Thread: 15 amp and 20 amp circuits in same box

Hybrid View

  1. #1
    DIY Junior Member LHO's Avatar
    Join Date
    Sep 2011
    Location
    Washington
    Posts
    24

    Default 15 amp and 20 amp circuits in same box

    I have added a partition wall in an existing space (next to kitchen). I will be adding one outlet extending the existing 20 amp circuit. Also, I want to have one of these outlets switched with the overhead light circuit. I am wondering if there is a problem with cutting the "hot" tab on the side of the receptacle and having the top outlet switched 15 amp, the bottom 20 amp? My concern would be if someone plugged in a surge protector (like below) or other device that gangs the upper and lower outlets. (I don't plan to do this here, but I use two such devices in other rooms.) If the two circuits are on opposite sides of the phase it could get ugly if one of these is plugged in.
    Name:  89-010.jpg
Views: 480
Size:  13.5 KB

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,227

    Default

    But nothing would be wrong with installing a second receptacle on the 15 amp circuit right beside or above or below the 20 amp circuit.

    If you split one receptacle then there is some other issues other than the one you posted that would need to be addressed so do as I suggested for simplicity

  3. #3
    DIY Junior Member LHO's Avatar
    Join Date
    Sep 2011
    Location
    Washington
    Posts
    24

    Default

    I could put two duplex recepticals -- I presume that I can put them in the same box (yes, I know, connect all neutrals and grounds).

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,227

    Default

    connect all grounds yes

    each neutral goes with its own circuit so do not connect all neutrals

  5. #5
    DIY Junior Member LHO's Avatar
    Join Date
    Sep 2011
    Location
    Washington
    Posts
    24

    Default

    Quote Originally Posted by jwelectric View Post
    connect all grounds yes

    each neutral goes with its own circuit so do not connect all neutrals
    Just so I understand -- Are the neutrals not connected because of the different amperage of the circuits? I ask this because several of the switch boxes have switches from different 15 amp circuits. In this case the neutrals are all connected.

  6. #6
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    272

    Default

    Quote Originally Posted by LHO View Post
    Just so I understand -- Are the neutrals not connected because of the different amperage of the circuits? I ask this because several of the switch boxes have switches from different 15 amp circuits. In this case the neutrals are all connected.
    The neutrals from different circuits should not intermingle. The current that leaves the panel on circuit A should return on wiring associated with circuit A only, not circuit B or C or any other.

  7. #7
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,317

    Default

    Quote Originally Posted by LHO View Post
    ... having the top outlet switched 15 amp, the bottom 20 amp?
    As I understand things, either would still only be a 15A outlet as far as its actual rating is concerned unless the outlet was specifically configured/designed/engineered for 20A (with one horizontal blade, I think) in the first place. In other words, multiple 15A outlets are typically used in 20A circuits.

    Quote Originally Posted by LHO View Post
    My concern would be if someone plugged in a surge protector (like below) or other device that gangs the upper and lower outlets.
    I have never seen one of those multipliers ever gang the uppers and lowers together (although that might not be true of an actual surge-protecting multiplier). In fact, I occasionally use one of them on the end of an extension cord and have never found the unused blades on the back energized. So then, the upper and lower parts of the multiplier would still act just like their places of actual connection whether or not the upper and lower were separated at the wall receptacle.
    Last edited by leejosepho; 10-24-2011 at 09:50 AM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  8. #8
    DIY Junior Member LHO's Avatar
    Join Date
    Sep 2011
    Location
    Washington
    Posts
    24

    Default

    Quote Originally Posted by leejosepho View Post
    As I understand things, either would still only be a 15A outlet as far as its actual rating is concerned unless the outlet was specifically configured/designed/engineered for 20A (with one horizontal blade, I think) in the first place. In other words, multiple 15A outlets are typically used in 20A circuits.


    I have never seen one of those multipliers ever gang the uppers and lowers together (although that might not be true of an actual surge-protecting multiplier). In fact, I occasionally use one of them on the end of an extension cord and have never found the unused blades on the back energized. So then, the upper and lower parts of the multiplier would still act just like their places of actual connection whether or not the upper and lower were separated at the wall receptacle.
    It's not the outlet that would be 20 amp, it's the circuit and of course, the 20 amp circuit has #12 wire.

    I did get out a multiplier and a surge protector multiplier. You are right the top and bottom blades are not connected.

Similar Threads

  1. Bonding when 2 circuits in one box?
    By jch in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 03-30-2011, 02:42 AM
  2. two circuits in one box?
    By tregg in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 07-13-2010, 06:18 PM
  3. new kitchen circuits
    By wallygater in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 10-20-2009, 06:43 PM
  4. combining circuits
    By beekerc in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 03-13-2009, 02:19 PM
  5. New Kitchen Circuits Using 12-3
    By DrummerDad in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 07-25-2007, 10:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •