Thread: advice on wire gauge for built in oven

  1. #46
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by leejosepho View Post
    Before I knew the difference between AFCI and GFCI, I had an AFCI trip and never stay on and nobody here could ever explain why.
    I guess I missed out on that one.

    I do know that a GFI for an appliance is different than a Personal Protective GFI.

    Personal Protective GFIs trip in the 5 MA or so range

    and Appliance GFIs trip at around 30 MA.


    If you run a appliance on a Personal Protective GFI, You are Very Lucky if it Does Not Trip on occasion.


    If You really want to be 100% safe, Turning OFF the Main Breaker works much better than anything...
    Last edited by DonL; 12-12-2011 at 12:23 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  2. #47
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by DonL View Post
    Don't give up Electromen®

    Not all of us are as lucky as JW in this real world.

    I think You meant to say "Have fun, Ill be back."
    Hi Don, sometimes it IS hard to just read and enjoy the discussion and remain quiet for long, even though you swore it off. Discussion is good; don't worry be happy. We can't win every argument, but we can put our $.02 in.
    I am definitely not a pro plumber, but I am a pro crastinator

  3. #48
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by DonL View Post
    ... I had an AFCI trip and never stay on and nobody here could ever explain why.
    I guess I missed out on that one ...
    That was just a little side issue in my workshop thread while we were all discussing/debating/arguing the matter of whether ground rods ever actually accept/conduct/convey any faulted current.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  4. #49
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Oops. Browser fault!
    Last edited by jwelectric; 12-12-2011 at 10:00 AM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  5. #50
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by leejosepho View Post
    That was just a little side issue in my workshop thread while we were all discussing/debating/arguing the matter of whether ground rods ever actually accept/conduct/convey any faulted current.
    Sure they do.

    Most of the Current will take the path of Least resistance...
    Last edited by DonL; 12-12-2011 at 01:29 PM. Reason: Op Error
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  6. #51
    DIY Junior Member Electromen's Avatar
    Join Date
    Dec 2011
    Location
    Pittsburgh
    Posts
    17

    Default

    Quote Originally Posted by DonL View Post
    I guess I missed out on that one.

    I do know that a GFI for an appliance is different than a Personal Protective GFI.

    Personal Protective GFIs trip in the 5 MA or so range

    and Appliance GFIs trip at around 50 MA.
    I've never heard of ones that are for appliances. There is GFCI protection for large service entrances, like 800 amp and above which are different. For personal protection I only know of one type available in the receptacle and circuit breaker. If there are ones dedicated to appliances I'd like to learn about it.
    Electrical Contractor since 1980

  7. #52
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by DonL View Post
    Sure they do.

    Least path of resistance...
    Wow! Current takes every available path not just the path of least resistance. The earth being a high resistor will conduct little or no current from a 120 supply.

  8. #53
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by DonL View Post
    I guess I missed out on that one.

    I do know that a GFI for an appliance is different than a Personal Protective GFI.

    Personal Protective GFIs trip in the 5 MA or so range

    and Appliance GFIs trip at around 50 MA.


    If you run a appliance on a Personal Protective GFI, You are Very Lucky if it Does Not Trip on occasion.


    If You really want to be 100% safe, Turning OFF the Main Breaker works much better than anything...
    There is the Ground Fault Circuit Interrupter that we install for those places outlined in 210.8 such as bathrooms, garages, outdoors, crawl spaces, unfinished basements, kitchens and other places that are installed to protect the user.

    Then there is ground-fault protection of equipment as outlined in 215.10 for feeders and 230.95 for services where these are 600 volts or less and more than 1000 amps.

    These are two different types of ground fault protection

  9. #54
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by Electromen View Post
    I've never heard of ones that are for appliances. There is GFCI protection for large service entrances, like 800 amp and above which are different. For personal protection I only know of one type available in the receptacle and circuit breaker. If there are ones dedicated to appliances I'd like to learn about it.

    They Vary depending where in world that you are.


    United States

    GFI receptacles in the USA have connections to protect downstream receptacles so that all outlets on a circuit may be protected by one GFI outlet.

    In the United States, the National Electrical Code requires GFCI devices intended to protect people to interrupt the circuit if the leakage current exceeds a range of 4–6 mA of current (the trip setting is typically 5 mA) within 25 ms. A GFCI device which protects equipment (not people) is allowed to trip as high as 30 mA of current; this is known as an Equipment Protective Device (EPD). "RCDs" with trip currents as high as 500 mA are sometimes deployed in environments (such as computing centers) where a lower threshold would carry an unacceptable risk of accidental trips. These high-current RCDs serve for equipment and fire protection instead of protection against the risks of electrical shocks.

    GFCI outlets are required by law in wet areas (See National Electrical Code (US) for details.)

    In the U.S., the National Electrical Code requires GFCIs for underwater swimming pool lights (1968); construction sites (1974); bathrooms and outdoor areas (1975); garages (1978); near hot tubs or spas (1981); hotel bathrooms (1984); kitchen counter receptacles (1987, revised 1996 and specifically excluding the refrigerator outlet, which is usually on a dedicated circuit); crawl spaces and unfinished basements (1990); wet bar sinks (1993); laundry sinks (2005).[7]

    This link has some more info;

    http://en.wikipedia.org/wiki/Residual-current_device


    Sorry about the MA error on my part "equipment (not people) is allowed to trip as high as 30 mA of current"
    I think I put 50MA, I stand correcting Myself.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  10. #55
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by jwelectric View Post
    There is the Ground Fault Circuit Interrupter that we install for those places outlined in 210.8 such as bathrooms, garages, outdoors, crawl spaces, unfinished basements, kitchens and other places that are installed to protect the user.

    Then there is ground-fault protection of equipment as outlined in 215.10 for feeders and 230.95 for services where these are 600 volts or less and more than 1000 amps.

    These are two different types of ground fault protection


    Let me get my book out...
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  11. #56
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by jwelectric View Post
    The earth being a high resistor will conduct little or no current from a 120 supply.
    If this is the case, Then why can I go outside and take an extension cord, connect the Hot (Black /small blade) side to a light bulb and connect the other side of the light bulb to a Ground Rod (Connected to nothing but earth), and it lights up ?

    (I do not recommend trying this, unless you are an electrician)

    Please Tell me where the Voltage / Current return path is coming from ? Sounds like FM.

    I think that you could learn more from some Experimenting.


    If Earth Ground is that bad then why does the NEC even require it ?

    And if you are correct (as You must be) then a GFI for outdoor use is Useless, is it not ?


    I would like to learn something new because Theory only works in a Vacuum,
    That is, unless you know every single variable...
    Last edited by DonL; 12-12-2011 at 02:45 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  12. #57
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    We are not even getting this Oven Fixed, lol...
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #58
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by DonL View Post
    If this is the case, Then why can I go outside and take an extension cord, connect the Hot (Black /small blade) side to a light bulb and connect the other side of the light bulb to a Ground Rod (Connected to nothing but earth), and it lights up ?
    ,Do you understand the difference between parallel and series connected resistance?

    Quote Originally Posted by DonL View Post
    I think that you could learn more from some Experimenting.
    I do this experiment several times a year. I am having different results than what you are having.
    Quote Originally Posted by DonL View Post
    If Earth Ground is that bad then why does the NEC even require it ?
    The answer is found in 250.4. There are four reasons to connect a wiring system to earth, 1- lightning, 2- Power surges, 3- unintentional contact with higher-voltage lines, and 4- stabilize the voltage
    Using the requirement of 250.56 of the NEC of 25 ohms and 120 volts Ohm’s Law says if I connected a 15 amp breaker directly to an 8 foot rod then only 4.8 amps of current will flow.
    Most residential transformers across the US are supplied on the primary by 7200 volts. Using the same 25 ohms this high voltage will push 288 amps of current through the earth. (Unintentional contact) A lightning strike will have a very high voltage and in the event of a strike earth will allow a magnitude of current to flow with that kind of a push. Should lightning strike the high voltage lines the secondary will have a “surge” of 1/30 of whatever the lightning strike was but it will be high enough to push a lot of current through the earth. (power surge)
    The power company does everything it possibly can to achieve at the most 10 ohms on their grounding electrodes. Look at the pole holding any transformer and see their conductor going to their electrode.
    In most cases across the US the resistance of grounding electrodes on homes will be 300 ohms and upwards. To drive an 8 foot single rod anywhere in America and you will be darn lucky to have less than 100 ohms.

    Quote Originally Posted by DonL View Post
    And if you are correct (as You must be) then a GFI for outdoor use is Useless, is it not ?
    If you really meant what you said in your last sentence of this post you would have been listening when I explained how a GFCI device works. The connection to earth plays no role in the equation. What makes one open is when there is a difference of .004 to .005 amps between the black and white conductors connected to the device.
    A human with a resistance of say 10k ohm and using 25 ohms for earth this would be a total of 10025 ohms. Divide 120 volts by 10025 ohms and there will be about .012 amps flowing. This is just shy of the “let go threshold” but more than enough to trip a GFCI device, almost three times the amount of current to open the GFCI device.

    Your light bulb experiment above done with math will be as follows;
    120 volts with a 100 watt light bulb and the resistance of the rod at school that averages ~500 ohms. To find the resistance the test was done with a three point reading for a more accurate reading by an engineer three years ago.
    To find the resistance of the bulb we will square the voltage and divide by the wattage which gives us 144 ohms
    Add the resistance of the rod and bulb and forget the resistance of the conductor being that it is so small will give us a total resistance of 644 ohms.

    Now to see how much wattage this circuit will allow to flow we will square the voltage and divide it by the resistance and the total wattage this circuit will allow to flow is just over 22 watts. Yep late at night one might see the bulb glow.

  14. #59
    In the Trades mtcummins's Avatar
    Join Date
    Jun 2010
    Location
    Pittsburgh PA
    Posts
    380

    Default

    Y'all can talk theory till yer bleu in the face...

    I know for a fact that GFCIs do trip w/o reason. There's probably a good 100 million people in this country who could confirm that they've had random trips.

    As for your comments about what work I do, no I don't do new construction. I hate it. I do historic renovations and restorations. My contractor... not sure how (or why?) you made any random assumptions about the kind of work they do, but they do massive amounts of new construction. He'll tell you the same thing... the damn things trip on their own. Not all the time, not always with the same tools, just randomly. You're still operating under the assumption that they act 100% consistently, so that a tool that trips one once would always trip them. This is false. So no, they aren't running to the GFCI all day, that would assume consistent failure, which would indicate either a faulty GFCI or a faulty tool.

    If your head is too far up your arse to deal with reality, that's your problem. Theory or no theory, calculate all you want. Think about it for another few years, run the calcs, read your textbooks. Keep telling people the "facts" based on books. Fact is, in the real world the things do trip, and its not always for a good reason. Many thousands of people can confirm this. Therefore, GFCIs should not be put on appliances such as refrigerators, freezers, cooktops, D/W, disposals, etc.

  15. #60
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by mtcummins View Post
    Y'all can talk theory till yer bleu in the face...

    I know for a fact that GFCIs do trip w/o reason. There's probably a good 100 million people in this country who could confirm that they've had random trips.

    As for your comments about what work I do, no I don't do new construction. I hate it. I do historic renovations and restorations. My contractor... not sure how (or why?) you made any random assumptions about the kind of work they do, but they do massive amounts of new construction. He'll tell you the same thing... the damn things trip on their own. Not all the time, not always with the same tools, just randomly. You're still operating under the assumption that they act 100% consistently, so that a tool that trips one once would always trip them. This is false. So no, they aren't running to the GFCI all day, that would assume consistent failure, which would indicate either a faulty GFCI or a faulty tool.

    If your head is too far up your arse to deal with reality, that's your problem. Theory or no theory, calculate all you want. Think about it for another few years, run the calcs, read your textbooks. Keep telling people the "facts" based on books. Fact is, in the real world the things do trip, and its not always for a good reason. Many thousands of people can confirm this. Therefore, GFCIs should not be put on appliances such as refrigerators, freezers, cooktops, D/W, disposals, etc.

    Very Well Put...
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Converting from larger to smaller wire gauge
    By maurice53 in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 05-21-2011, 12:16 PM
  2. Wire gauge for new double-oven?
    By Artie in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 11-11-2010, 07:51 AM
  3. wire gauge change mid circuit
    By rockycmt in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 01-09-2009, 11:29 AM
  4. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM
  5. heavy gauge bare copper wire
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 03-26-2008, 07:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •