    Default Need to break vacum in water softener drain line

    have a 1/2" pex drain line running outside as I can't run it into my septic system anymore.......I installed a Watts N36 vacuum breaker at the highest point to allow all the water to drain and eliminate any freezing problems. During regeneration the valve disk flutters making a moaning/groaning sound. Any ideas? Drain is under house pressure when it runs....

  2. #2
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    The 1/2" PEX has a smaller ID than 1/2" PE drain line so you are reducing flow to drain and that is not a good idea because the gpm flow rate is already flow controlled in the control valve. Most residential softners require a 1/2" ID drain as a minimum. If you have to or want to use PEX, use 3/4".

    That may or may not be the cause of the abnormal noise you hear.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    How long is the run of pex? Where along the run is this vacuum breaker? Change out the rest of the run after the vacuum breaker to larger pipe provided you can have enough standpipe to assure it cannot backup and overflow. An AAV on the bigger drain pipe should be quieter.

  4. #4
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default What it looks like

    6' from the softener to the vacuum break which is along the ceiling so make it a 3' rise.....then it runs downhill to a dry well outside of the house less than 30 feet......the drain hose from the softener is 1/2" matchs the pex........the vacuum breaker is attached via a tee with 3/4 pex. connection running vertically

  5. #5
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default Possible answer from another forum

    A response to another similar question about drains freezing from water held by a vacuum lock stated that if the end of the drain line is open then the water should drain back to the highest point in the drain line which is in my floor joists.......so my vacuum breaker was actually a waste of money.............does this make sense??

  6. #6
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    Yes.

    No breaker is needed as long as water can flow freely out the end of the drain line, which means no freezing of a pool of water on the end of the drain line.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  7. #7
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default Case closed

    Thanx for the help.........so much for dealing with the pros at my plumbing supply house. at least my money will keep them in business..............

  8. #8
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default case reopened

    i think I still need a vacuum break as the drain line drips with the leftover water....i tested the other side of the loop to see if the tank valves were leaking and no dripping..so I'm guessing there is still some water left in the drain that is held by a vacuum and is slowly weeping out.....the side that i tested had no vacuum and drained completely. so i'm back looking for some type of vacuum breaker other then the n36 unit i tried....

  9. #9
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Replace the outside piping with larger pipe and deploy an air-gap. That is how I deal with mine.

  10. #10
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    Quote Originally Posted by smithwd View Post
    i think I still need a vacuum break as the drain line drips with the leftover water....i tested the other side of the loop to see if the tank valves were leaking and no dripping..so I'm guessing there is still some water left in the drain that is held by a vacuum and is slowly weeping out.....the side that i tested had no vacuum and drained completely. so i'm back looking for some type of vacuum breaker other then the n36 unit i tried....
    Unless you have a leak, the dripping will quit shortly after regneration.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  11. #11
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by smithwd View Post
    A response to another similar question about drains freezing from water held by a vacuum lock stated that if the end of the drain line is open then the water should drain back to the highest point in the drain line which is in my floor joists.......so my vacuum breaker was actually a waste of money.............does this make sense??
    With 1/2 pex, the capillary action could trap water unless it was perfectly pitched. A larger pipe such as 1 - 1/2" or 2" PVC properly pitched should drain even without an AAV. Of course, when running buried pipe, ground swelling or settling can create sags or humps that trap water. The larger the pipe the less affected they are by sags or humps.

  12. #12
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default no leaks

    i tested for leaks at the softeners just to make sure.........i still think that some water is left in the drain near the high point and that's my source of dripping until its gone.........I haven't found too many Vacuum breakers like the watts N36 that might fit................................

    before the drain exits the house it has a 15' flat run along the wall........the high point is 3 feet above that.....possible some water left in that..

    is there a "breather" available that would add air but not allow the water to leak out...say install it on the top of a tee??
    Last edited by smithwd; 10-21-2011 at 06:23 AM.

  13. #13
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default bright idea....

    between the highest point of the drain and the exit level i'll put a trap .(extend the drain line to the floor then bring it back up.....that should collect any exess water from the high point...

  14. #14
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by smithwd View Post
    between the highest point of the drain and the exit level i'll put a trap .(extend the drain line to the floor then bring it back up.....that should collect any exess water from the high point...
    With a contiguous pipe without an air gap, it would be like holding your finger on the top of a straw. The vacuum and capillary action conspire to keep the water in the straw.

  15. #15
    DIY Junior Member smithwd's Avatar
    Join Date
    Dec 2009
    Location
    Marlborough, CT
    Posts
    17

    Default final resolution

    I think I'll use the tee at the highest point of the drain and run the third leg into the washing machine drain as a breather...........if the outside line freezes then it goes into the septic as a backup...voila.....

Similar Threads

  1. Constant Water flow through water softener drain line
    By Dale M. in forum Water Softener Forum, problems, installation and reviews
    Replies: 6
    Last Post: 10-23-2011, 02:13 PM
  2. Sewer line break in rubble-filled crawl space
    By neverenoughtools in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-21-2008, 11:57 AM
  3. Connect a new line to a water softener
    By marky in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-28-2008, 02:07 PM
  4. location of drain line for water softener
    By dony45 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 07-14-2008, 07:42 AM
  5. main water line break
    By flabbb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 09-17-2007, 12:11 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •