Does this wet vent meet code?

Users who are viewing this thread

Pghsebring

DIY Member
Messages
107
Reaction score
2
Points
18
Location
Florida
Well, i'm just about finished with my main bathroom (other thread), now it's about time to tackle the basement bathroom. I found this picture on this site:

attachment.php


Now, that vent is going up 2 stories, and into the attic. I want to know if i should run it over to the 2" vent from my other full bathroom (ie, join them in attic) and send them both out the existing hole in the roof (one 2" vent), or if i should punch another hole in the roof, and run each out a separate hole? If the answer is "separate holes," that new vent is running up through an exterior wall, and if i went straight out the roof, would be pretty close to the eave/edge of roof. Is this ok? Is there a required distance from the edge of the roof for a vent penetration? If it must be moved/offset, what is the best way to do this - a couple of 90s? Supports needed in any way?

Thanks in advance.
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
The first drawing show the toilet downstream.

Then you changed the drawing to have the toilet upstream of everything. Whenever the toilet is flushed, it will siphon the shower trap. Where the toilet is placed in the system is "very" important.

2nd drawing is wrong, wrong, wrong.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
You should ask your plumbing inspector. Though Terry has a valid point, in a lot of places that are under the IPC, we can now wet vent in any order so technically the 2nd drawing may be ok. At least it is here.
 

Gary in NJ

Member
Messages
119
Reaction score
0
Points
16
Location
NJ
Is there any way that you can vent behind the WC and tie it back (up and over to) the existing vent?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I am not an engineer...but I suspect that in todays world of 1.6 GPF, soon to be 1.28 GPF, it may not be such a big deal to flush a toilet past a tub. But your inspector will have the final say!
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
Except that when toilets were five gallons, the water went by very slowly.
With the 1.28, they have sped up the flush, and now the water will skip across a fixture cross and push water out of an opposing bowl. That never, ever happened with the five gallon bowls. But it does with the new 1.28 gallon bowls. If anything, the plumbing needs to be much better for the new bowls. It's sudden and deadly.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
I wondered and then argued the point when they changed the rule but my argument fell of deaf ears. Apparently the boys that write the code know better than us dumb plumbers. Whenever possible I have always favored having an upstream fixture wash the toilet drain but again, nobody seems to see the value in that anymore. I still do it when possible though. It saves a lot of return calls.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
You should ask your plumbing inspector...
Exactly, and then don't argue code with him/her.

There are two things in both pictures that my inspector would never allow. He made me add a vent for the shower, would not let me wet vent it. The other thing he never let me get away with is to Tee or elbow on the same horizontal plane. I had to use a combination of a rolled Y and rolled elbow to form a drop.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Well, the distance from trap to the wet vent comes into play but if the shower (and any other bath group fixtures) are within the prescribed distances than the inspector would have to approve it. Your Canadian code is a bit different though. If you use a rolled wye or combo on the horizontal then you negate the wet vent so yes, yo then need to individually bent the shower
 

Pghsebring

DIY Member
Messages
107
Reaction score
2
Points
18
Location
Florida
You should ask your plumbing inspector. Though Terry has a valid point, in a lot of places that are under the IPC, we can now wet vent in any order so technically the 2nd drawing may be ok. At least it is here.

2009 IPC here. So it may be allowed?
 

Pghsebring

DIY Member
Messages
107
Reaction score
2
Points
18
Location
Florida
Is there any way that you can vent behind the WC and tie it back (up and over to) the existing vent?

Let me look into that...but the main problem is the toilet is on the far side of the bathroom from where the drain line is.

...but even if i do, isn't the shower still downstream, and problem terry references still there?

Here's another question....is there any limit on the length of the arm for the WC? 8 ft for example?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The toilet flowing past the shower, (in UPC terminology it is a 'major fixture' over a 'minor' one), which is the problem. ANY time that occurs the 'minor' fixture must have its own independent vent to eliminate the problem. If the "code" does not require a vent for the toilet, then it also may not have a length restriction, because the two go together. The IPC is more concerned with inexpensive installation, so it allows many variations which the UPC does not.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
In the UPC code, the toilet must be vented within six feet.
It's simple to install plumbing for that bath that would pass a UPC inspection. Just vent the shower. It's not going to kill you to spend $10 more.
 