    Default Water Heater Gas Connection

    I'm back again with another gas WH replacement question regarding the gas connection to my (potentially) new WH. I've seen several pictures, videos, etc of making the connection from incoming gas line to the WH gas valve and noticed variations in how they're piped. The attachment shows the most common I've seen, top image, and also what my current connection looks like, bottom photo.

    My questions are basically;

    1) what's the difference
    2) is one preferred/recommended over the other

    My potentially new WH will be 40,000 BTU and my current is 32,000 BTU so I'm sure I'll need to make some sort of change but was curious as to the piping differences first.

    Thanks in advance.

    Name:  WHGasLine.jpg
Views: 978
Size:  39.2 KB

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    It depends on local code.
    In the West, they like to see flexible connectors. We have earthquakes.

    Some places that don't acknowledge the danger prefer solid connections. I would talk to your local plumbing inspector about it.

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Terry says it all. Local codes prevail. FWIW, I have 7 gas appliances in my home and all of them are connected with flex tubing. My water heater water lines are also flex tubes and all of my water using fixtures have flex connections.

  4. #4
    DIY Junior Member sjm133's Avatar
    Join Date
    Aug 2011
    Location
    Mobile, AL
    Posts
    14

    Default

    I guess the basis of my question was regarding that round doo-hickey in the line leading into the valve in the photo. What is it? The top image shows an option of flex line or solid line with the the drip leg and no round doo-hickey.

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    It looks like a high pressure line with pressure reducer.
    Is this an LP water heater?


  6. #6
    DIY Junior Member sjm133's Avatar
    Join Date
    Aug 2011
    Location
    Mobile, AL
    Posts
    14

    Default

    It's Natural Gas. That little silver plate on the top reads "Max Pressure 10 PSIG". Also, those yellow bands, one around vertical line and one on top of the doo-hickey, both read "2 PSIG GAS".

  7. #7
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    So yes, it's a reducer. That has to stay there.
    You can hard pipe from it, or use a flex. Since you already have soft copper coming in, that's like a flex line anyway.

  8. #8
    DIY Junior Member sjm133's Avatar
    Join Date
    Aug 2011
    Location
    Mobile, AL
    Posts
    14

    Default

    Excellent. Glad I asked. So as I mentioned at first, I'm looking at replacing my 32k BTU with a 40k. Will this affect any of this piping?

Similar Threads

  1. Help with electric heater connection!!
    By the_bosun_mate in forum Electrical Forum discussion & Blog
    Replies: 32
    Last Post: 12-01-2008, 12:31 PM
  2. Water heater connection leak
    By tonkin1983 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-07-2007, 04:59 PM
  3. Sink noise and HVAC heater....connection???
    By prollins1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 11-23-2006, 05:55 AM
  4. Flex or rigid connection to water heater
    By jonb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 10-18-2005, 07:39 AM
  5. Water meter to pvc connection??
    By Roshe in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 02-23-2005, 06:46 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •