and hook them up without going through all the confusion Iím having, but I want to get it right.

    Ted

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    This generator will have GFCI protection on the receptacles that is integral to the generator. This means that if you donít switch the neutral the GFCI device will trip every time you switch the breaker in the panel.

    This generator will need to be installed as a separately derived system, meaning the neutral will need to be switched in the transfer switch.

    A UL standard for portable generators now requires this.

    [Engine Generators] Engine Generators for Portable Use


    GENERAL
    This category covers internal-combustion-engine-driven generators rated 15 kW or less, 250 V or less, which are provided only with receptacle outlets for the ac output circuits. The generators may incorporate alternating- or direct-current generator sections for supplying energy to battery-charging circuits.
    When a portable generator is used to supply a building or structure wiring system:
    1. The generator is considered a separately derived system in accordance with ANSI/NFPA 70, "National Electrical Code" (NEC).
    2. The generator is intended to be connected through permanently installed Listed transfer equipment that switches all conductors other than the equipment grounding conductor.
    3. The frame of a Listed generator is connected to the equipment-grounding conductor and the grounded (neutral) conductor of the generator. When properly connected to a premises or structure wiring system, the portable generator will be connected to the premises or structure grounding electrode for its ground reference.
    4. Portable generators used other than to power building or structure wiring systems are intended to be connected to ground if required by the NEC.

    I highly recommend that you save a bunch of money and simply use cords to power what ever you need powered by this generator during a power outage. The amount of time used to go to the panel to switch from one circuit to another to keep from over loading the generator will be about the same as moving the cord from one appliance to the other.

    Keep in mind that this generator will not power more than about 25 to 30 amps for any amount of time without damaging the generator output board.

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    JW, where is that info from? Right from UL?

    That changes a lot of things and is pretty absurd if you ask me.
    Switched neutrals from a portable genny??? So Gen-Tran panels, interlocks, and other extremely convenient devices will be rendered obsolete?? Real smart UL. This is push people into doing it the dangerous way.
    Last edited by Speedy Petey; 12-03-2011 at 08:06 AM.

  4. #4
    DIY Junior Member Ted M's Avatar
    Join Date
    Dec 2011
    Location
    Northern New Hampshire
    Posts
    12

    Default

    JW: Thanks for the reply.

    I did read your text above with the underling, etc., in previous posts.

    I'm convinced that my Generac XG7000E will have to remain bonded and run as an SDS.

    However, running from cords seems to be a major inconvenience also.

    I'd have to rewire my furnace connections, and the well pump also.

    Some friends of mine in CT were without power for a week.
    If that happened to me I'd like to have some hot water also.
    The XG7000E could run my water heater (with little else).
    Rewiring it for cords would be difficult.

    I'm sure I could wire up an X-Series (neutral switching) transfer box.
    Like you said though, it's a one-time expensive item.

    Ted

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    [
    Quote Originally Posted by Ted M View Post
    JW: Thanks for the reply.
    You are very welcome

    Quote Originally Posted by Ted M View Post
    I did read your text above with the underling, etc., in previous posts.
    I'm convinced that my Generac XG7000E will have to remain bonded and run as an SDS.
    This is what UL mandates and the NEC will reflect this in the near future

    Quote Originally Posted by Ted M View Post
    However, running from cords seems to be a major inconvenience also.
    I have been using this method for several years now and it isnít as bad as it seems. The problem comes when one wants to use the generator for a load bigger than it is designed to carry.

    Quote Originally Posted by Ted M View Post
    I'd have to rewire my furnace connections, and the well pump also.
    With the little generator the well is all it could safely pull at once. I hope it is a gas furnace in which case it would be little effort.

    Quote Originally Posted by Ted M View Post
    Some friends of mine in CT were without power for a week.
    If that happened to me I'd like to have some hot water also.
    the longest time we were without power was 11 days and we lived through it with little or no discomfort
    Quote Originally Posted by Ted M View Post
    The XG7000E could run my water heater (with little else).
    Rewiring it for cords would be difficult.
    It would be a major strain on that little generator to supply a water heater if the elements were 4500 watts. To have anything else even a 100 watt light would be more than it could carry for any amount of time. If you look closely at the manual it states that the rating of the generator is 29 amps continuously and 36 amps surge.

    Quote Originally Posted by Ted M View Post
    I'm sure I could wire up an X-Series (neutral switching) transfer box.
    Like you said though, it's a one-time expensive item.
    Ted
    I have never heard of or seen a X series transfer switch.

    When someone wants to use a generator for optional backup power they would be well advised to size the generator for the load being served. I have been dealing with these small generators for many years now and it has been my experience that the generators just do not fulfill the desires of the user. They are constantly having them repaired or replaced not to mention running outside to restart it after it stalls.

    I would recommend that if you are wanting to use the well, water heater, heat and watch TV while the lights are on then go ahead and spend the upfront money and install at least a 14KW generator that will carry all this load without having to sit in the dark while the water heater heats up. These small generators are not designed to carry this large of a load and to keep it from stalling you will be constantly be running back to the panel to turn something off while something else is on.
    This is not to mention the damage that might happen while using electronic devices such as TV and sound around systems and the like.

    We use two small generators when we have a power failure. One is just for the well as we have horses that require water. The other is for a lamp that is carried from one room to the other as needed.
    We do not watch TV and only connect to the refrigerator and freezer for 30 minutes at a time twice a day. We leave the doors shut so there is not warm air introduced to the inside of them.
    We have gas logs and they do a fair job of keeping us warm. We use this time for some family bonding the way families should bond.

  6. #6
    DIY Junior Member Ted M's Avatar
    Join Date
    Dec 2011
    Location
    Northern New Hampshire
    Posts
    12

    Default

    JW: The Reliance X-Series is new. You can see them on the Reliance site. These panels switch the neutrals also.

    See:
    http://www.reliancecontrols.com/Prod...x_series&c=&f=


    I know the water heater is a large load. 240 volts, 18 amps or so.
    I would have to run it only once a day. Everything else turned off. Have to try it once anyway.
    No problem running up and down stairs to switch things on and off.

    My furnace is oil/air. 120 volts and 12.5 amps.
    House is extremely well insulated. Use 275 gallons of oil a year.
    I'd just run the furnace (only) a few times a day.

    The well pump is rated 230 volts and 4.4 amps.
    Again, I'd just run it when the water tank got low.

    I expect there to be inconveniences when on emergency power.
    There were plenty of times things were inconvenient with no power at all!

    The 7000 running watts will have to do for me.
    Managing the loads properly will be the least inconvenience.
    The heavy load items will just have to be run without anything else on.

    Ted

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Speedy Petey View Post
    JW, where is that info from? Right from UL?
    You can see it here
    http://database.ul.com/cgi-bin/XYV/t...962&sequence=1

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Thank you for the link. Donít know why but my mind went to X-10 remote switching devices.

    The problem with the well and the water heater is found in Section 430.22 for the well and 422.13 for the water heater. The inrush current needed to start the well motor might be enough to cause a voltage drop across the circuit board of the generator. The same is true of the continuous load of the water heater load should anything else be on at the same time. Here in lies the danger to your set up.

  9. #9

    Default

    Quote Originally Posted by Speedy Petey View Post
    JW, where is that info from? Right from UL?

    That changes a lot of things and is pretty absurd if you ask me.
    Switched neutrals from a portable genny??? So Gen-Tran panels, interlocks, and other extremely convenient devices will be rendered obsolete?? Real smart UL. This is push people into doing it the dangerous way.
    Yup. During the October snowstorm I had two HOs who wanted whole house transfers. They both had the unfortunate luck to live in the only town that has an inspector that is wise to the switched neutral and enforces it. As soon as they heard the price they both said they would take their chances with the illegal way. So instead of having two homeowners using an interlock kit they are using nothing. I understand the need to change the code, but it has come at a high price as far as safety is concerned.

    Ted thanks for the link on the Reliance panels. I've been looking for something to replace the non neutral switching Gen-Trans and if its similar cost or even just a little more it could be a potential substitute.

    -rick

  10. #10
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    What is the difference in UL listed and UL Approved ?

    The UL Mark is Stuck on a lot of JUNK, I Think.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  11. #11
    DIY Senior Member Rich B's Avatar
    Join Date
    Sep 2008
    Location
    New Jersey
    Posts
    282

    Default

    The switched neutral code is something I do not see often and have not seen it very much. I work for a generator service company. I have worked for this company for 18 years. I have done field work and worked on transfer switches and generators of all sizes. We have tied in large portable generators many times to take the place of one that is broken or getting repaired or replaced. Very few transfer switches switch the neutral and just about every generator has the neutral bonded to the frame.

    I just saw a 400 amp transfer switch installed that was permitted and inspected. It is for use with a large generator not yet in place. It has NO switched neutral and was inspected by the towns electrical inspector. His main concern was the grounding system......The final inspection was maybe a month ago.

    We have sold a ton of units for home owners because of the storms this past fall. We sold a lot of Briggs 10-12kw standby units with transfer switches. None of those switches switch the neutral. We are not installing these units ourselves, licensed electricians or contractors are. I have not heard any feedback about this issue from anyone.
    Last edited by Rich B; 12-04-2011 at 04:36 AM.

  12. #12
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Rich B View Post
    The switched neutral code is something I do not see often and have not seen it very much. I work for a generator service company. I have worked for this company for 18 years. I have done field work and worked on transfer switches and generators of all sizes. We have tied in large portable generators many times to take the place of one that is broken or getting repaired or replaced. Very few transfer switches switch the neutral and just about every generator has the neutral bonded to the frame.

    I just saw a 400 amp transfer switch installed that was permitted and inspected. It is for use with a large generator not yet in place. It has NO switched neutral and was inspected by the towns electrical inspector. His main concern was the grounding system......The final inspection was maybe a month ago.

    We have sold a ton of units for home owners because of the storms this past fall. We sold a lot of Briggs 10-12kw standby units with transfer switches. None of those switches switch the neutral. We are not installing these units ourselves, licensed electricians or contractors are. I have not heard any feedback about this issue from anyone.
    And this in no way means that any one of them is installed in a code compliant and safe manner.

    When the neutral is bonded to the generator frame and is not switched there is a parallel path on the neutral and the grounding conductor. This is a BIG no-no and is dangerous even if there has been no reported incident you have heard of. I promise you that I have heard of many incidents of where someone was hurt due to the improper installations of small stand-alone generators and help investigate one fire due to improper bonding while refueling of a generator that was bonded and the neutral was not switched. The person had burns over 30 percent of his body simply because he wanted that stand-alone generator connected to his house.

    As with a lot of people there is a lot of confusion with electrical inspectors when it comes to the earth ground. This is spelled out in 250.4(A)(1) of the NEC and has nothing at all with how a generator works.

    I have spent many hours trying to get these small stand-alone generators outlawed from being connected to premises wiring systems and will continue my fight against such ridiculous setups. They have their place in society and connected to someone’s home is NOT one of them.
    Unless the person using one of these small generators has some knowledge about electricity they are asking for problems. Case in point;
    A lady with COPD and using an oxygen concentrator hired an electrician to install a generator so she would have power for her machine in case of a power failure. The little old lady was on SSI and had a limited income so the electrician installed a 5500 watt generator for backup power.
    This worked out fine as the next door neighbor would come over and set everything up and start the generator for the woman when the power went out.
    Power goes out during an ice storm, neighbor comes and starts the generator and everything is fine. Lady is hungry and has had no breakfast so she goes to make something real quick and a pot of coffee. Some of her medication requires her to take it with food as well as her being a diabetic and requiring her to eat when her blood sugar gets low. The generator stalls and leaves her without any power.
    Neighbor returns home from work and notices that the generator is not running so goes over to check thing out and finds lady in floor. Her blood oxygen got very low and she passed out.
    Thank God she pulls through this ordeal and there was no real harm except she did not have what she thought she had paid for, backup power. This set up was replaced with a 24KW generator so she could have heat during a power failure without worry about it stalling out. With this new setup she didn’t need any help starting the generator as it started all by itself. All this was paid for by the tender hearts of her family and friends and the rebate from the electrical contractor that installed that bunch of bull crap in the first place.

    Those who know me on these forums know that I work side by side with people who are on the Code Making Panels as well as with people from UL and Met Labs. I spend a lot of time at our State Capitol working with the DOI and with NCIAEI on education material for contractors and inspectors. I am continually talking about such issues as the stand-alone generators being connected to premises wiring systems and the dangers involved. This is with some of the greatest minds in the electrical industry and not with someone who thinks they know what they are talking about.
    Most of these units especially those made in the past are not approved for use during inclement weather and not approved for connection to premises wiring systems. This is why the mandate that ALL RECEPTACLES be protected by GFCI so that the connection between a system that is already bonded will cause the GFCI device to open. This forces the switching of the neutral should one be connected to someone’s home. It is a life safety issue and not something that someone thinks they know something about.

  13. #13
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by Rich B View Post
    The switched neutral code is something I do not see often and have not seen it very much. I work for a generator service company. I have worked for this company for 18 years. I have done field work and worked on transfer switches and generators of all sizes. We have tied in large portable generators many times to take the place of one that is broken or getting repaired or replaced. Very few transfer switches switch the neutral and just about every generator has the neutral bonded to the frame.

    I just saw a 400 amp transfer switch installed that was permitted and inspected. It is for use with a large generator not yet in place. It has NO switched neutral and was inspected by the towns electrical inspector. His main concern was the grounding system......The final inspection was maybe a month ago.

    We have sold a ton of units for home owners because of the storms this past fall. We sold a lot of Briggs 10-12kw standby units with transfer switches. None of those switches switch the neutral. We are not installing these units ourselves, licensed electricians or contractors are. I have not heard any feedback about this issue from anyone.
    And I'll keep installing them until such time that I see a written electrical code disallowing them or have an inspector flag one with proper documentation.
    To say they are all inherently unsafe is kind of ambiguous.

  14. #14
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Speedy Petey View Post
    And I'll keep installing them until such time that I see a written electrical code disallowing them
    Here it is, 110.3(B) and the link in post #7

    Also see 702.11 for the installation process for connecting one of these self-contained generators to a premises wiring system.
    (A) Addresses a Separately Derived System and requires a ground rod as outlined in 250.30, no exceptions
    (B) Non-separately Derived System allows the grounding electrode of the premises wiring system
    How do we determine the difference between the separately derived system form the non-separately derived system? The bonding at the generator, if the neutral is bonded to the frame it is a separately derived system and will require an electrode to be installed at the generator and the neutral to be switched.

    To connect a stand-alone generator to the premises wiring has rules that must be followed no matter if we see the danger or not.

    250.34 does not require a grounding electrode system for stand-alone generators only if the generator is being used as a stand-alone system with no connection between the generator and the equipment being supplied such as distribution panels such as service equipment. See the Informational Note under 250.34(C)
    There it is in black and white and the rules for using one of these generators as an optional backup system.

    As long as they are being used with cords from the generator to the appliance then there is no violation of the installation instructions and the NEC but the minute that one is connected to a panel then the listing and the NEC takes hold and the requirements must be met.

    And remember that just because an inspector signs off on an installation does not relieve the contractor of liability or at least not here in North Carolina. Should something go wrong the electrical contractor is the one who is gone after not the inspector. Unless it is a case of gross negligence the inspector is protected by the state and in the worst case will only loose his inspection certificate.

    As with the case of the fire in my earlier post the installation had nothing to do with starting the fire but the bonding at both ends of the neutral got the electrical contractor a trip to the licensing board and the inspector was not approached in any way.

  15. #15
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    110.3(B) says to follow the manufacture's instructions and does not apply IMO.

    All I can say is I am glad you are not my inspector.

Similar Threads

  1. Generac Portable Generator
    By rockycmt in forum Electrical Forum discussion & Blog
    Replies: 36
    Last Post: 12-06-2011, 03:24 PM
  2. Generac NG generator
    By bubb1957 in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 11-22-2011, 02:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •