    Exclamation Studor Valve Odor

    Terry,
    Our 3-level piling home was completed about 7 months ago. We didn't find out until it was too late that our Plumber was a crook who had to be watched every minute. I was acting as onsite project manager to protect our investment, so he didn't get away with much. But he insisted that the only way to plumb two areas of this house was with two studor vents, one in the level 2 laundry and one hidden behind the master cabinetry on an outside wall of a bumpout area/level 3. He guaranteed that we would never smell a thing. We almost immediately had a problem with the 2nd level vent. He fixed it before final walk-through, but I have no idea how. The sewer odor is now overpowering in the master bath. I am at my wits end and don't have a clue how to handle this issue. Even if it were possible to pull the cabinets out and put a charcoal filter cap on the vent, I would assume that it would be necessary to replace the filter at certain intervals. Is there a workable option for us?
    Thanks!
    Last edited by thrumyiz; 08-17-2011 at 08:43 AM.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Well, two things re an AAV: it MUST be accessable, since it will fail eventually - it can't be burried in a wall - it needs an access panel; and, an AAV should ONLY let air in, not out. So, if it is truely smelling because the AAV is leaking, it should be replaced.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    I wonder if one of the AAVs is malfunctioning. The main concern plumbers have about them is that since they are a mechanical device, they will eventually fail. For that reason, they are never supposed to be enclosed or otherwise inaccessible. Sounds like at least one of yours is. My suggestion is to gain access to them, then replace each of the one at a time to see if that cures the problem. When using AAVs, there still must be at least 1 conventional vent to the outside of the house. Like 'em or not, but they still should not emit odor.

    http://www.studor.com/products/box-g...sSpecSheet.pdf
    Last edited by Terry; 08-17-2011 at 03:18 PM.

  4. #4
    DIY Junior Member thrumyiz's Avatar
    Join Date
    Aug 2011
    Location
    Florida Gulf Coast
    Posts
    3

    Default

    Wow....this guy was worse than I ever imagined. It appears that we're just beginning to see the consequences of the "Crooked Builder Domino Effect". I really believed just being on site 24/7 would save us. Actually, it did for the most part. But this one is going to haunt us for the rest of our lives. The one thing I did right - something that has saved us every time, thus far - is taking very detailed rough-in photos. I'll locate the vents on the photos and we'll cut a panel into the cabinet backs. Here is my fear. I followed your link. He absolutely did NOT install a studor vent, or anything similar for that matter! He installed a piece of pvc with a cap on it. This is bad, isn't it???

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    Is it bad?
    Well, it's not vented, and it may be that the traps are siphoning themselves dry.

    If the pipe is in the wall behind the counters, I would suggest that the vented panel be on the wall between the lower and upper cabinets. I guess the plumber didn't want to spend the "extra" amount for the AAV. They are kind of pricey considering how cheap plastic pipe would have been.
    I find that it's cheaper and quicker to just run the vent up through the roof.
    The only time that it kinda makes sense would be on an island.
    Last edited by Terry; 08-18-2011 at 09:14 AM.

  6. #6
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Considering what you have found, I'm thinking it might be wise to have a plumber examine you home and see what it would take to properly vent everything. It seems to me you may be in pretty deep for a DIY job.

  7. #7
    DIY Junior Member thrumyiz's Avatar
    Join Date
    Aug 2011
    Location
    Florida Gulf Coast
    Posts
    3

    Default

    My thanks to you all for helping me pinpoint the issue and begin the resolution process. You are right, Gary, when you suggest that we not try this as a DIY job! I've called another plumber to come in and install both studor vents and access panels after I determine the exact location from the rough-in photos. This site and all of you are amazing!

  8. #8
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    Were was the building inspector when this job was being done? Someone had to sign off before the home was closed in.

    John

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    YOU were the "project engineer", but what were YOUR credentials? Just because you were there was NO guarantee that the work was done properly. ALL you could do was make sure it looked nice. If YOU allowed him to install caps on the vents instead of Studor vents, and that they were installed in the correct locations, then you were NOT a very good superintendant.
    Licensed residential and commercial plumber

Similar Threads

  1. AAV/Studor noise
    By cmwood70 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-15-2008, 05:52 PM
  2. Sump Pump Odor and Check Valve Questions
    By fracai in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 02-24-2008, 07:39 PM
  3. Natural Gas Odor, Bad Valve on Empire?
    By molo in forum HVAC Heating & Cooling
    Replies: 9
    Last Post: 09-15-2007, 05:58 PM
  4. what size studor vent?
    By keithrog73 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 09-05-2006, 04:54 AM
  5. Studor Vent Help
    By finn in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-24-2005, 05:45 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •