Can the tub drain use the DWV 3" vent? The distance between the tub and the DWV 3" vertical part is less then 15". Or, it has to vent using its own 1.5" vent, and then the 1.5" vent would merge with the 3" vent in the attic?

Thanks,
DWV Diagram.jpg
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
You can't run a toilet down a tub vent in Seattle, or anywhere.

You will need to run a 1.5" vent between the tub p-trap and the stack and then either go through the roof, or revent at 42" above the floor.