    Default Air in water line after backwash

    I have a hydroflo acid neutralizer unit-TNFA15 I installed last year (It's still covered by the 5-year warranty).
    I'm on well water. I haven't had any well issues.

    For over a year, the system has worked without problem. No water leaks, no air in the water line.
    About three months ago, I started getting air in all my water faucets the morning after the backwash. The air will come out in a big pulse (including toilets). After that, I'm fine until the next backwash (every six days).

    I called the local supplier I bought the unit from. They say I may have a bad control head. I can return it to them, they will ship it to the factory where it will be tested, If it's bad, the factory will give me a credit. (I can buy a new head now and get a credit for it, so I have continuous service.) The cost for the control head is as much as the whole unit. ($500-$1000)

    Before I return the unit and risk the $500, I'd like to eliminate other possible problem sources.
    I've done a physical inspection of the control head exterior, and it's perfectly clean.
    Is it possible that the well pump is bringing up air under semi-continuous use required to run the backwash?
    --A few weeks ago (I think after we started having the air in the water line problem) we had a power outage and I had to run my generator intermittently to run the well pump. (The generator is just large enough to power the pump--not much else runs when the pump does.)

    Do you have any other ideas or has anyone seen a similar problem?
    Thanks,
    Mark

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,687

    Default

    Do you have a bladder tank or one with an air volume control? The AVC on my precipitation tank needs to be cleaned periodically. Due to the high GPM flow during backwash, the pressure will drop a little lower than the pump kick-in setting which lowers the water in the tank enough to release air into the water stream.

    As a test, turn off the power to the pump and drain the tank a few PSI below the kick-in to see if air releases.

  3. #3
    handy homeowner Mark Plumb's Avatar
    Join Date
    Oct 2011
    Location
    Maryland
    Posts
    3

    Default

    I have an air bladder tank. Installed 10+ years ago. Never had to repressurize it.
    When I had to run the pump from the generator, I had to be near the water system while it ran. I didn't notice anything unusual during that time.

  4. #4
    In the Trades Akpsdvan's Avatar
    Join Date
    Dec 2009
    Location
    Alaska
    Posts
    1,471

    Default

    It is possible that the well pump is bring up the air.
    With in the last few weeks I had a customer that had air that was getting in some place between the pump-pitless and the run into the house is getting air and messing up the softener..

    I would check the pressure tank and the rest of the system for where the air is coming in.

  5. #5
    handy homeowner Mark Plumb's Avatar
    Join Date
    Oct 2011
    Location
    Maryland
    Posts
    3

    Default 100% Correct

    I didn't believe it, but you were right on target.
    I was getting ready to bring the acid neutralizer control head back to the supplier for an exchange (and it would have cost me for a new head and for 2xshipping) when I started noticing that we had very low water pressure. We called a plumber to have a look, at it turned out that we had a bad pressure tank; when we used water, the well pump was running continuously (and then turning off when it overheated). Since the pump was 13 years old, we decided to replace it as well with a constant pressure system.

    Thank you.
    Mark

  6. #6
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,792

    Default

    A "bad" pressure tank can't cause the problem unless it is leaking. So you had a leak somewhere between the pump and the pressure switch that was probably fixed when they changed the pump.

    I wouldn't have gone with a constant pressure pump. A regular pump and Cycle Stop Valve would have been a much better choice and cost much less.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  7. #7
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,945

    Default

    I would have saved even more money and replaced the tank and the pump with a regular pump.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. I get a continuous flow of water from the backwash drain pipe (Culligan Medallist)
    By toddomel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 10-12-2010, 01:33 PM
  2. Outside Backwash Drain
    By zientm in forum Water Softener Forum, problems, installation and reviews
    Replies: 7
    Last Post: 01-16-2010, 06:19 PM
  3. Neutralizer backwash HELP.
    By 1krzqb in forum Water Softener Forum, problems, installation and reviews
    Replies: 1
    Last Post: 07-27-2009, 07:16 AM
  4. Backwash Filtration System
    By sparker in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 01-09-2009, 09:13 PM
  5. Dirty water after backwash
    By jjamison in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 09-13-2007, 08:37 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •