Thread: expansion tank connected to pressure release valve

  1. #1
    DIY Junior Member TeeDee's Avatar
    Join Date
    Oct 2011
    Location
    belleville, il
    Posts
    1

    Default expansion tank connected to pressure release valve

    As they would say on the radio, long time listener, first time caller.

    I'm installing a Peerless gas boiler (MI-04). It shows in the manual that I can hook up an air elimination device on the same pipe as the pressure release valve. Can I also connect the expansion tank to this pipe? I ask because this is the way is was installed in the house it was removed from. A 1 inch pipe that comes up for the top of the boiler to a T. The horizontal pipe off that T is the pressure release valve. The vertical pipe that continues extends 20 inches to another T. The pipe to the right of the T is the air vent and the pipe to the left of the T is the expansion tank. Is this okay? Thanks in advance. I will add photos if it helps...and if I can figure out how..
    Last edited by Terry; 10-12-2011 at 12:19 PM.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    Please add the photos. 800 pixels or less.

    The PRV needs to come off the main piping for the unit and so does the expansion tank. You need to make sure these are on the pressure side.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,938

    Default

    Yes you can as long as there are no valves between the expansion tank, the relief valve and the boiler itself
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  4. #4
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    285

    Default

    Careful here. The pressure relief valve (PRV) on any boiler and it's location are specified by the manufacturer. In general the relief valve is installed off a direct connection to the top of the boiler and nothing can be between the PRV and the boiler save pipe.
    There may be a tee off the top for an expansion tank but the boiler does not care where the expansion tank is, only the circulator worried about such things.

Similar Threads

  1. Water well tank- Minimum Pressure Release Valve
    By Keith Robinson in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 08-24-2011, 02:38 PM
  2. Rannai pressure release valve leaking
    By shawndh in forum Tankless Water Heater Forum
    Replies: 3
    Last Post: 05-15-2010, 05:45 PM
  3. Best location for Thermal Expansion Tank and Pressure Reducing valve?
    By bobwood in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-10-2008, 07:15 PM
  4. tank valve - momentary water release
    By lhoward145 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 01-19-2008, 07:45 AM
  5. Is this a pressure release valve?
    By craniac in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 05-12-2007, 08:08 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •