Thread: SPRAGUE b-31R NATURAL GAS REGULATOR

  1. #1
    DIY Junior Member reevesjo's Avatar
    Join Date
    Oct 2011
    Location
    Indiana
    Posts
    2

    Default SPRAGUE b-31R NATURAL GAS REGULATOR

    Newbie here, but have a problem. Doing some re-piping on a nautral gas fired boiler in a radiant heating system my dad installed 50 years ago. I am fortunate to have a gas well on the property that produces 20 psi at the well. Just inside the home is this old, old Sprague regulator 3/4" NPT fittings. I want to replace it with 1" version. I am running new 1 1/4" polyethelene from the well to the house.
    1. Do I even need a pressure regulator with this low 20# pressure? There is plenty of volume. We never run out...yet.
    2. Is this Sprague the one to use?
    3. How do I set the pressures, with a psi gauge or manometer?

    The boiler is 140,000 input; 112,000 output
    40 gallon hot water heater
    kitchen gas range
    small space heater in one room

    Thanks for any advice, Joe

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    You have got to be kidding right?
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Appliances are designed for around 0.5 psi...20psi will damage things, and likely blow up the house.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    1 inch of water [4 C] = 0.036 pound/square inch

    Nat gas appliances typically run on 7in.wc
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    DIY Junior Member reevesjo's Avatar
    Join Date
    Oct 2011
    Location
    Indiana
    Posts
    2

    Default Dead serious, not kidding.

    Thanks Tom Sawyer. 7 inch water column is what I wanted to hear (or read). I can handle it with that info.
    Joe

    Quote Originally Posted by Tom Sawyer View Post
    1 inch of water [4 C] = 0.036 pound/square inch

    Nat gas appliances typically run on 7in.wc

Similar Threads

  1. Bad pressure regulator?
    By dabensys in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 05-28-2010, 05:53 AM
  2. How to choose a pressure regulator?
    By redsoxfan in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 12-20-2008, 03:31 PM
  3. Home water regulator???
    By Cybertrout in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 02-11-2008, 06:03 PM
  4. Natural gas regulator question
    By footer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 13
    Last Post: 12-30-2005, 07:39 PM
  5. watts regulator
    By eric in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-20-2005, 08:00 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •