Thread: Pump overload tripping at night

  1. #1
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default Pump overload tripping at night

    The overload on my pump control box has tripped 3 out of the last 4 nights. It only happens at night and we wake up to no water. When I reset it, the pump runs fine all day and then it trips again over night. I have been trying to figure it out with no luck. I measured current in the 3 legs to the pump and got Red = 1.1A, Black = 10.7A and Yellow = 11.0A. I'm not that familiar with electrical issues so I'm not sure if this is normal. I have a 3/4 HP pump that I think is running on 240V. Any suggestions?
    Last edited by ehuddle; 10-30-2011 at 08:41 AM.

  2. #2
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    As a follow up, I measured the resistance between the legs on the motor at the well head. I got 9.2 Ohms Yellow-Red, 10.2 Ohms Red-Black and 2.8 Ohms Yellow to Black.

  3. #3
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Search and read the franklin AIM manual and it will give you all the specs.

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    In most homes the pump will have no reason to run during the overnight hours, so it does not sound like an overload trip.

  5. #5
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    My water softener recharges at night. The overload on the control box is what is tripping. I've tried to reproduce it by forcing the pump to cycle repeatedly with no luck. Is there anything a softener can do to cause the overload to trip?

  6. #6
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by ehuddle View Post
    I've tried to reproduce it by forcing the pump to cycle repeatedly with no luck. Is there anything a softener can do to cause the overload to trip?
    Is the softener on a completely different circuit? *Maybe* the softener is somehow reducing voltage to the pump and the pump's amperage is going too high. Try manually cycling the softener while you watch.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  7. #7
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    The softener plugs into the GFCI outlet in the garage so I don't think it's on the same circuit. Electrical is not my specialty. I'll dig into that a little more when I get home. I did manual cycle the softener and it did not trip.

  8. #8
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Wow. Your first post gave all the info I needed to determine the problem. Your pump is pulling way too many amps.

    That motor, according to the charts, should pull no more than 8 amps. Your pump/motor is fixing to quit, you better get it fixed ASAP.
    Last edited by Texas Wellman; 10-31-2011 at 08:47 PM. Reason: Silly spelling errors.

  9. #9
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    TW is right, a 3/4 HP should pull no more than 8 amps. The real question is, how is it working at all? Probably already survived the average of 7 years and cycled itself to death.

  10. #10
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    The pump has been in operation for 3 yrs as of October 16th when we moved into the newly built house. I was assuming it was the pump.

  11. #11
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    The average life of a submersible is 7 years. If it only lasted 3 years, it must be cycing a lot. One of your neighbors pumps doesn't cycle much and will last 11 years. That is why the average is 7 years.

  12. #12
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by ehuddle View Post
    The softener plugs into the GFCI outlet in the garage so I don't think it's on the same circuit.
    The pump gets 120V from one line and then 120V from the other to get a total of 240V, and the softener gets 120V from one of those lines at the breaker panel. However, I have seen situations where a 120V outlet has been illegally tapped from one of those lines (such as at or near the pump) ... but that is obviously not your case there in a relatively new home.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  13. #13
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    I had a neighbor (who happens to be an electrician) mis-diagnose his pump by measuring amps. Turned out to just be a bad heatshrink that was sending current to ground. (Yes JW, current can go to ground)

    The jury is still out until the pump is pulled and the wire inspected.

  14. #14
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    Quote Originally Posted by leejosepho View Post
    The pump gets 120V from one line and then 120V from the other to get a total of 240V, and the softener gets 120V from one of those lines at the breaker panel. However, I have seen situations where a 120V outlet has been illegally tapped from one of those lines (such as at or near the pump) ... but that is obviously not your case there in a relatively new home.
    Don't make any assumptions here. I actually had to sue the builder of my home for poor construction. I can't even figure out who dug the well because he fled to the Virgin Islands during the court case. Long story...

  15. #15
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    I doubt that yours is hooked up to the wrong voltage. But any driller who flees to the islands or even spends the off season there is probably not reputable.

Similar Threads

  1. HELP!!!!Overload Keeps Tripping on Submersible Pump
    By Dwayne N in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 10-21-2009, 12:21 PM
  2. Thermsl overload on pump
    By Ford2001 in forum Pumps and Tanks Well Forum & Blog
    Replies: 5
    Last Post: 10-14-2009, 06:22 PM
  3. Problems with pump -38F last night
    By MaryBC in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 01-17-2009, 04:24 PM
  4. sprinklers tripping well pump
    By brett14 in forum Irrigation / Sprinkler Forum
    Replies: 6
    Last Post: 08-20-2008, 10:22 AM
  5. Well pump breaker tripping
    By Warren in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 10-23-2005, 08:32 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •