copper and steel in contact

Users who are viewing this thread

demetre

New Member
Messages
2
Reaction score
0
Points
0
Location
nyc
Is it ok for copper water lines to be in contact with steel studs, hangers or bx cable or will it cause future corrosion in the copper?

Plumbers often put the plastic inserts between copper and steel but sometimes do not do a completely thorough job of it.

See attached pics from a renovation.
 

Attachments

  • IMG_0897.jpg
    IMG_0897.jpg
    56.2 KB · Views: 382
  • IMG_0899.jpg
    IMG_0899.jpg
    41 KB · Views: 336
  • IMG_0898.jpg
    IMG_0898.jpg
    57.1 KB · Views: 324

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
I always install so that the copper and the steel do not touch.
Plumbers UPC tape, plastic wings or inserts, copper unistrut clamps.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
"Touching" is a problem,but not necessarily the one you think it is. The problem is that the copper is going to move back and forth and the metal will wear a hole in it.
 