    Hello,

    Could any of you help me with setting this thing (outdoor reset) up properly? People on this site were a real good help last time I had questions, and I thank all of you for your time.


  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    I would need to know which model you have or a photo
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Junior Member GregoryR's Avatar
    Join Date
    Jul 2011
    Location
    Maine, USA
    Posts
    21

    Default



    Uploaded with ImageShack.us

    I had tried to upload one earlier, but I think it was too large. This should work.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    Set the slide switch to mod and turn the dial to 160 to start. You're up here in Maine with me so, when it gets damn cold out, if the house won't heat, turn the dial up 20 degrees until it will. You can also try going lower if the house is heating ok. The dial is what sets the temperature differential between outside temp and boiler supply temp, adjusted for degree days. I found that 160 to 180 seems to work pretty good around here.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    DIY Junior Member GregoryR's Avatar
    Join Date
    Jul 2011
    Location
    Maine, USA
    Posts
    21

    Default

    Quote Originally Posted by Tom Sawyer View Post
    Set the slide switch to mod and turn the dial to 160 to start. You're up here in Maine with me so, when it gets damn cold out, if the house won't heat, turn the dial up 20 degrees until it will. You can also try going lower if the house is heating ok. The dial is what sets the temperature differential between outside temp and boiler supply temp, adjusted for degree days. I found that 160 to 180 seems to work pretty good around here.

    Done and done, thanks so much. Hopefully we'll see some savings now that this thing is actually doing its job.

Similar Threads

  1. Fleck 5600SE settings
    By burleymike in forum Water Softener Forum, problems, installation and reviews
    Replies: 15
    Last Post: 09-17-2011, 04:58 AM
  2. Water Softener settings
    By OhioTurner in forum Water Softener Forum, problems, installation and reviews
    Replies: 4
    Last Post: 07-31-2011, 02:46 PM
  3. Culligan MK 50 programming settings
    By Outhouse in forum Water Softener Forum, problems, installation and reviews
    Replies: 2
    Last Post: 08-08-2010, 07:56 PM
  4. Clack WS1 EE settings
    By mgssrs in forum Water Softener Forum, problems, installation and reviews
    Replies: 20
    Last Post: 03-06-2010, 07:19 AM
  5. Proper Aquastat Settings
    By Backglass in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 11-12-2007, 06:53 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •