Thread: Water? in the bottom of furnace/AC cabinet

  1. #1
    DIY Member tregg's Avatar
    Join Date
    Dec 2009
    Location
    Iowa
    Posts
    31

    Default Water? in the bottom of furnace/AC cabinet

    I went to change the air filter and noticed an inch of water standing in the bottom just below the squirrel cage fan. I don't see any drain hose at that level so I take it somethin ain't right. I wonder where's it coming from and what to do about it. I guess I'll drill a hole in the side at the bottom but should I call somebody? The air's been running a lot lately with all the heat.
    "PULL LEMULE"

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,408

    Default

    The condensate drain is likely clogged, and instead of running out the drain, is backing up into the cabinet. You need to clean the drain which starts in the tray underneath the evaporator coil (it could be clogged anywhere in that pipe). One time I had a similar situation, and found a woody fungus that clogged it all up, but it's often dust and mold.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member Runs with bison's Avatar
    Join Date
    Aug 2009
    Location
    Midwest
    Posts
    892

    Default

    In a rental I lived in for a long time we had regular problems with pink algae clogging the condensate drain. I used bleach once a month to suppress it until the drain finally clogged solid. The problem at that point was the cast iron standpipe was solid packed (iron scale takes up over 7 times the volume of the original iron if I remember correctly.) Once it was augured out and a large bore PVC pipe inserted I never had to mess with it again (no bleach either.) A few years later I had to clear all of the iron pipes going though the slab and the run to the street main as well. Actually cleared the latter twice as a parachutist went MIA down the commode...ah the joys of pre-schoolers. Didn't have to tie a yellow ribbon on the magnolia, because we recovered the poor wayward soul out in the yard.

    Another possibility is that the evaporator is icing up internally and blocking the drain.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    Yearly maintainence needs to be done on AC units and clearing the pan drains is part of that along with cleaning the condensor coils
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    DIY Member tregg's Avatar
    Join Date
    Dec 2009
    Location
    Iowa
    Posts
    31

    Default

    I think I got it-the installers left no clean out access so I had to drill thru the pvc and when I ran a snake all the goodies came out. thx for the advice
    "PULL LEMULE"

  6. #6
    DIY Junior Member TheycallMeDave's Avatar
    Join Date
    Jul 2011
    Location
    Northern Florida
    Posts
    13

    Default

    The a/c system is likely low on freon which causes the evaporator above the furnace to freeze the condensate on it until it overflows the evaporator condensate pan and starts to drip down the center of the furnace winding up on the floor underneath the blower. Have the a/c system serviced and before the Service Tech comes out, shut off the system so the ice buildup on the evaporator can thaw .

  7. #7
    DIY Junior Member tempritespokane's Avatar
    Join Date
    May 2011
    Location
    Spokane
    Posts
    17

    Default

    I cant believe that the installers left no clean out access. That seems like an obvious thing to do. I'm glad you figured it out.

Similar Threads

  1. Water coming in at bottom of sump basin
    By ric-a-pic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-30-2008, 08:33 AM
  2. Can I use an under cabinet WATER FILTER with a regular mixer tap kitchen faucet?
    By silverlake in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 09-19-2008, 06:53 AM
  3. Water in the bottom of water softner salt tank.
    By JBoogie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 03-18-2008, 10:38 AM
  4. vacuum refief valve placement on bottom feed water heater
    By Basement_Lurker in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 17
    Last Post: 02-07-2008, 04:09 AM
  5. Bottom of Pump / Bottom of Well
    By GPM in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 05-01-2007, 05:35 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •