I am not suggesting, I am telling you that you can't wet vent through a bar sink, kitchen sink, laundry tray, washing machine etc, only bath group fixtures.
My local plumbing code does not make any mention of this restriction. Can you please elaborate?
From the code I'm working with:
"Wet vent means a soil-or-waste pipe that also serves as a vent pipe and extends from the most downstream wet-vented fixture connection to the most upstream fixture connection."
"2.5.2.1. Wet Venting
(See Appendix A.)
1) A soil-or-waste pipe may serve as a wet vent provided that
a) the hydraulic load is in accordance with Table 2.5.8.1.,
b) the number of wet-vented water closets does not exceed 2,
c) where 2 water closets are installed, they are connected at the same level by
means of a double sanitary T fitting if the vent pipe is vertical and by means
of a double Y fitting if the vent pipe is horizontal,
d) the water closets are installed downstream of all other fixtures,
e) trap arms and fixture drains connected to the wet vent do not exceed 2 inches
in size, except for connections from emergency floor drains in accordance with
Sentence 2.5.1.1.(3),
f) the total hydraulic load on the wet vent does not exceed the limits stated in
Table 2.5.8.1. when separately vented branches or fixture drains in the same
storey, having a total hydraulic load not greater than 2 fixture units, are
connected to the wet vent or a wet-vented water closet trap arm,
g) the hydraulic load of separately vented fixtures that drain into the wet
vent are not included when sizing the continuous vent that serves the wet vent,
h) where a wet vent extends through more than one storey, the total discharge
from any one storey above the first storey does not exceed 4 fixture units,
i) there is not more than one nominally horizontal offset in the wet vent, and
i) the offset does not exceed 1.2 m for pipes 2 inches or less
in size, or
ii) the offset does not exceed 2.5 m for pipes larger than 2 inches
in size,
j) the wet-vented portion is not reduced in size except for the portion that is
upstream of emergency floor drains in accordance with Sentence 2.5.1.1.(3),
and
k) the length of the wet vent is not limited."