    Default Single person shower to double person shower

    I need to rip out my shower and re tile it. I was thinking of making it bigger and adding a second shower head and separate control.

    I was just planning to extend the pipes and T out to the new shower valve. I don't think there is an issue with any of that as far as code, but if there is could someone tell me.

    Where I thought I may have the issue is with the drain. I was just planning on using the existing drain that is there, maybe move it a bit if I could to the centre so it's easier for my tile guy to mortar the floor slope. Will the existing drain be big enough and be able to handle the extra flow from the double tap? Is there actually any extra flow considering I am just branching off an existing half inch line? The house is pretty new 5 years or so, so the ABS is 1.5 inch.

    I am in Burlington Ontario by the way.

    Also, when moving the drain, it would be a no-no to notch out the floor joists right? I wouldn't think I should do it, but if I am allowed, and if it makes for a nice centred drain one joist over I would consider it.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    1. Two valves mean TWICE as much water, regardless of the pipe size to the valves.
    2. The existing drain should handle the added flow, if it IS the minimum 2". If it is 1 1/2", then it was NEVER to code and will be too small.
    3. It is NEVER a "good" idea to notch joist, but if you decide to drill holes in them, there are strict specifications as to the size and WHERE it can be done.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    In the USA, a 2" drain for a shower has been code for awhile. Not sure about Canada. Bigger is better. It's not great to be in standing water that can happen if the drain is too small or restricted. But, 1.5" should work. The reason they went bigger is to take care of those what-if situations so that you don't overflow the curb of the shower if you say drop the washcloth or stand on the drain cover and don't notice right away...the bigger drain can clear the backup faster.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Junior Member khedrei's Avatar
    Join Date
    Nov 2009
    Location
    Burlington, Ontario
    Posts
    18

    Default

    I am trying to remember what the drain was in my old house, built in 1995 or so, when I changed the tub to a stand up shower. I believe it was only 1.5 inch. Actually thinking carefully about it, I am sure that it was.

    When did the code change? If that is the case, and it is only 1.5 inch then how would I go about changing it? I suppose I would have to redo the entire drain all the way to the 3 inch stack? Does the vent need to be 2" as well?

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    The vent can stay the same size.

    Two shower valves on 1/2" pipe is fine.
    Don't notch the joists. You can drill them if you leave 2" between the hole and the edge.

  6. #6
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Quote Originally Posted by khedrei View Post
    The house is pretty new 5 years or so, so the ABS is 1.5 inch.

    I am in Burlington Ontario by the way...
    Code in Ontario requires 2" for a shower drain. I don't know how it passed inspection.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    I cannot remember ANY time when a 1 1/2" drain was acceptable for a shower, (I have never seen any shower drain with a 1 1/2" outlet), and that goes back to the 50s.

  8. #8
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,964
    Blog Entries
    5

    Default Holes in Joists and Beams

    I would upgrade that drain to a 2" line straight back to the stack. Like Terry mentioned no notching of the floor joists and keep your holes with 2" (1 7/8") top and bottom. These numbers are for a 2"x10" floor joist.

    The largest hole you can drill through your floor joist is 2 3/8" for a 2"x10" framing member. I found a good blog site from a structural engineer - check out his site. You will notice as well not to drill through the shear and movement critical areas.

    http://woodengineering.blogspot.com/...iaphragms.html


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  9. #9
    DIY Junior Member khedrei's Avatar
    Join Date
    Nov 2009
    Location
    Burlington, Ontario
    Posts
    18

    Default

    In my old place, it was a bathtub I ripped out and turned into a stand up shower. Would a tub have been 1.5" but a stand alone shower different? That would be an oops now, but the house is sold. Nothing I can do. I know for a fact though that when I ripped it out, and cut the drain, I just redid the fixed trap, and moved the drain slightly and I never bought 2" pipe it was all 1.5" and fit back together perfectly so I wasn't dreaming.

    So no notching of the joists then. But I can drill a hold big enough for a 2" abs pipe as long as I leave clearance top and bottom if I am understanding you correctly. I will have a look at the site. Thanks.

    So redoing the 1.5" line all the way to the stack could definately require some major wall demolition. But neccessary to pass code.

  10. #10
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,639

    Default

    Quote Originally Posted by khedrei View Post
    I need to rip out my shower and re tile it. I was thinking of making it bigger and adding a second shower head and separate control.
    Adding a second shower head will take all the fun out of 2 people showering together.

    I do believe. But then again I am in Texas, where Southern girls enjoy it.

    Sorry folks, I just speak the truth.


    DonL
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The limitations on where and how big you can drill through a joist include where vertically, and also how close to the ends it can be done. A plank joist gets most of its strength from the continuous top and bottom portions, and the middle supports those edges (just like in an i-beam). You don't want to drill real close to the ends, as instead of shear and compression along the length, it is mostly in compression vertically, and a hole there weakens it more.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default

    code once allowed 1.5" diameter for showers.
    It has been discussed before in this forum.

    In Canada, I believe it is still permitted. 1.5" pipe.

    At any rate, the LENGTH of the 1.5" section of pipe is a key number to know before anyone prescribes a total re-do. If it's a foot or two in length until the stack, the pipe will safely carry the shower drain water to the stack.

    I believe they still use 1.5" pipe for washing machine standpipes in Canada. They have the same Kenmore machines as the US has. And all the other brands too. They are not restricted to using little machines only. Any washing machine that can be sold in the US can be sold in Canada. I'd like to point out that there seems to be NO horde of Canadians griping their washing machines standpipes "can't take it." Total silence. Nobody is complaining. ((!!??!!!).

    Ultimately, a 2" pipe allows greater distances (self-venting). In Canada houses are generally small or medium size. The need for a 2" pipe is for DISTANCE to the stack, not because of the amount of water hitting the drain grate or being pumped into the opening of the washer standpipe.


    By the way:
    Tubs still have 1.5" pipe as their accepted normal prescribed size.


    p.s. the thread starter person may be mistaken. It may be 2" in his house and he cannot see the difference.

    I hope this helps.

  13. #13
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Quote Originally Posted by geniescience View Post
    In Canada, I believe it is still permitted. 1.5" pipe...
    I'd like to see a code citation of that. Back in '98 when I did the plumbing in my home, the inspector insisted on 2".

  14. #14
    DIY Junior Member khedrei's Avatar
    Join Date
    Nov 2009
    Location
    Burlington, Ontario
    Posts
    18

    Default

    geniescience is correct that I have not actually lifted the drain on my existing shower to see weather it was 1.5 inch or 2 inch. What I do know is that at my last home, the drains coming from the tubs were definately 1.5 inch abs. Seeing as this already is a stand alone shower, I suspect that when I tear it out, I will likely see a 2 inch drain if it is in fact the code now.

    Thank you all for the info.

    I can also atest to the fact that our washer drain lines are in fact 1.5 inch, and this is true for all the new houses I have been to and helped friends install washers. Never had any issues with any of the new front loaders that drain large amounts of water very quickly.

    Is there somewhere I can look up the code in Ontario for the showers? I know the fancy drains all come in a 2" abs size. My guess is that this is the reason.

Similar Threads

  1. Replies: 18
    Last Post: 09-02-2011, 08:56 PM
  2. Looking for 2 person bath with shower.
    By arfeller in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 02-01-2010, 05:01 PM
  3. A person claims to be a plumber
    By Thatguy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 49
    Last Post: 05-17-2009, 08:09 AM
  4. Hello - New person here.
    By struong in forum Tankless Water Heater Forum
    Replies: 13
    Last Post: 03-23-2008, 02:57 PM
  5. Hello - New person here.
    By struong in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 03-23-2008, 02:57 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •