Thread: Firewall Outlet Box Placement(s)

  1. #1
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Question Firewall Outlet Box Placement(s)

    I am doing a condo kitchen remodel and replacing an existing firewall (5/8" fire rated drywall on wooden studs). Code says that the outlet boxes must have no more than a 1/8" air gap between the box and drywall cutout and this air gap is to be fire caulked.

    Now, does the box have to extend into the cutout or can a metal expansion ring suffice (the box installed at the rear of the drywall as to enable a more concise cut-out), the problem being cutting such an exact opening and hoping to have it hit the installed box?
    Jack of All Trades...

    ...Master of None...

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,154

    Default

    The box should be flush with the face of the drywall. If it is not, you need to use a box extender.

  3. #3
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Default

    THANX!

    So the box should be set to the outer surface of the drywall and an extension ring used if wall finishing material(s) is used.

    Makes perfect sense...
    Jack of All Trades...

    ...Master of None...

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by KULTULZ View Post
    and this air gap is to be fire caulked.
    Where are you getting this information?
    I have never heard of any such rule

  5. #5
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Cool

    Quote Originally Posted by jwelectric View Post
    Where are you getting this information?

    I have never heard of any such rule
    First, I am not a licensed professional and gain what little knowledge I have from boards such as this and technical publications. Any guidance I receive is greatly appreciated.

    I understand that any opening in a firewall structure must be protected from fire blow-though, pipes, cables and outlet boxes. I have also read through many manufacturers materials that a box penetration be tight and caulked (either with caulk or a pad) to prevent any blow-through which makes sense to me.

    From- http://database.ul.com/cgi-bin/XYV/t...818&sequence=1

    6. Metallic Electrical Outlet Boxes

    Listed metallic outlet boxes with metallic or nonmetallic cover plates may be used in floor-ceiling and roof-ceiling assemblies with ratings not exceeding 2 hours. These assemblies should have gypsum wallboard membranes. The metallic outlet boxes should be securely fastened to the joists and the opening in the wallboard facing should be cut so that the clearance between the box and the gypsum wallboard does not exceed 1/8 in. The surface area of individual boxes should not exceed 16 sq. in. The aggregate surface area of the boxes should not exceed 100 sq. in. per 100 sq. ft of ceiling surface.
    While the above excerpt does not specifically call for caulking, it may be in another section I have not discovered yet.

    So to answer your question, more word of mouth than actual knowledge. Any help is appreciated. This is a condo one hour rated wall and the builder did a terrible job (IMO) (Example- Non-rated ice supply box in fire wall and plastic outlet boxes with no backing).
    Jack of All Trades...

    ...Master of None...

  6. #6
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,661

    Default

    Quote Originally Posted by KULTULZ View Post
    THANX!

    So the box should be set to the outer surface of the drywall and an extension ring used if wall finishing material(s) is used.

    Makes perfect sense...

    You are going the correct direction KULTULZ.


    Good Luck on your project.


    DonL
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,661

    Default

    Quote Originally Posted by jwelectric View Post
    Where are you getting this information?
    I have never heard of any such rule

    That is the way it is done here, in condos.

    I guess you did not get that memo.


    Enjoy your weekend.


    DonL
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  8. #8
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Thumbs up

    THANX DON... appreciated...
    Jack of All Trades...

    ...Master of None...

  9. #9
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by KULTULZ View Post
    I am doing a condo kitchen remodel and replacing an existing firewall (5/8" fire rated drywall on wooden studs). Code says that the outlet boxes must have no more than a 1/8" air gap between the box and drywall cutout and this air gap is to be fire caulked.?
    If there is two boxes with one looking into two different units that are in the same stud bay then protection is required.

    If there is only one box in the stud bay looking into either unit then nothing is required.

    A fire wall would separate the two units between the walls and again nothing would be required for the box.

  10. #10
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Exclamation

    Quote Originally Posted by jwelectric View Post

    If there is two boxes with one looking into two different units that are in the same stud bay then protection is required.

    If there is only one box in the stud bay looking into either unit then nothing is required.

    A fire wall would separate the two units between the walls and again nothing would be required for the box.


    That explains the plastic boxes used by the builder and the fire caulking on the partition wall headers. The firewall is two separate studded walls between the units and now I see what you are telling me.

    So as long as there are two walls, one doesn't need to worry about blow out? The fire is considered contained within the unit (sprinklers also)

    You think you have it figured out and it bites you in the butt. I am assuming overhead can lights still have to be within a fire rated enclosure here?

    So in the grand theme of things, the builder was correct (I was assuming the inspector missed it) in not making the unit wall blow proof?

    THANX AGAIN gentlemen for the education....
    Jack of All Trades...

    ...Master of None...

  11. #11
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Just a note, some plastic boxes carry a 2 hour fire rating.

  12. #12
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    A double, or offset stud wall is often just done for sound proofing, and may only have minimal fire rating effect. That comes from blocking and the surface (like the 5/8" rated drywall). The comment about boxes facing either direction was about them being in the same stud bay. If there's only one in that stud bay, no problem. If there's one facing into each unit in the SAME stud bay, then you need to treat it differently since you then could have a cross-over point into both units; otherwise, the wall surface (drywall) would be the fire block.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  13. #13
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Default

    Quote Originally Posted by Jim Port View Post

    Just a note, some plastic boxes carry a 2 hour fire rating.
    GOOD POINT... But who would guess? UL labeled, correct?
    Jack of All Trades...

    ...Master of None...

  14. #14
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Thumbs up

    Quote Originally Posted by jadnashua View Post

    A double, or offset stud wall is often just done for sound proofing, and may only have minimal fire rating effect. That comes from blocking and the surface (like the 5/8" rated drywall).

    The comment about boxes facing either direction was about them being in the same stud bay. If there's only one in that stud bay, no problem. If there's one facing into each unit in the SAME stud bay, then you need to treat it differently since you then could have a cross-over point into both units; otherwise, the wall surface (drywall) would be the fire block.
    I cannot see the adjoining condo receptacles.

    I only have six penetrations to worry about. I think I will caulk and use-



    -and cover guards (covers are plastic) just to be safe.

    Again, THANX GUYS! Proper info is difficult to find and understand...
    Jack of All Trades...

    ...Master of None...

  15. #15
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by KULTULZ View Post


    That explains the plastic boxes used by the builder and the fire caulking on the partition wall headers. The firewall is two separate studded walls between the units and now I see what you are telling me.

    So as long as there are two walls, one doesn't need to worry about blow out? The fire is considered contained within the unit (sprinklers also)

    You think you have it figured out and it bites you in the butt. I am assuming overhead can lights still have to be within a fire rated enclosure here?

    So in the grand theme of things, the builder was correct (I was assuming the inspector missed it) in not making the unit wall blow proof?

    THANX AGAIN gentlemen for the education....
    A fire wall will have rock between the two studed walls.

    If there is no rock between the studded walls then where is the fire protection?

    In a single family dwelling the wall that is between the attached garage and the interior of a house is a fire wall. A box that looks inside the home and a box that looks to the garage would require a fire pad.
    Although this is overlooked in most cases for a single family dwelling everyone worries about an apartment, why?

Similar Threads

  1. Replies: 9
    Last Post: 12-11-2012, 12:01 PM
  2. Acrylic tubs and Firewall in a condo
    By Kyle Ashley in forum Remodel Forum & Blog
    Replies: 16
    Last Post: 07-16-2011, 08:42 AM
  3. convert NEMA 6-20R outlet to standard 110 outlet?
    By cham33 in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 08-16-2010, 02:27 AM
  4. Replies: 9
    Last Post: 07-18-2008, 07:16 PM
  5. y placement
    By damorej in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 02-16-2005, 03:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •