(206) 949-5683, Top Rated Plumber, Seattle
Results 1 to 2 of 2

Thread: Need help gas line supply calculation

  1. #1
    DIY Junior Member
    Join Date
    Nov 2011
    Location
    Maine
    Posts
    1

    Default Need help gas line supply calculation

    I am installing a Paloma PH-28CDVSP Commercial Direct Vent Gas Tankless Water Heater. LP I have an 11" w.c. 250,000 BTU regulator from my tanks and less than 5 foot of line to inside my house 3/8" copper tube that goes to a 3/4" rigid pipe to enter house and back to a copper tube. With that said the max input BTU's for this unit is 199,000. I have to run 12' to get to the unit and the only other appliance on this is a cooktop, no furnace, nothing else. The propane co. told me I can use the existing 3/8" tubing to supply the unit and should not see a starvation issue, I am beginning to wonder with all of the reading I am doing. any input would be great. Oh and the unit will heat water up to 180 degrees at full throttle which I will never use. (yes it is overkill but got the unit for less than half price for a residential unit of the same temp rise/flow.) Thanks

  2. #2
    DIY Member bsperr's Avatar
    Join Date
    Apr 2008
    Location
    Athens, GA
    Posts
    71

    Default

    I'm no expert, but the tables in the fuel gas code show the capacity of 3/8 copper for LP at 11" wc as only 188K BTU/hr at 10 feet and 129K BTU/hr at 20 feet with a pressure drop of .5" wc. An accurate pipe sizing would require more details about your piping system, but it doesn't look like that length of 3/8 copper would supply that water heater at full demand, which is what you would size for. You can read the fuel gas code online for free at nfpa.org, you just have to set up a free account. Appendix B has some helpful examples of gas pipe sizing.
    Last edited by bsperr; 11-02-2011 at 10:19 AM.

Similar Threads

  1. Calculation for heat supply to a given area
    By idoc4u in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 07-22-2010, 01:41 PM
  2. I need help with a pump calculation
    By mishomi in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 05-17-2010, 05:42 AM
  3. Drawdown Calculation....
    By watrax in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 09-08-2009, 06:29 AM
  4. Load calculation?
    By Nate R in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 12-22-2007, 01:49 AM
  5. Supply line
    By Cookie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-01-2007, 02:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •