Thread: Electrial Requirements for Hot Water Heater

Hybrid View

  1. #1
    DIY Junior Member safeire's Avatar
    Join Date
    Jun 2011
    Location
    Ohio
    Posts
    16

    Default Electrial Requirements for Hot Water Heater

    I just had an electrician check out my hot water tank because it has flipped the breaker since it was first installed. This gentleman is telling me I need to have a new line put in between the hot water tank and the panel. All he did was walk around the basement but never actually checked anything with any meters or other diagnostic tools. He is highly rated on Angie's list but it seems odd that putting a new hot water tank that is the same size as what I had before would require additional power.

    I'm asking this question on this forum because I'm trying to confirm how much power is needed for my electric hot water tank. Ever since it was installed, it flips the breaker. I have 240 coming into the house and the tank is an 80 gallon tank which is the same as I had before. The label on the tank shows single phase 208V and single phase 240V.

    Is there a test that I can run or somewhere I can look up the power requirements myself? I don't want to spend the money to put in a new line if it isn't necessary.

    Thank you.
    Safeire

  2. #2
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    It should say on the WH what the requirements are. However, nearly all full size electric WH use a 30A 240v circuit with 10/2 wire (assuming copper). Look at your panel and see if the WH breaker is 30A (or whatever the plate on the WH says).

    Even if the breaker size is correct, you still might have the wrong size wire (hard to tell without being there).

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Check the watts rating on the water heater. It will either be 4500 watts, which requires a 25 amp breaker, and usually a 30 will be used. Or it is 5500 watts which requires the 30 amp breaker. #10 wire would be ok for either, unless it is a very long run.

    Undersized wire, if that was the issue, might overheat, might cause the water heater to not heat up fast...but why would that trip a breaker???

    Personally, I don't put great faith in the "list". You need an electrician who will tell you why the breaker is popping. That will explain what needs to be done.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    CB do fail on occasion, too. If it is the proper size for the wiring and is sufficient for the WH, then you might pop in a new CB (best left to an electrician unless you are conversant with the proper safety standards). It could also be someone was sloppy when installing the thing, and the connection is shorted. This would certainly pop the breaker.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    DIY Junior Member safeire's Avatar
    Join Date
    Jun 2011
    Location
    Ohio
    Posts
    16

    Default

    Thank you. The label says for the 208V, 4125 and for the 240V 5500.

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by safeire View Post
    Thank you. The label says for the 208V, 4125 and for the 240V 5500.
    OK so you definitely should have a 30 amp breaker, #10 wire. Still don' t know why the breaker pops

  7. #7
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    Okay. Now let's check the breaker. Find the one for the WH and it will have a number on it (25, 30, etc.).

    It may be that the old WH had a smaller element and the thing is on a 25A breaker, although 30A breakers are typically installed for WHs. Your new WH would take a 30A breaker.

    After you check the breaker size, take a look at the wiring coming into the WH. If it is Romex (flat looking cable), it should have some numbers printed on it. Look for numbers such as 10/2, 10-2, 12/2, 12-2, etc. and see what it says. If you aren't sure, you could take a couple pics and post them up on here and we might be able to help you figure it out.

    If the breaker and wiring are both correct, then I would get someone (other than this guy) to come out and take a look. Maybe have him replace the breaker (if it is weak) and have him look the WH connections over and make sure something isn't shorting out.

    Although not as likely, it could also be a defect in the WH with a bad t-stat or element causing a short when that t-stat cycles on.

  8. #8
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by nukeman View Post
    Okay. Now let's check the breaker. Find the one for the WH and it will have a number on it (25, 30, etc.).

    It may be that the old WH had a smaller element and the thing is on a 25A breaker, although 30A breakers are typically installed for WHs. Your new WH would take a 30A breaker.

    After you check the breaker size, take a look at the wiring coming into the WH. If it is Romex (flat looking cable), it should have some numbers printed on it. Look for numbers such as 10/2, 10-2, 12/2, 12-2, etc. and see what it says. If you aren't sure, you could take a couple pics and post them up on here and we might be able to help you figure it out.

    If the breaker and wiring are both correct, then I would get someone (other than this guy) to come out and take a look. Maybe have him replace the breaker (if it is weak) and have him look the WH connections over and make sure something isn't shorting out.

    Although not as likely, it could also be a defect in the WH with a bad t-stat or element causing a short when that t-stat cycles on.
    Good post!
    I am definitely not a pro plumber, but I am a pro crastinator

  9. #9
    DIY Junior Member safeire's Avatar
    Join Date
    Jun 2011
    Location
    Ohio
    Posts
    16

    Default

    Quote Originally Posted by nukeman View Post
    Okay. Now let's check the breaker. Find the one for the WH and it will have a number on it (25, 30, etc.).

    It may be that the old WH had a smaller element and the thing is on a 25A breaker, although 30A breakers are typically installed for WHs. Your new WH would take a 30A breaker.

    After you check the breaker size, take a look at the wiring coming into the WH. If it is Romex (flat looking cable), it should have some numbers printed on it. Look for numbers such as 10/2, 10-2, 12/2, 12-2, etc. and see what it says. If you aren't sure, you could take a couple pics and post them up on here and we might be able to help you figure it out.

    If the breaker and wiring are both correct, then I would get someone (other than this guy) to come out and take a look. Maybe have him replace the breaker (if it is weak) and have him look the WH connections over and make sure something isn't shorting out.

    Although not as likely, it could also be a defect in the WH with a bad t-stat or element causing a short when that t-stat cycles on.
    Thank you, Nukeman, for the recommendations. I will take a look and see what I can find.

  10. #10
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by safeire View Post
    All he did was walk around the basement but never actually checked anything with any meters or other diagnostic tools.
    If a qualified electrician sees a serious deficiency such as an undersized wire, there is not much point in up-sizing the breaker since it all has to be code compliant. There is no point in playing with meters or any diagnostic tools until the most expensive part of the deficiency is dealt with.

    So, who installed the new water heater and connected to a purportedly undersized wire?

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Find someone who knows what he is doing to check the breaker and wire size. The new heater has 5500 watt elements, but that would NOT have been the common one for your former heater. It would be unusual for the wires to the heater to be smaller than #10, even if a smaller breaker was installed.
    Licensed residential and commercial plumber

  12. #12
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Well here we are flapping our collective gums...and no response from the OP! Nobody has said his wires are undersized. Everyone says they need to be CHECKED. We unfortunately have no idea why the breaker trips....is it too small for the 5500 watt, is it worn out?????

  13. #13
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by jimbo View Post
    Nobody has said his wires are undersized.
    This is true. I at least used the term "purportedly" since the OP leaves us with very little detail, saying only that he will "need to have a new line put in between the hot water tank and the panel".

  14. #14
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Undersizedl wires would NOT trip the breaker,but they could overheat. The breaker COULD be undersized, regardless of the wire's size.
    Licensed residential and commercial plumber

  15. #15
    DIY Junior Member safeire's Avatar
    Join Date
    Jun 2011
    Location
    Ohio
    Posts
    16

    Default

    Quote Originally Posted by LLigetfa View Post
    If a qualified electrician sees a serious deficiency such as an undersized wire, there is not much point in up-sizing the breaker since it all has to be code compliant. There is no point in playing with meters or any diagnostic tools until the most expensive part of the deficiency is dealt with.

    So, who installed the new water heater and connected to a purportedly undersized wire?
    Thank you, LLigetfa, for your response. He is a licensed electrician with 35 years experience so my expectation was that he would do some testing to diagnose where the problem was coming from. But, if 35+ years (or really, any # of years since I'm not a licensed electrician) experience allows him to eyeball the problem, I guess that's good enough then. I'm just trying to do my due diligence so I don't waste my time or set my house on fire because I didn't do my homework.

Similar Threads

  1. question on water heater venting (orphaned water heater)
    By harveymasons in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-23-2010, 06:11 AM
  2. electrial for new disposal hookup
    By tony norton in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 02-02-2010, 11:56 AM
  3. shutoff requirements
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-22-2009, 04:22 PM
  4. Which toilets to buy given my requirements?
    By watfallet in forum Toilet Forum discussions
    Replies: 10
    Last Post: 02-18-2007, 11:02 AM
  5. GPM requirements for a whole house water filter
    By Zot in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 06-12-2006, 11:51 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •