    With the use of a regular retention tank, chlorine requires a minimum of 20 minutes contact time and 30 minutes is a better goal.

    Chlorine is heavier than water and while setting in water will fall to the bottom of a solution tank unless the solution is constantly being stirred/mixed 24/7. Without stirring/mixing the solution tank pickup tube will be picking up the strongest chlorine solution from the bottom of the tank and the solution being used/injected will constantly be reducing in strength until the next time new solution is added to the solution tank.

    That makes proper retention time more critical and why maintaining a free chlorine residual of .2 to 1.5 ppm is a must. Free chlorine is different than total chlorine. The free chlorine should be tested after the retention tank and not from the bottom of a retention tank.

    Pressure tanks of any kind should not be used for chlorine retention.

    The best retention tank I've ever seen... I sold a lot of them over many years with only two problems; one an owner broken bottom drain elbow and a broken during shipment distributor tube.

    http://www.apwinc.com/retention_tank.html
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  2. #32
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    Quote Originally Posted by Gary Slusser View Post
    Pressure tanks of any kind should not be used for chlorine retention.
    By a "pressure tank" I have to assume you mean either a captive air or hydro-pneumatic tank. What I linked to is neither although it is still considered a pressure vessel.

  3. #33
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    Both of those are good links. I like fiberglass or plastic tanks instead of metal when using chlorine.

    A captive air or hydro-pneumatic pressure tank needs 75% to 80% air. A retention tank has no air in it. So a 100 gallon pressure tank only holds 25 gallons of water, where a 100 gallon retention tank holds 100 gallons of water. Both have to be capable of handling pressure, but without any air, the retention tank won’t give any drawdown. Using a 100 gallon retention tank in front of a 100 gallon pressure tank would actually give you about 125 gallons of retention space.

    Like I said earlier, I have used a CSV and a 4 gallon pressure tank with a variable flow chlorinator. I just used enough 12” pipe to hold about 100 gallons of water before I reduced it back down to 1 ” pipe and went into the house. That way my retention “tank/pipe” is underground and didn’t take up any room in the pump house.

  4. #34
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Name:  ct-40.jpg
Views: 165
Size:  33.4 KB

    Any opinion, good or bad on the CT-80? Many of our customers use it, and the new design is a huge improvement for the connections. I have not heard any complaints, but any feedback would be appreciated.

  5. #35
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by LLigetfa View Post
    By a "pressure tank" I have to assume you mean either a captive air or hydro-pneumatic tank. What I linked to is neither although it is still considered a pressure vessel.
    Reading their description it is either, and its also air over water with their air volume control.

    It is also a retention tank if you plumb in the bottom and out the top.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  6. #36
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by valveman View Post
    Like I said earlier, I have used a CSV and a 4 gallon pressure tank with a variable flow chlorinator. I just used enough 12” pipe to hold about 100 gallons of water before I reduced it back down to 1 ” pipe and went into the house. That way my retention “tank/pipe” is underground and didn’t take up any room in the pump house.
    A potential problem is if you are using chlorine for iron. I've seen raw water with iron in it cause 1" and 1.25" PE pipe to block up with rust to no more than a 3/8" hole in it. Your 12" piece could become a sediment trap and the sediment being flushed out can cling to the inside of the smaller pipe.

    Nothing else you'd use chlorine for would do that.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  7. #37
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    Quote Originally Posted by Gary Slusser View Post
    A potential problem is if you are using chlorine for iron. I've seen raw water with iron in it cause 1" and 1.25" PE pipe to block up with rust to no more than a 3/8" hole in it. Your 12" piece could become a sediment trap and the sediment being flushed out can cling to the inside of the smaller pipe.

    Nothing else you'd use chlorine for would do that.
    Thanks for that tip. I will remember that.

  8. #38
    DIY Junior Member hcw3's Avatar
    Join Date
    Oct 2011
    Location
    Los Angeles, CA
    Posts
    26

    Default

    This discussion is educational...

    Help me to understand this:

    Regarding the chlorine injector, when running on a standard system (non-CSV). Doesn't the flow rate vary in a standard pump/pressure-tank system, depending on the pressure developing as the tank reaches 'full'?

    IOW doesn't a 12GPM pump perhaps start out in its ON cycle at 12GPM flow and, as the PSI of the system increases, slow to some lower GPM?

    In which case the chlorine injector needs to be adjusted to the average GPM between start and stop?

    In that case how do we know the actual GPM in order to set the chlorine injector correctly?

  9. #39
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    Ja, pump GPM runs on a curve, so you just SWAG it. The pump curve can vary also with changing water levels.

  10. #40
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by hcw3 View Post
    This discussion is educational...

    Help me to understand this:

    Regarding the chlorine injector, when running on a standard system (non-CSV). Doesn't the flow rate vary in a standard pump/pressure-tank system, depending on the pressure developing as the tank reaches 'full'?

    IOW doesn't a 12GPM pump perhaps start out in its ON cycle at 12GPM flow and, as the PSI of the system increases, slow to some lower GPM?

    In which case the chlorine injector needs to be adjusted to the average GPM between start and stop?

    In that case how do we know the actual GPM in order to set the chlorine injector correctly?
    The solution feeders I used to use had adjustments on the pump that set the volume of solution to be injected and once set (based on free chlorine of .2-1.5 ppm) you left it alone unless your free chlorine residual test showed more or less than .2-1.5 ppm. The free chlorine test is done on water from a sample port (spigot) installed just after the retention tank.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  11. #41
    DIY Junior Member hcw3's Avatar
    Join Date
    Oct 2011
    Location
    Los Angeles, CA
    Posts
    26

    Default

    It's good to know at what point to test the free chlorine. I made the mistake of testing after the carbon filter.

    I have tested immediately after the contact tank, and it's 'off the scale'; my scale only goes to 3ppm.

    The feed-pump that was installed is adjustable, but I've adjusted it to the minimum, and I've diluted the solution to 1:6.

    According to my calculations, pumping @ 5.4GPM, with the Stingray feeder set at the minimum or approx. 10gal/day, the water going into the contact tank is @ 11ppm chlorine.

    Should I simply continue trying lower concentrations, using trial and error, to obtain the lower free-chlorine ppm needed coming out of the contact tank?
    Last edited by hcw3; 04-04-2012 at 07:56 PM.

  12. #42
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Continue to lower your concentrations. A gallon of chlorox bleach is 65000 PPM.

  13. #43
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    Without a CSV the pump performs according to the curve. So a 10 GPM pump might start out pumping 12 GPM at 40 PSI, and by the time it shuts off at 60 PSI will be down to 10 GPM flow. So that is an average of 11 GPM as far as your injector pump is concerned.

  14. #44
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,946

    Default

    Yes........................
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  15. #45
    DIY Junior Member hcw3's Avatar
    Join Date
    Oct 2011
    Location
    Los Angeles, CA
    Posts
    26

    Default

    Ok, that figures. Thanks.

    About this Chemilizer injection pump that ditttohead mentioned...

    Quote Originally Posted by ditttohead View Post
    Check out the Chemilizer HN55 pump, it uses the water flow to pump, and it has a set ratio. it is approximately $200 plus a chemical storage tank. The most common is 128-1 ratio. For every 128 gallons of water the house uses, it will pump 1 gallon from the chemical tank. Mixing a gallon of bleach with 35-45 gallons should get you into the 5-10 PPM range.
    At this time I have only a 5 gal solution tank. Is there any reason I shouldn't use the Chemilizer HN55 with 1:500 injection? I figure I could then use approx. 1:12 clorox to water to give me around 10ppm, and I'd only need to refill the 5g tank about once a month. Any problem with this higher concentration at a 1:500 injection?

    Has anyone here got any experience with the Chemilizer? In their docs they suggest that the injector needs to be installed before the pressure switch. I'd like to have a branch coming off the line before the injector, to connect my non-chlorinated garden-hose, and it would be tidier to install it all after the pressure tank.

    Another question, the Chemilizer is installed with 3/4" hose connections. I have 1" pipe from the pressure tank, which goes all the way through the softener system. Will reducing to 3/4", and then expanding back to 1" here at the injector, cause problems with noise or otherwise? Does this kind of 'compression and decompression' make trouble?

    Thanks for all the help with this guys, it sure is nice to have knowledgeable input, trying to get this system right.

Similar Threads

  1. Carbon filter before or after water softener
    By Bloom80 in forum Water Softener Forum, problems, installation and reviews
    Replies: 7
    Last Post: 09-29-2011, 07:52 AM
  2. Rebedding a Culligan Carbon Filter / General Water Treatment System Questions
    By scrupul0us in forum Water Softener Forum, problems, installation and reviews
    Replies: 8
    Last Post: 09-11-2011, 08:23 AM
  3. seeking fridge filter without carbon
    By jeremytl in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 06-15-2011, 09:36 PM
  4. Carbon tank not working
    By Mrs. Smith in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 11-07-2008, 07:47 AM
  5. Whole house carbon filter installation with softener
    By dabiz7 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 02-27-2008, 03:36 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •