Anyone use an angle finder to check for 1/4" per foot slope?

Users who are viewing this thread

JoshRountree

Member
Messages
53
Reaction score
0
Points
6
Location
West Jefferon, NC
Seems to me it would be way easier to check it with an angle finder instead of a 1" block attached to a 4 ft. level? A 1/4" block attached to a 1 foot level would work too, but the angle finder seems so easy?
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Plumbers are trained to use their torpedo levels and just crack the bubble !

In 30 plus years have never failed a inspection yet
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Another way would be to use a line level. That is a level with hooks on each end that hook over a stout cord. Drive stakes at each end of the run and measure the distance of the run. This will tell you how much fall is needed for that section. Now stretch the cord from one stake to the next with the high end on top of the beginning point When level is located, tie the cord off and measure down the stake the distance you have determined is needed for the slope.
 

JoshRountree

Member
Messages
53
Reaction score
0
Points
6
Location
West Jefferon, NC
What is your definition of an "angle finder"? There are many types of "slope/pitchlevels" to give pipes the proper grade.

http://www.digipas.com/DWL-280 Specs.html



anything to put on top of a pipe to see what angle it is.

BTW, the angle in degrees that I came up with for 1/4" per foot is 1.19348942 degrees, can anyone confirm or deny if that is right?

You'd just plop the digital level on the pipe, look for 1.19 degrees and you're good! The only drawback is it's hard to find one with a degree of accuracy better than 0.2, I'm sure it'd be at least as accurate as a 4 foot bubble level?
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
1/4" per foot is 2.0833 percent
.25 / 12.0
Code books say 2%

That looks like a nice level though.
I'm used to using a simple level and just looking at the bubble.
They last for years and years and don't need battery changes. But gadgets are cool too.
 
Last edited:

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
IF you are working with plastic pipe, it is seldom "straight", so your digital level or angle finder is only going to measure the grade of a 12" section of pipe, unless you "slide" it along the ENTIRE length of the pipe. A 4' level distributes the inaccuracy over a longer distance and is thereform more accurate.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
When I designed and built my house, I calculated the slope along with all the drops I needed for turned elbows etc. working backwards from the septic field and then worked off the drawings measuring to the level structure. The torpedo level was used more for confirmation. I calibrated the torpedo level by placing it on top of the 4 foot level.
 