Thread: Pump and Tank stolen

  1. #1
    DIY Junior Member dcorazal's Avatar
    Join Date
    Jul 2011
    Location
    Minnesota
    Posts
    10

    Default Pump and Tank stolen

    I am buying a side by side duplex (double bungalow) that has had all the pluming stolen including the well and tank.
    I have little experience with wells but have done a lot of research and have a few questions about the well install and hope I can get some expert advice.
    Here’s what I know so far:
    1: The house was built in 1961 and I can’t find any records from the city regarding the well. I assume that the well casing is the original.
    2: I measured the bottom of the well at 125’ and the static level at 85’.
    3: The well casing is 6” and is in “a pit” under the front step.
    My plan is to drop a submersible pump down 100’ with 160psi poly pipe. I have researched the procedure and my local ******* sells most all the fittings that I need. That should put my pump about 23’ from the bottom and 17’ from the static level. As far as I can tell this should be fine?
    I have a couple of questions:
    1: I have no idea how many gallons per minute the well will produce so I am going to try a ¾ hp 10gpm pump and hope that will be okay. Could someone give me any advice as to test the gpm?

    2: At the top of the well I am using a well cap with 3 holes in it one for the 1 ¼ pipe one for the vent and one for the wiring. I have 2 questions here. Where do I run the safely cable through and what fitting should I use at the top of the poly pipe to turn and go to the pressure tank. I can’t seem to find a 90 degree barbed elbow? I have seen a couple of pictures of a “T” at the top of the well cap, one plugged and one side running to the tank.

    Any advice would be appreciated.

  2. #2
    DIY Junior Member dcorazal's Avatar
    Join Date
    Jul 2011
    Location
    Minnesota
    Posts
    10

    Default

    Correction: The static level is 38' not 85'

  3. #3
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,154

    Default

    Use a galv coupling, a long galv nipple. a galv tee with a plug to go through the well seal. Don't use a safety rope. Use one piece of poly, no splicing, and set it 3' off bottom. Use a ball valve on the discharge after the galv tee so you can control the output, turn it on and see what happens.

  4. #4
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    sounds like you are thinking of using steel or plastic hose barbs. I hope you are using SS or brass!

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Is the pit heated? It gets cold in Minnesota. We don't generally come out the top of the casing around here but rather, well below grade with a pitless. My pitless is 8 feet below grade.

  6. #6
    DIY Junior Member dcorazal's Avatar
    Join Date
    Jul 2011
    Location
    Minnesota
    Posts
    10

    Default

    Thanks for the replies:
    The Pit is heated because it is under the front of the garage. I'm guessing that there is enough heat coming from the house and also that It has been that way since it was installed.
    Yes, I am going to use the Long brass hose barbs with ss hose clamps.

    I drew an image and scanned it into a pdf of what my plans are.

    valveman: I'm not sure I understand your advice. Please know that I am not questioning your expertise:
    Use a galv coupling, a long galv nipple. a galv tee with a plug to go through the well seal. could you look at my pdf and see if that is what you were advising?

    Don't use a safety rope. Okay

    Use one piece of poly, no splicing, Yes got it

    and set it 3' off bottom. Use a ball valve on the discharge after the galv tee so you can control the output, turn it on and see what happens.

    I was planning on setting the pump at 100' which would be 25' off the bottom and 62' below static level. Reason: 100' in stock at store and I read some place that you should not put the pump any closer than 5' from the bottom.


    Any thing else I shold be thinking about?
    Thanks for the help!

  7. #7
    DIY Junior Member dcorazal's Avatar
    Join Date
    Jul 2011
    Location
    Minnesota
    Posts
    10

    Default

    Having trouble getting the pdf for load because it was too big. I took a picture of it and attached that. Hopefully that works
    Attached Images Attached Images  

  8. #8
    Porky Cutter,MGWC Porky's Avatar
    Join Date
    Jan 2008
    Location
    Virginia Beach, VA
    Posts
    727

    Default

    Listen to what valveman says; use no rope, that's old technology. The reason he says 3 feet off bottom is in the event the well is a low producer you'll get the most water stored in the 6" casing. However if you feel the well may be a good producer installing the pump on the end of 100' of polypipe will be fine.

    If you are going to have to buy a new tank and fittings I recommend that you research http://www.cyclestopvalves.com/products.html for the Pside-Kick. It includes a WX-102 Tank and all fittings from the pump line to the house. It's not necessary to install a large tank today if you install a Cycle Stop Valve. A CSV will keep your pump from cycling and give you constant pressure while taking a shower. Your family will love it.
    Porky Cutter, MGWC
    (Master Ground Water Consultant)

Similar Threads

  1. trying to find a well pump to replace the one that was stolen
    By dssgateway in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 09-21-2010, 09:40 AM
  2. tank and pump; how to stop pump
    By mak123 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 07-29-2009, 04:42 PM
  3. tank and pump
    By mak123 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 07-19-2009, 07:13 AM
  4. What if a good deal might turn out to be stolen?
    By leejosepho in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 11-16-2007, 02:12 PM
  5. GPM from pump, or is it from tank?
    By rick.a in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 05-16-2007, 09:08 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •