    I'm adding some shoplights to my garage and am running EMT conduit from a new switch to the fixtures. Because of the switch and fixture locations, the most efficient plan is to run the conduit up the wall from the switch to a 4" box on the ceiling and then branch in 2 directions to the fixtures. Is this branch OK? Somewhere in the back of my mind I remember seeing something about not branching like this, that the run has to be continous from the switch to each fixture in a daisy chain. I could do the single run but it would mean more conduit and more wire.
    Thanks.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Sounds like a plan to me

  3. #3
    DIY Junior Member Al G.'s Avatar
    Join Date
    Jul 2009
    Location
    Woodbridge, VA
    Posts
    17

    Default

    The switch will control receptacles in the ceiling for plug-in shoplights. Do those receptacles need to be GFCI protected? The switch will be in a 2-gang box with a GFCI receptacle. If those in the ceiling need to be protected can I put the switch in the hot conductor coming off the load side of the GFCI?

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; seeing something about not branching like this, that the run has to be continous from the switch to each fixture in a daisy chain

    That would be VERY cumbersome in an installation where the switch was positioned at the center of the string of lights. At one time, as long as the lights were plugged into a "single device receptacle" so it could NOT be used for an extension cord, for example, it would not have to be GFCI protected.
    Licensed residential and commercial plumber

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    Everything in a garage should be GFCI protected.

    If it is wired properly, it does not matter how you go about it. You can use a GFCI breaker, one GFCI receptacle feeding the rest of the garage, or all GFCI receptacles.

    Also worth mentioning is that the EMT is an approved grounding conductor, and all metal boxes with devices must be pig-tailed to a proper machine threaded ground screw installed in the box.

Similar Threads

  1. Circuit Breaker Question
    By eric3872 in forum Electrical Forum discussion & Blog
    Replies: 17
    Last Post: 07-02-2011, 06:48 PM
  2. circuit breaker question
    By floridian in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 01-30-2009, 02:59 PM
  3. Bathroom wiring circuit question
    By docpops in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-02-2008, 03:20 PM
  4. Stove circuit sleeve question
    By Ian Gills in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 12-07-2007, 07:33 AM
  5. Subpanel Circuit Question
    By mln in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 09-20-2007, 06:45 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •