    I'm getting ready to run wiring for five outdoor receptacle and am wondering how far off the ground they must be?

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    That all depends on how high you want them mounted. There is nothing that mandates how high.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    It might be prudent to keep them out of the 'splash' zone (the area where rainfall splashes back up after running off the roof) and above the normal snow load (probably not a consideration in warmer states). Then, I don't like to have to lean over too far, either!
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Junior Member itr674's Avatar
    Join Date
    Dec 2009
    Location
    NC
    Posts
    14

    Default

    Quote Originally Posted by jwelectric View Post
    That all depends on how high you want them mounted. There is nothing that mandates how high.
    thanks, I think I will plan on 24" above mulch then...

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by itr674 View Post
    thanks, I think I will plan on 24" above mulch then...
    18 to 24 inches is what just about everybody around here mounts them. Be sure to mount them so they aren’t easily broke off. I use a 4x4 post installed at least 24 to 36 inches deep to hold them in place.

    Also remember that PVC boxes and pipe will fracture easily when cold. If using PVC I highly recommend using 80 instead of 40 and nothing smaller than inch for its strength.

  6. #6

    Default

    There's no minimum height requirement for recepticals in residential applications. The only requirements are that for each dwelling at grade level there is one receptical accessible not more than 6.5" at the front and back of the dwelling.
    Mountain Eagle
    DIY - sure I'll try anything

Similar Threads

  1. No Ground for Outdoor Lights
    By hormy_83 in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 09-16-2009, 06:25 AM
  2. Single receptacle to a double receptacle
    By beeger11 in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 05-02-2009, 06:01 PM
  3. What would magnetize a receptacle?
    By Taylor in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 10-06-2008, 01:39 PM
  4. Changing receptacle
    By tlong_66 in forum Electrical Forum discussion & Blog
    Replies: 18
    Last Post: 04-09-2008, 07:16 PM
  5. How to tap off a receptacle
    By jar546 in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 02-26-2008, 07:03 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •