    Hi all,

    I'm adding 4 new circuits to my main panel for a kitchen remodel. To get the new wires from the panel into my house, I added a new conduit from the panel which enters into my crawl space. The new conduit goes to a junction box. I will have 4 hots, 4 neutrals and 4 grounds coming into this box, via the conduit (1 inch EMT). Going out of the junction box I will have 4 romex cables (going to the 4 new circuits).

    I have a 42 cubic inch metal box. There is nothing in the box other than spliced wire and wire nuts. I think this should be OK. Here is my calculation:

    I have 8 hots, 8 neutrals and 8 grounds in the box. The grounds as a whole count as one conductor. The 8 hots and 8 neutrals add to 16 conductors. That's a total of 17 conductors. To my knowledge each 12 awg wire counts as 2.25 cu inch. So I have 17 x 2.25 = 38.25. So I think I should be fine. Can someone confirm this.

  2. #2
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,772

    Lightbulb

    This one interests me as well
    I am definitely not a pro plumber, but I am a pro crastinator

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Antonio4791 View Post
    I have 8 hots, 8 neutrals and 8 grounds in the box. The grounds as a whole count as one conductor. The 8 hots and 8 neutrals add to 16 conductors. That's a total of 17 conductors. To my knowledge each 12 awg wire counts as 2.25 cu inch. So I have 17 x 2.25 = 38.25. So I think I should be fine. Can someone confirm this.
    Your math is correct.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    My chart calls a # 12 = 2.62 cu.in. which would make you a bit undersized, but in the real world it probably does not make a big difference.

  5. #5
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    You could have used one ground wire from the panel, but the math is correct, just like Mike said.
    Yes I am A Pirate-Jimmy Buffett

  6. #6
    DIY Junior Member Antonio4791's Avatar
    Join Date
    Jul 2010
    Location
    South Pasadena CA
    Posts
    11

    Default thanks

    Thanks guys. I'll continue with my plan.

    Now I will have everything on dedicated circuits.

  7. #7
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Quote Originally Posted by hj View Post
    My chart calls a # 12 = 2.62 cu.in. which would make you a bit undersized, but in the real world it probably does not make a big difference.
    The NEC allowance for #14 is 2 CI, for #12 2.25 CI.

Similar Threads

  1. Water use - hissing G-Max Korky 528 fill valve - Quiet Fill
    By urdrwho in forum Toilet Forum discussions
    Replies: 51
    Last Post: 09-23-2012, 04:15 PM
  2. fv75 fill pro delta toilet fill valve operation
    By SuperSewist in forum Toilet Forum discussions
    Replies: 2
    Last Post: 11-07-2010, 08:01 AM
  3. An All-metal Dishwasher Air Gap
    By ehseger in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 10-03-2009, 03:19 PM
  4. Metal to Metal connections
    By valvemistress in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 06-14-2008, 08:07 AM
  5. Toilet flange that is PVC & Metal (metal is Rusted)
    By Donnaml in forum Toilet Forum discussions
    Replies: 2
    Last Post: 01-22-2006, 07:45 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •