    I'm installing a new water heater.. 240V, 4500W, so that is 18.75 amps..so I need a double 20 amp circuit? I guess using the existing double 30A would be to much..(.Hmm just answered that question by looking at the other blog..150% over 18.75A is 28.125A and the next higher breaker is 30A so I'm good)....
    I would also like to wire the heater to the existing dryer plug for ease of moving the tank, is it OK to use a dryer plug and wires of the correct gauge or should I really use metal conduit?
    Last edited by LOKI48; 10-14-2011 at 11:41 AM. Reason: found part of answer

  2. #2
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    stay with a 30 or 25 amp breaker. Since a heater is not defined as portable, its probably "illegal" though I see no safety issues. Dryers only get moved every 10 years anyway.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    In this area, the heater MUST be connected to the wall with a wire enclosed in a metal sheath, i.e., NO bare Romex or "line cord".
    Licensed residential and commercial plumber

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    A 3 pole dryer receptacle would NOT be at all acceptable for a water heater. It has 2 hots and a neutral..no ground. It is completely unacceptable to use the neutral to ground the water heater. Back in the day, that was OK for a dryer, but not a good idea and no longer allowed on new circuits.
    A 4 prong dryer receptacle would in theory work...2 hots , neutral, ground. But that is not the correct receptacle for a water heater circuit. You would really want to use a regular NEMA 6-30, IF your inspector allows a plug at all.

    I wonder about the advisability of using a plug a the disconect means for a water heater, since you could easily indavertantly pull the plug under load....not a good idea.


    A 20 amp circuit is probably not correct for 4500 watts. But 25 amps would be. Since 25 amp breakers are not common, a 30 amp is usually used.

  5. #5
    DIY Junior Member Amish Electrician's Avatar
    Join Date
    Oct 2011
    Location
    Arkansas
    Posts
    17

    Default

    The water heater should be on a 30-amp circuit with #10 wires, all the way to the unit.

    Where you come out of the wall, you should have a disconnect switch. One of the $12 disconnects they sell for use with air conditioners will work fine.

    Unless the heater is small (5 gallon or less), it's not allowed to have a cord & plug connection in the latest electric code. I may not like this, but that's the rule. So, your connection between the disconnect and the heater will probably use "MC," which has wires wrapped in a metal sheath. The length you use should have four wires in it. You'll need the black, the red, and the green. The white will not be used. The 'home stores" either will cut it to length, or sell you a 25-ft. roll.

Similar Threads

  1. Question? Will a Energy efficient dryer cost more or less then a Gas dryer
    By 87vertgt in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 09-15-2011, 05:37 PM
  2. Is drain acceptable?
    By 20rose in forum Toilet Forum discussions
    Replies: 1
    Last Post: 06-09-2010, 07:33 AM
  3. To plug or not to plug into a GFCI outlet
    By DIY in forum Electrical Forum discussion & Blog
    Replies: 26
    Last Post: 04-15-2009, 04:13 PM
  4. Can I use dryer plug for my steam generator?
    By mtls in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 10-21-2007, 01:19 PM