Replacing the aquastat has no effect on the zone valves at all. The L8148 has two terminals ( T T ) that call the burner and circulator. I'm not sure what you have for zone valves but in any case there will be two wires or terminals from the zone valves that switch TT. These should be wired in parallel to TT on the 8148
You can find wiring diagrams for pretty much anything old or new at www.taco-hvac.com
You could have saved yourself some money by leaving the 8124 and just pulling and capping the blue wire which disables the low limit function. Oh well, live and learn