    Is it wise to provide a bond between the hot and cold water pipes of a water heater?

    The electrical panel is for a 200-amp service, so should a #4 gauge wire be the right size then? Is it NOW correct to also bond the natural gas pipe along with the hot and cold pipes? Does doing so create any kind of hazard?

    Thanks, Chuck

  2. #2
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    If your house is plumbed with copper or galvanized pipe you should have a bond to the cold water pipe already. A shower valve completes the bond to the hot water side.

    The gas line will be sufficiently bonded by the gas appliance's electrical connection. This assumes you have an equipment ground on the circuit that provides power to the appliance.

    When was this house built? Is the water line to house metal? What kind of gas piping do you have?

  3. #3
    sea-bee chuck b's Avatar
    Join Date
    Jan 2011
    Location
    levering, michigan
    Posts
    72

    Default Reply

    Thanks for the information.

    House is plumbed with copper with a jumper on each side of the water meter. The natural gas line in question by the water heater is of course not electric, but the nearby natural gas furnace is which the gas line also supplies. Not sure what you mean by a shower valve completing the bond.

    Your comments?

    Quote Originally Posted by ActionDave View Post
    If your house is plumbed with copper or galvanized pipe you should have a bond to the cold water pipe already. A shower valve completes the bond to the hot water side.

    The gas line will be sufficiently bonded by the gas appliance's electrical connection. This assumes you have an equipment ground on the circuit that provides power to the appliance.

    When was this house built? Is the water line to house metal? What kind of gas piping do you have?

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    The only requirement for bonding a metal water pipe is found in 250.104 and this section requires the bonding point to be accessible.

    There is no requirement to bond the hot to the cold as they both are from the same potable water system. If you are worried about the bonding taking place the valve that is used to turn the hot and cold water on at the shower does this bonding as well as other types of plumbing mixing valves and supports.

    The gas pipe will need to follow the installation instructions that come with any flexible connections to the gas equipment. All 250.104 calls for is the equipment grounding conductor that is installed with the branch circuit conductors supplying a piece of gas equipment such as the heat.

  5. #5
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    Quote Originally Posted by chuck b View Post
    Not sure what you mean by a shower valve completing the bond.
    He said it better.
    Quote Originally Posted by jwelectric View Post
    There is no requirement to bond the hot to the cold as they both are from the same potable water system. If you are worried about the bonding taking place the valve that is used to turn the hot and cold water on at the shower does this bonding as well as other types of plumbing mixing valves and supports.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    Placing a bond between the hot and cold lines at the heater is ALWAYS a good idea. Many heaters start leaking because of "stray" currents passing from the hot side to the cold by going THROUGH the water heater, and since this is a high resistance path, it deteriorates the water heater. I once had a heater that lasted 4 months and when it failed it was like someone used a can opener on the top of the heater DIRECTLY from the hot outlet to the cold inlet. There is usually no sign of electrical activity to be detected, but after I installed a jumper between the two pipes, they never had any more troubles.

Similar Threads

  1. Bonding when 2 circuits in one box?
    By jch in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 03-30-2011, 02:42 AM
  2. Bonding
    By Bgood in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 06-17-2009, 04:01 AM
  3. Bonding ground rod to water pipe to nuetral bus
    By Lakee911 in forum Electrical Forum discussion & Blog
    Replies: 47
    Last Post: 02-06-2008, 02:18 PM
  4. Metal Bonding?
    By molo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 08-14-2007, 06:49 AM
  5. pvc not bonding
    By foghat35 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 03-08-2007, 07:20 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •