    Since you cannot answer I have put you on permanent ignore.

  2. #17
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Furd View Post
    At the generator inlet connection that you have installed in the garage you would connect the neutral and equipment ground terminals together. While this is normally NOT in accordance with either good practice or the electrical codes the FACT that your generator is a "separately derived source" makes it acceptable. .
    Do not do this, I repeat do not do this
    The GFCI device will protect any thing down stream..



    Don you are incorrect
    Last edited by jwelectric; 07-17-2011 at 04:45 AM.

  3. #18
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by DonL View Post
    Connect the ground to the nearest ground available.

    Ground it like the manufacture recommends.

    F the BS...
    Quote Originally Posted by DonL View Post
    When in doubt, Follow manufactures directions...
    Wow, for an older man your latest few posts make it seem like you are some angry kid.

    So anyway, you keep spouting "Follow manufactures directions.."

    I looked at them. The OP looked at them. NEITHER of us sees where it says to connect it to a grounding electrode system. I am amazed that you keep so firm on this stance since it is simply not true.
    If you see it in the instructions, and not under the section for connection to a building's electrical system, PLEASE post your findings.

  4. #19
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    Proper operation of Honda Generator;


    http://www.mayberrys.com/honda/gener.../operation.htm


    Have a Great Day.


    DonL
    Last edited by DonL; 07-17-2011 at 06:12 AM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #20
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by DonL View Post
    Proper operation of Honda Generator;


    http://www.mayberrys.com/honda/gener.../operation.htm


    Have a Great Day.


    DonL
    I couldn't find any requirement or suggestion to connect the portable generator to an earth connection in this link.
    Could you point it out please.

  6. #21
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    Quote Originally Posted by jwelectric View Post
    I couldn't find any requirement or suggestion to connect the portable generator to an earth connection in this link.
    Could you point it out please.

    "Make sure the system is grounded according to local regulations."





    For Your reading Pleasure;

    http://www.electrical-design-tutor.c...grounding.html

    http://www.cumminspower.com/www/lite...ingAC-2-en.pdf

    http://www.osha.gov/OshDoc/data_Hurr..._generator.pdf

    http://en.wikipedia.org/wiki/Earthing_system

    http://en.wikipedia.org/wiki/Ground_%28electricity%29


    "The terms ground and grounding are used in US electrical practice. In the UK the equivalent terms are earth and earthing."
    Last edited by DonL; 07-17-2011 at 09:59 AM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #22
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by DonL View Post
    "Make sure the system is grounded according to local regulations."

    That is not a recommendation or requirement to connect to earth.

    Should this generator be connected to a transfer switch then the grounding of the premises wiring is required to be connected to earth and this would be the local regulations that is being referenced not the installation of an electrode system for the genset.

    The devices outlined in the original post is not part of the premises wiring system and is nothing more than an extension of the generator receptacle then no earth connection is required.

    As defined in the NEC an automobile does not have a ground wire anywhere in its electrical system but instead has a connection to the negative post of the battery which in layman’s terms is called ground. This is where a lot of confusion comes to the reference to ground in the premises wiring system of our homes.
    In our homes the word ground means a connection to earth. It is through the main bonding that the fault current is allowed to return on the neutral conductor to the source which causes the fuse to blow or the breaker to trip.

  8. #23
    DIY Member JAR8832's Avatar
    Join Date
    Feb 2008
    Location
    Wisconsin
    Posts
    98

    Default

    jwelectric,

    Do you agree with the recommendation to bond the ground and neutral inside of the inlet? The generator has overload protection but GFCI is not specified. Thanks.
    Last edited by JAR8832; 07-17-2011 at 09:26 AM.

  9. #24
    Engineer Furd's Avatar
    Join Date
    Jul 2007
    Location
    Wet side of Washington State
    Posts
    446

    Default

    Quote Originally Posted by jwelectric View Post
    Do not do this, I repeat do not do this
    The GFCI device will protect any thing down stream..



    Don you are incorrect
    IF the Honda generator has a built-in GFCI then I agree with jwelectric. If it does NOT have a built-in GFCI then the method I suggest IS acceptable.

    OR you could use a portable GFCI between the generator and the power inlet in the garage. This is probably the best option.

  10. #25
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by JAR8832 View Post
    jwelectric,

    Do you agree with the recommendation to bond the ground and neutral inside of the inlet? The generator has overload protection but GFCI is not specified. Thanks.
    No
    Do nothing but lpug it in. The receptacle that you are plugging the cord into on the generator is GFCI protected.

  11. #26
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Furd View Post
    IF the Honda generator has a built-in GFCI then I agree with jwelectric. If it does NOT have a built-in GFCI then the method I suggest IS acceptable.

    OR you could use a portable GFCI between the generator and the power inlet in the garage. This is probably the best option.
    no this is not acceptable.

  12. #27
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    Quote Originally Posted by DonL View Post
    "Make sure the system is grounded according to local regulations."





    For Your reading Pleasure;

    http://www.electrical-design-tutor.c...grounding.html

    http://www.cumminspower.com/www/lite...ingAC-2-en.pdf

    http://www.osha.gov/OshDoc/data_Hurr..._generator.pdf

    http://en.wikipedia.org/wiki/Earthing_system

    http://en.wikipedia.org/wiki/Ground_%28electricity%29


    "The terms ground and grounding are used in US electrical practice. In the UK the equivalent terms are earth and earthing."

    Study this info and decide.


    The only thing that you need to do is Ground the Electrical generating source, at the source.
    The Bonding is done internal inside the generator.


    Period...
    Last edited by DonL; 07-17-2011 at 10:33 AM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #28
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    The first two links are for fixed generators and the third link says the same thing we are trying our best to explain to you
    A portable generator does not need nor require a earth ground.

    The bonding is done to the frame of the generator

  14. #29
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    Quote Originally Posted by jwelectric View Post
    The first two links are for fixed generators and the third link says the same thing we are trying our best to explain to you
    A portable generator does not need nor require a earth ground.

    The bonding is done to the frame of the generator
    Do it how you want to do it, I will do it and recommend the way that it should be done correctly.


    The original poster wanted facts, not opinions.


    The Facts are in the docs...
    Last edited by DonL; 07-17-2011 at 01:29 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  15. #30
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by DonL View Post
    Do it how you want to do it, I will do it and recommend the way that it should be done correctly.


    The original poster wanted facts, not opinions.


    The Facts are in the docs...
    So all that is left to do is for you to read and study them. Any and all of the links that you posted is nothing more than opinion. The facts come from the code books and the code book is what I have quoted.

    What you have done is muddy the water with a lot of junk and opinions. In this thread you have not made one statement of fact but only your opinion which is wrong.

Similar Threads

  1. Inverter for AC powered backup sump?
    By RinconVTR in forum Pumps and Tanks Well Forum & Blog
    Replies: 14
    Last Post: 08-30-2010, 01:12 PM
  2. Portable generator and generator panel incompatibility
    By luc in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 05-21-2009, 12:29 PM
  3. Backup power DC/inverter approach
    By alternety in forum Electrical Forum discussion & Blog
    Replies: 22
    Last Post: 03-13-2008, 12:35 AM
  4. Grounding a portable generator
    By Cubey in forum Electrical Forum discussion & Blog
    Replies: 82
    Last Post: 12-22-2007, 11:34 AM
  5. Portable Generator Grounding
    By jdavis1137 in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 11-03-2007, 04:00 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •