yep, boiler is reaching set temperature probably 180 degrees, then shuts down, circ pump will continue to circulate until room thermostat setpoint is reached, in the mean time when the boiler water temperature drops to the set temperature probably around 170 degrees, the boiler will fire up agian and run until the 1800 degree temperature is reached, hopefully your zone is not configured in such a short loop that the boiler will short cycle meaning go on go off in a short period of time, or your temperature set pointys are so close together that this could happen, sounds like your system is operating like it was designed to do, is it a wonderful thing