Aprilaire 600A won't turn on

Users who are viewing this thread

Mortal798

New Member
Messages
24
Reaction score
0
Points
0
Location
Pinckney, MI
Hi everybody,

I have an Aprilaire 600A, and just like the title says - it won't turn on. I have 24vAC at the 'R' and 'C' terminals in the controller. The water solenoid is hooked up to 'H' terminals. The outdoor temp sensor is hooked up to 'ODT.' And the unit is set up to use the call for heat from the t-stat to detect blower operation, so 'W/G' on the Aprilaire controller is hooked up to 'W' on the furnace board and 'Cf' on the controller is hooked up to Common on the furnace.

Does it sound like my connections are correct? It won't even light up in 'Test/Reset' mode. Any ideas? Thanks in advance!
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The solonoids don't last forever...you can just replace that, if it's the problem. If it has 24vac across the input to the solonoid, but it hasn't turned on, it's probably that.
 

Mortal798

New Member
Messages
24
Reaction score
0
Points
0
Location
Pinckney, MI
Is that a new install ?

Did it ever work ?

It used to work, I turned it off for the summer. Then I removed the old furnace and replaced it. Once I reconnected the 600A, it wouldn't turn on. I have 24vAC at the controller, but the display doesn't light up - and it won't even go into test mode. I think I may have a bad controller.

The furnace works like a million bucks, just that d#$* humidifier won't come on.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Hi everybody,

I have an Aprilaire 600A, and just like the title says - it won't turn on. I have 24vAC at the 'R' and 'C' terminals in the controller. The water solenoid is hooked up to 'H' terminals. The outdoor temp sensor is hooked up to 'ODT.' And the unit is set up to use the call for heat from the t-stat to detect blower operation, so 'W/G' on the Aprilaire controller is hooked up to 'W' on the furnace board and 'Cf' on the controller is hooked up to Common on the furnace.

Does it sound like my connections are correct? It won't even light up in 'Test/Reset' mode. Any ideas? Thanks in advance!

The 2 H output terminals should have the 24VAC always-on transformer output winding is series with the solenoid,
connected to them.

Measuring from terminal H - H You should see 24VAC when the unit is not calling for humidity.
 

Mortal798

New Member
Messages
24
Reaction score
0
Points
0
Location
Pinckney, MI
The 2 H output terminals should have the 24VAC always-on transformer output winding is series with the solenoid,
connected to them.

Measuring from terminal H - H You should see 24VAC when the unit is not calling for humidity.

Yes, and when the solenoid comes on all the voltage should drop. The solenoid coming on isn't the problem (well, it may be a problem later...), the controller doesn't come on to tell the solenoid to come on. The controller doesn't even light up in test mode.
 