Thread: vertical distance to p-trap for washing machine

  1. #1
    DIY Junior Member sam.'s Avatar
    Join Date
    Jul 2011
    Location
    Brooklyn
    Posts
    4

    Default vertical distance to p-trap for washing machine

    Hey, I am new here, prior just reading and learning. I am Sam, for Samantha inspired by "Bewitched" ( tv show from 60-70s ).

    Due to tight quarters my washing machine drain empty's into the 3' stand on the floor and then 4' additional from the basement ceiling till it hits the p-trap. This was so I could vent it properly. It is an old house and this was the best way to catch the vent (8" above top of p-trap ) without destroying a wall that is full of lath, plaster, sheet rock... nasty mess. Is that ok?

    Thanks,

    Sam

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Probably not. I assume the NYC code is probably as strict as the UPC which requires the following:
    Trap shall NOT be below the floor.
    Trap shall be 6 to 18 inches above floor
    Standpipe SHALL be min 18" max 30"

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; this was the best way to catch the vent (8" above top of p-trap )

    The standpipe is much too long, because it allows the water to gain a high velocity before it reaches the trap. And, I am not sure what the significance of "8 inches above top of P-trap" is because there is no regulation like that.

  4. #4
    DIY Junior Member sam.'s Avatar
    Join Date
    Jul 2011
    Location
    Brooklyn
    Posts
    4

    Default "high velocity"

    thanks HJ, jimbo, what does the high velocity cause? I had a feeling it was wrong.

    I just need to wash the clothes until my good plumber comes back from VK end of July. I then can dig out the wall and bring the vent connection in high enough to correct the trap. The trap was originally installed below the floor with no vent.

    So if I understand correctly, there is no regulation on the vertical distance from p-trap to vent?

    Sam.

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,199
    Blog Entries
    1

    Default

    The vent comes off at the same level as the trap arm.

    Otherwise it becomes and S trap and it siphons.

    Like mentioned above, too long of a standpipe and it can also siphon a trap
    Too short of a standpipe and it can overflow.

    The vent is between the p-trap and the connection to the other plumbing.
    It breaks the siphon, otherwise you trap gets sucked dry and whatever is downstream of that, you will get to smell in you home.
    Vents go through the roof and daylight in the breeze and get dispersed outside of the home.
    If you look on the roof, you will see pipes penetrating the roof.

Similar Threads

  1. P-Trap/Vent question for new washing machine
    By tkram01 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 03-04-2013, 05:48 AM
  2. Minimum vertical distance from tub bottom to p-Trap inlet?
    By bagdanoj in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 10-20-2009, 11:18 PM
  3. Help with Washing Machine trap/drain/vent
    By schomeowner in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 11-08-2008, 09:29 PM
  4. Washing machine trap
    By Giles in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 19
    Last Post: 10-05-2008, 05:18 PM
  5. Trap on washing machine drain?
    By twojciac in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-17-2007, 01:48 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •