    Default Basement bath/laundry

    Hello again wise plumbers...

    As I've posted recently, I'm in the starting stages of a basement remodel, to include a new bathroom. To do so requires an ejector, and some other concrete cracking/excavation - for the toilet and shower, at least.

    In an effort to minimize the concrete work, the following struck me: Can I have a shower and laundry next to each other; the shower with a 2" trap, and its own vent in the wall bounding the shower, and the laundry with a 2" standpipe and trap, and its own vent, with the drainage of the laundry then flowing via a santee into the vent pipe of the shower?

    Like this:
    Attached Images Attached Images  

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    No you can not.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Member Kestrel's Avatar
    Join Date
    Aug 2011
    Location
    Seattle
    Posts
    32

    Default

    Drat.

    Is that because the laundry hook-up makes the shower a wet vent?

  4. #4
    DIY Member Kestrel's Avatar
    Join Date
    Aug 2011
    Location
    Seattle
    Posts
    32

    Default

    Would this work?
    Attached Images Attached Images  

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    It's not technically a wet vent (as I understand it), that's where multiple fixtures are attached to the same drain line that may only have one vent. On your proposed situation, the only vent is being asked to be a drain...not the same thing. Once a vent becomes a vent, it must always remain a vent - you can't use it as a drain.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    You've already made it easy by deciding to have the laundry close to the bathroom, now don't make it hard by trying to use a vent as a drain.

    You're going to have to remove concrete no matter what, why not do it all once and do it right?

  7. #7
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    Your 2nd drawing will work and meet code.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  8. #8
    DIY Member Kestrel's Avatar
    Join Date
    Aug 2011
    Location
    Seattle
    Posts
    32

    Default

    Thanks everyone - expert advice much appreciated.
    The other day I posted a diagram that was generally well received, including wet venting a lav into the toilet drain. A detail of that drawing is below.

    I'm trying to understand - it's OK to take a lav drain and drop it down the toilet's vent, but not to do the analogous and drop the laundry's drain down the shower's vent? Is that correct? Is it because the lav/toilet/shower are all a 'group' that are allowed to wet vent together, and this excludes the laundry?
    Attached Images Attached Images  

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    NO! It is because the washer is a "high volume and flow" device, and its water going past the shower drain connection, WITHOUT a vent, could aspirate the water from the shower trap. It would NOT be vented, because you have the shower vent occulded by the water flowing from the washer. IF you could do it, you would NOT need the washing machine vent in the first place. I have one customer who has a "high flow" device connected to his toilet's vent, apparently because it was the "easiest" place to connect it, and every time water discharges it sucks all the water out of the toilet.
    Last edited by hj; 08-23-2011 at 05:57 AM.
    Licensed residential and commercial plumber

  10. #10
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Why you keep insisting on using the vents as drains?

  11. #11
    DIY Member Kestrel's Avatar
    Join Date
    Aug 2011
    Location
    Seattle
    Posts
    32

    Default

    I'm not insisting on anything - I'm just trying to learn.
    I suppose I come up with some of these strategies because I don't like concrete work, and I'm trying to minimize it. It's dusty and dirty, the debris is heavy - I just don't enjoy doing it as much as framing or running pipe or installing windows. I was looking for the design scheme for this bathroom that would allow the least amount of concrete break-up and refilling, that's all.
    It also seems that using vents for drains - like the lav into the toilet - was OK. I didn't know how far this extended. I totally understand now about the high flow nature of the original scheme above not being a good or workable idea.
    Thanks

Similar Threads

  1. Bath + Laundry Layout Feedback
    By dcp143 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 11-15-2012, 12:03 PM
  2. Laundry/bath on slab - drainage
    By dwhiteykc in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 04-03-2011, 07:02 PM
  3. Bath + Laundry Layout Feedback
    By dcp143 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 10-26-2010, 06:19 AM
  4. swap laundry room to half bath
    By tonyf3 in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 09-10-2008, 08:49 PM
  5. Add Shower to 1/2 Bath / Laundry Room
    By tromo in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 11-21-2006, 11:04 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •