I have to have a nat gas pipe moved and it will really be just a small change on the main line after it enters the house.

There are 3 items supplied by this line.

Furnace, water heater and stove.

All 3 items have shutoff valves. The meter is outside and has a shutoff before the meter but not after the meter.

My question is how is a pressure test done once the line is moved?

Does the line just get pressurized with everything connected or do the appliances and meter need to be shutoff from the test?

What pressure is used and for how long....5lbs?
 

Cwhyu2

Consultant
Messages
1,615
Reaction score
22
Points
38
Location
Cincinnati OH
Our energy company will allow a add on if it is less than 10 ft of added pipe without a pressure test. More than that you will have to disconnect all your fixtures and remove valves and cap off the whole system.then test.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You have to disconnect the pipe from the meter, or the utility's regulator will just "dump any pressure above its normal setting, since that is what it is supposed to do.
 

Plumber2011

Expert Plumber
Messages
70
Reaction score
0
Points
0
Location
Boston, Massachusetts
Website
www.norwoodplumbing.com
Hi Rich,

Disconnect and cap everything, especially the meter, as mentioned. Then, check local code requirements to know the exact pressure test to use in your area. In my area we test at 3 P.S.I. for 15 minutes, but we use a special test gauge that reads in 1/10th LB increments. In other areas, they use 30 P.S.I gauges and test to 25 P.S.I. for 10 minutes, so the test pressure is definitely specific to your area.

You can purchase a test setup (see image) or you can make one by buying the gauge, a shutoff , an 1/8" shrader valve and necessary fittings to build your own.

Good luck!
 

Attachments

  • Gas test1.jpg
    Gas test1.jpg
    7.3 KB · Views: 642

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
Thanks for the info it is appreciated. I was unclear about the meter and the appliances needing to be disconnected. Now I know how it should be done by whoever I select to do the work....Thanks agan....
 

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
Do not trust any fittings you buy from H-D........Made in China....

For the second time I have had a fitting that was porous and leaked.

Had a chromed/heavy cast bronze screw together p-trap leak right thru the chrome a few years ago.

This time a simple 1/2" pipe black iron cap to complete a gas pipe pressure test that caused a very slow pressure loss.......Painted all fittings with soap solution and discovered the culprit......


The damn Chinese imported products should be banned.....Nothing but junk and endless problems and added work.......
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks