Thermostatic valve operation; is the hot or the cold or both controlled?

Users who are viewing this thread

let it flow

New Member
Messages
8
Reaction score
0
Points
1
Location
Thousand Oaks, CA
Does a thermostatic valve control the hot flow and let the cold flow freely, or does it control the cold flow and let the hot flow freely? Or does it close one off as it opens the other?

And while I have the attention of you thermostatic experts; How fast is a "fast" responding thermostatic valve? Several seconds?, about 1 second?, small fraction of a second? Do all thermostatic valves also incorporate a pressure balance to handle the sudden changes while the thermostat slowly adjusts for the long term temperature?
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Usually it will control the hot water. If the temperature starts rising it will shut down the hot water, and if there is not enough cold water to balance it, it will eventually shut the hot water off entirely. If there is no hot water, it would try to keep adding more, but the water would just stay cold. Most have a paraffin "motor" and it operates fairly rapidly, but NOT instantaneously. Most do not have "room" for both pressure balance and thermostats, and a pressure balancing feature would be redundant.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks