    Default 240 2pole30amp breaker testing

    I am having some issues with a 2pole 30amp 240 breaker. It appears that I am not getting 240 volts at my outlet.
    I have a multimeter and when I check each pole I get 120 on each pole, but I don't get 240 when testing both poles.
    Any help would be appreciated.
    Thanks,
    Martin

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,681

    Default

    My guess is that it isn't a 240V breaker but rather a ganged 120V. How much space does it occupy in the breaker panel? A 240V breaker needs to be wide enough to span both legs.

  3. #3
    DIY Junior Member MartinE's Avatar
    Join Date
    Aug 2011
    Location
    Missouri
    Posts
    7

    Default

    It is a double wide breaker. It will not trip one breaker seperate like a ganged breaker.

  4. #4
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Bad connection at the breaker or a lost leg to the panel or the house are are possibilities. What other 240V circuits are in the house?

  5. #5
    DIY Junior Member MartinE's Avatar
    Join Date
    Aug 2011
    Location
    Missouri
    Posts
    7

    Default

    Quote Originally Posted by ActionDave View Post
    Bad connection at the breaker or a lost leg to the panel or the house are are possibilities. What other 240V circuits are in the house?
    I have checked and rechecked the connections. I have a hot water heater and a range that are each 2 Pole 30 amp breakers.
    I just added the dryer 2 Pole 30 amp breaker.

  6. #6
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Just one breaker panel in the house? Did you check voltage at the other 240V outlets?

  7. #7
    DIY Junior Member MartinE's Avatar
    Join Date
    Aug 2011
    Location
    Missouri
    Posts
    7

    Default

    Quote Originally Posted by ActionDave View Post
    Just one breaker panel in the house? Did you check voltage at the other 240V outlets?
    Yes, each one tests okay with 240 when testing both poles.
    The only thing that I can come up with is that the breaker is bad, but I don't understand why I get the 120v when testing each pole seperate.

  8. #8
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Either you have either lost one leg on the circuit in question (bad connection, bad breaker, broke wire)and the voltage is backfeeding through the other 240V circuits or you have both hots on the same phase.

  9. #9
    Engineer Furd's Avatar
    Join Date
    Jul 2007
    Location
    Wet side of Washington State
    Posts
    446

    Default

    Is this in a General Electric panel? One that takes half-slot breakers? If yes, then you need to move the circuit breaker over one slot.

    There are a couple of other panels that have this quirk but I don't remember the make.

  10. #10
    DIY Junior Member MartinE's Avatar
    Join Date
    Aug 2011
    Location
    Missouri
    Posts
    7

    Default

    Quote Originally Posted by Furd View Post
    Is this in a General Electric panel? One that takes half-slot breakers? If yes, then you need to move the circuit breaker over one slot.

    There are a couple of other panels that have this quirk but I don't remember the make.
    I had a three wire plug and wire on this breaker and had 240v at the plug.
    I switched it to a 4 wire and plug to match the dryer.
    Now I don't have the 240v.

    It's an old Panel with Federal Pacific thin Stab-Lok breakers.

  11. #11
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,772

    Default

    Quote Originally Posted by MartinE View Post
    Yes, each one tests okay with 240 when testing both poles.
    The only thing that I can come up with is that the breaker is bad, but I don't understand why I get the 120v when testing each pole seperate.
    That depends where you are measuring. If you measure from each hot leg to ground or the Neutral. You will measure 120 Volts. You said you replaced the receptacle with a 4 prong unit to match the bew Dryer's plug? Is your cable from the panel to the dryer receptacle 10/2 plus a ground or is it 10/3 plus ground. the proper cable should have a red, a black, a white and a ground wire either bare or green to properly connect the 4 prong receptacle, and at the panel end, the red and the black should each go to one phase of that 30 amp breaker. the white should connect to the bus strip with the other white (neutrals, and the ground should be connected to the ground bus. The ground and neutral buses are seperate, but may be connected together by a bolt in the panel. In any case, you first need to measure the voltage at that 30 amp breaker at each phase to make sure you have 120 volts to ground and 240 (or whatever your actual 2xx voltage is in your area) between the 2 phases. The breaker may be bad, but if it worked before with your old dryer, I am under the opinion from what you wrote so far, you may have wired something wrong at the new receptacle. Just my opinion, and you know what opinions are worth.

    I reread your posts and just noticed you installed the new breaker (was there one there before? Is the new breaker plugged onto both metal "stabs", one phase on each of the stabs?. My advice sticks: first measure at the breaker itself, if you have not already done so.
    Everybody else that has answered you is correct in what they said too, but we need to get all the details of what you did to figure out what is wrong. It is possible, but not very likely that the "new" breaker you installed is bad.
    Last edited by BobL43; 08-30-2011 at 08:13 AM.
    I am definitely not a pro plumber, but I am a pro crastinator

  12. #12
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    As already mentioned, on some panels, you can only get a 240-vac CB to work properly if it is in certain slots...you may need to move it up or down one slot. Also, some panels I've noticed may have the tabs to mount a CB in places beyond where the bus bars go...i.e., while they look like they can hold more breakers, they are not really designed to do so.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  13. #13
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by MartinE View Post
    I have checked and rechecked the connections. I have a hot water heater and a range that are each 2 Pole 30 amp breakers.
    I just added the dryer 2 Pole 30 amp breaker.
    Quote Originally Posted by MartinE View Post
    I had a three wire plug and wire on this breaker and had 240v at the plug.
    I switched it to a 4 wire and plug to match the dryer.
    Now I don't have the 240v.

    It's an old Panel with Federal Pacific thin Stab-Lok breakers.
    A little confused here. Which is it, added a breaker or used an existing breaker.
    Either way, I am going to say that you have both hots on the same phase. This is very easy to do on Federal panels.

  14. #14
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    FPE-stab-lok breaker are no longer made,it could be the breaker or the way the receptical was wire.
    Check this out, www.inspectapedia.com/fpe/fpetest.htm

  15. #15
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    here is a link from our grovenment that holds a little more salt
    http://www.cpsc.gov/CPSCPUB/PREREL/prhtml83/83008.html

Similar Threads

  1. Air Testing
    By nelsonba in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-16-2007, 09:12 PM
  2. PVB testing
    By ToolsRMe in forum Irrigation / Sprinkler Forum
    Replies: 8
    Last Post: 06-06-2007, 01:16 PM
  3. DWV testing and a thank you
    By Hazel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-06-2006, 07:01 PM
  4. Sprinkler Air Vacuum breaker vs Pressure vacuum breaker
    By Mike Pascutiu in forum Irrigation / Sprinkler Forum
    Replies: 15
    Last Post: 05-28-2005, 01:47 AM
  5. Sprinkler Air Vacuum breaker vs Pressure vacuum breaker
    By Mike Pascutiu in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 13
    Last Post: 05-27-2005, 08:28 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •