  1. #16
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Quote Originally Posted by Terry View Post
    I'm a big fan of vertical.
    I like as many of my pipes to go straight up and down as possible.

    Popping vents through metal is a bit trickier though. Most of my vents are through comp shingles or cedar shakes.

    So.......your inspector never passed his state test? That's kind of sad.
    The inspector is I believe just a failed builder - for a good reason. And the state test I never heard of. Most state test are made for idiots for pass.

    I know better than most because I was chosen with 6 others to Re-write on salary and paid vacation a contractors old test that my 5 year wold would have passed.

    BUT I would vent a kitchen sink on 40 ' of 2 " pipe and I'll send HJ 10,000$ the day it stops working....

  2. #17
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    quote; BUT I would vent a kitchen sink on 40 ' of 2 " pipe and I'll send HJ 10,000$ the day it stops working....

    If you are saying you would put a trap under the sink and then run a 2" line 40', WITHOUT a vent, then it will NOT stop working, but it WILL malfunction, which is a different problem, immediately. And if you did do that, then you might be a "general engineering contractor", (whatever that is), but you are NOT a "mechanical engineer" and should NEVER be allowed to do ANY piping installation.
    Last edited by hj; 07-02-2011 at 05:50 PM.

  3. #18
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    California uses the UPC Plumbing code.
    That is not the same as a contractors test.
    The State keeps track of time on the job before a test can be taken.
    The minimum is 6,000 before the test can be taken.
    If you had half that time working with a "real" plumber, then you would be getting closer to understanding what we have been saying.
    Right now, it's like discussing plumbing with the hack that stocks the Home Depot plumbing department.
    They think that because the stand in front of plumbing parts, that it qualifies them as a plumber.
    I sat in front of the teacher in school, but was considered a "student".
    The teacher had teaching credentials. Help me out here. Who is a teacher on the site that can tell us what has to be done before you get your own classroom.

  4. #19
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    36 years in the field as a licensed master is pretty helpful

    Just for clarity though, the 40' run on a 2" line is not a problem if the pipe is properly pitched but there needs to be a vent on that line within the UPC trap to vent distance. Will the drain function without a vent? Sure it will, but there is a high probablility that with that distance and volume, of the trap being siphoned so either fun a vent up or put a Studor on it if local code allows.
    Last edited by Tom Sawyer; 07-03-2011 at 07:20 AM.

  5. #20
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Quote Originally Posted by hj View Post
    quote; BUT I would vent a kitchen sink on 40 ' of 2 " pipe and I'll send HJ 10,000$ the day it stops working....

    If you are saying you would put a trap under the sink and then run a 2" line 40', WITHOUT a vent, then it will NOT stop working, but it WILL malfunction, which is a different problem, immediately. And if you did do that, then you might be a "general engineering contractor", (whatever that is), but you are NOT a "mechanical engineer" and should NEVER be allowed to do ANY piping installation.
    Dont get your shorts in a wad. Why not wait a bit for the explanation before the insults. Maybe we missed something here. I was talking about the VENT line from the sink, within about 20" of the drain running mostly upwards in order to connect to the single stack out the roof.

    The original plumber thought a 3" first floor toilet vent stack could take 2 or three fixtures at most [for venting], and thought it fine to dump a upfloor toilet in that too.

    I thought you were saying a 20' 2" pure vent run would malfunction, and I upped it to 40'.

    Anyway, I'm not trying to engineer the plumbing, just want it to pass code with a single 3" vent.

  6. #21
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Quote Originally Posted by hj View Post
    quote; OK, so 5 fixtures, with only one, the kitchen sink, 18 feet away, can tie into the 3" stack and go out the roof with just one pipe

    Maybe, and maybe NOT. You are NOT telling us HOW the individual vents are getting into the attic so they can be tied together. HOW you do the piping is the important thing, NOT that the "sink is 18' away". That could mean MANY things, some of them legal and others not. It is like you saying, "My car can go 150 mph, is it okay if I drive it", without specifying if you mean on the road or at the track.
    Okay so I think some posts got deleted...

    But my lousy 2" kitchen sink vent, pure vent is on a mostly up run and then a sharp curve up and right into the 3" stack.

    This is an extraordinarily simple house to plumb because I did engineer a truss and wall combination which gives me a 12" deep experior wall to super insulate and run pipes with out a single hole to drill. We laid the half trusses down on the slab, connected them at the ridge and stood the whole house up in one day. Actually enough room in the roof truss members to do the HVAC ducting too.

    The whole house was plumbed up in part of a day. NO drills!

    But lots of controversy here because I probably didnt describe it all very well.

    I came to you small black pipe pros because the Head of building department says call a supply house for info, I have not done any ABS piping for several years, and the "plumber" is a double stacker of toilets that about killed me when i said we could put it all [fixture vents] in one 3" vent stack. Even after I made him run a new pipe for the upstairs toilet.
    Last edited by ballvalve; 07-03-2011 at 11:41 AM.

  7. #22
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    The important thing to know is that the purpose of vents is to protect the trap seals. Therefore codes list a maximum trap to vent distance.

  8. #23
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    I built a no-code wildlands cabin and plumbed every fixture with a auto-vent. 10 years later everything flushes like a champ.

    Auto vents would kill the pipe and plumbing industry after they allowed pex in.

    one advantage of the auto vent in a cabin is the traps dont dry out if you plug the drain or bag the toilet before you leave.
    Last edited by ballvalve; 07-06-2011 at 01:02 PM.

  9. #24
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    So basically you piped a mobile home LOL

    Auto vents are pretty much allowed everywhere and no, they have not killed the industry and they never will because knowlegable plumbers will only use them as a last resort and 99% of the DIY crowd has no clue how they operate nor do they understand what the vent system is supposed to do. Besides which, they are a mechanical device which can and will fail. A properly designed and installed DWV system does not rely on anything other than the laws of physics to operate flawlessly over the course of a lifetime without reliance on moving parts and mechanical devices. That is the beauty of a properly designed and installed DWV system.

    Now, if you will explain the logic and physics of the last sentence of your post, we are all dying to hear the explanation there.

    We licensed plumbers know things, many things in fact that 99% of homeowners don't know or understand nor do they want to. Some seem to think that this profession ( note the word profession ) can be learned in a couple weeks or by reading books or hanging out on forums. It takes years to master all of the aspects of modern plumbing & heating. Many hours in the classroom, at seminars and in the field. We need to understand and apply math that is well beyond the average high school graduates abilities as well as business and accounting skills to run our businesses efficiently. My cardiologist is a brilliant man. Top in his field. He rebuilt me a couple years ago and because of his knowledge and skill I will be here harrassing folks for many years to come. When his plumbing or HVAC needs attention he calls Us. He call us because as brillaint a surgeon he is he has no idea how to fix his own stuff. I get a little tired of those folks that seem hell bent on belittling a PROFESSION that they have a rudimentary understanding of at best. It's not the materials that will destroy the trade, it is apathetic and ignorant people that have forgotten why we need licensed plumbers. Perhaps a major cholera outbreak would stir their memories but I doubt it.

  10. #25
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Granpas vent system gave a place for the water in traps to evaporate to, at least in our dry climate - following that?

    AV's close the air connection when the fixture is not in use. closing the drain seals the unit up. A cabin with dry traps and a septic system can give a closed house a rather odd odor after 6 months.

    No one is knocking your profession other than there seem to be a plethora of bad and expensive plumbers in this area.

    And I wonder where 1/4 of this nation would live without those slimy mobiles with AV's? Damn odd that they actually work!

    Your house is filled with joints and new leak points now due to sprinklers, and all those valves in the house are mechanical devices. A well made AV will fail in the open position and for 3 bucks and a few twists, its all fixed. I'll just bet your doctor could understand that valve - pretty much like the ones he sees in a heart.

    Maybe you dont know it, but the plumbers union fought pex for millions of dollars. they manage to disallow AV's in many areas still, in concert with the pipemakers. What good is life to a plumber that shaves off 1/2 his time due to engineered materials?

    Some of your mob cities still require cast iron - they get a cut from more wages. You may be one of the few true pro's in that field, but I would read up on politics of plumbing - gas in plastic pipe? That took a big fight.

    The local 'pro' plumber I called to rod out a main drain said the septic tank was shot. He only had 100' of snake and stopped 5" short of a fix. There was a cleanout in the crawl space 20 feet closer, but it would have meant getting dirty.

    After I spent 600 bucks finding the tank and fixing his 5" of cheapness, I got a bill for 175$ Thats a pro, eh?

    Funny thing about your doctor, if he slipped and you died, you still owed him 75 grand or more. If you broke his toilet when installing it, who would pay for the new one?

    Thats why he calls you - because his last corpse's wife gave him $100,000 to kill him. would you screw around under a sink with that money lingering in your bank account for your slip with the scalpel? A true PROFESSION is where you get to f&*^% up and still get paid - thats doctors, lawyers and politicians, and a some dentists. ARTISANS get to fix their screw ups.

    PS. Read "roughing it" good ol Mark Twaine managed to insult every 'profession' on earth in that and a few other novels.
    Last edited by ballvalve; 07-07-2011 at 05:58 AM.

  11. #26
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,944

    Default

    Quote Originally Posted by ballvalve View Post
    Granpas vent system gave a place for the water in traps to evaporate to, at least in our dry climate - following that?

    AV's close the air connection when the fixture is not in use. closing the drain seals the unit up. A cabin with dry traps and a septic system can give a closed house a rather odd odor after 6 months.

    No one is knocking your profession other than there seem to be a plethora of bad and expensive plumbers in this area.

    Your house is filled with joints and new leak points now due to sprinklers, and all those valves in the house are mechanical devices. A well made AV will fail in the open position and for 3 bucks and a few twists, its all fixed. I'll just bet your doctor could understand that valve - pretty much like the ones he sees in a heart.

    Maybe you dont know it, but the plumbers union fought pex for millions of dollars. they manage to disallow AV's in many areas still, in concert with the pipemakers. What good is life to a plumber that shaves off 1/2 his time due to engineered materials?

    Some of your mob cities still require cast iron - they get a cut from more wages. You may be one of the few true pro's in that field, but I would read up on politics of plumbing - gas in plastic pipe? That took a big fight.

    The local 'pro' plumber I called to rod out a main drain said the septic tank was shot. He only had 100' of snake and stopped 5" short of a fix.

    After I spent 600 bucks finding the tank and fixing his 5" of cheapness, I got a bill for 175$ Thats a pro, eh?

    Funny thing about your doctor, if he slipped and you died, you still owed him 75 grand or more. If you broke his toilet when installing it, who would pay for the new one?
    Unless you are plugging the fixture drains up the water will evaporate out of the drain yes?

    You get what you pay for. I suspect you are not willing to pay for a decent plumber so you hire hacks and then get pissed off.

    I was addressing mechanical device in the DWV system i believe.

    Are you sure they WILL fail in the open position? And when they do they let sewer gas into the house.

    Yes they did fight pex and aav's and I wish they had won. It's not always about doing things cheap and fast. Well, maybe it is to some folks LOL

    I've heard your drain story before and can't help but wonder why you would hire someone that doesn't have the proper tools and knowledge to do the job. Are you sure you didn't hire an unlicensed handy hack?

  12. #27
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Judging by all the tv shows about rotten houses being torn apart, our profession has a parasite rate of about 50% hacks. And they are hard to spot by homeowner joe.

    Anyway, my handy hack is a worker to dream of, but is young and the inspector being a bit stupid, has been allowing him to wet vent toilets all around the area. And since his teacher liked to pepper the roof with future leaks, he never thought of one pipe only. As I said its a no drill one wall plumbing job so one stack made perfect sense on THAT house.

    The REAL problem is that our schools sold all their woodshops to buy computers. And the metal shops. So they graduate imbeciles that can only be taught on the job, and their mentor might be an idiot. I would say the school system owes me 500,000$ for all the kids I taught a trade to. For awhile they had a training program where they gave me half the wages back, but the kids were best suited to operating a press to make coat hangers. One big strong kid was wiring brushing a huge beam we cut on our sawmill, and actually started crying, and said he couldnt work that hard. left for home.

    Another one was a prima dona with some skills, and when asked to clean out the packing shed where all our blankets and plastic is kept, said the work was below him. I offered to help. He said nope. Never had such pleasure firing someone.

    Had a nice kid trying to build a cheap garden gate. One swing of the hammer, and had to stop him and ask carefully if he had a father. Well, up to age 3, when he ran off.

    I have a 5 year old that can strap off a load on a truck better than one guy I've had for 25 years. And the 5 year old finds PROBLEMS with the load and reports them. Its all about mentoring. If the kid sees a guy with a impact wrench in his hands, all 4 wheels are chocked both sides in about 40 seconds. Unfortunately, sometimes the guy is just walking past the truck to some other job.
    Last edited by ballvalve; 07-07-2011 at 12:09 PM.

  13. #28
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,773

    Default

    Quote Originally Posted by ballvalve View Post
    Judging by all the tv shows about rotten houses being torn apart, our profession has a parasite rate of about 50% hacks. And they are hard to spot by homeowner joe.

    Anyway, my handy hack is a worker to dream of, but is young and the inspector being a bit stupid, has been allowing him to wet vent toilets all around the area. And since his teacher liked to pepper the roof with future leaks, he never thought of one pipe only. As I said its a no drill one wall plumbing job so one stack made perfect sense on THAT house.

    The REAL problem is that our schools sold all their woodshops to buy computers. And the metal shops. So they graduate imbeciles that can only be taught on the job, and their mentor might be an idiot. I would say the school system owes me 500,000$ for all the kids I taught a trade to. For awhile they had a training program where they gave me half the wages back, but the kids were best suited to operating a press to make coat hangers. One big strong kid was wiring brushing a huge beam we cut on our sawmill, and actually started crying, and said he couldnt work that hard. left for home.

    Another one was a prima dona with some skills, and when asked to clean out the packing shed where all our blankets and plastic is kept, said the work was below him. I offered to help. He said nope. Never had such pleasure firing someone.

    Had a nice kid trying to build a cheap garden gate. One swing of the hammer, and had to stop him and ask carefully if he had a father. Well, up to age 3, when he ran off.

    I have a 5 year old that can strap off a load on a truck better than one guy I've had for 25 years. And the 5 year old finds PROBLEMS with the load and reports them. Its all about mentoring. If the kid sees a guy with a impact wrench in his hands, all 4 wheels are chocked both sides in about 40 seconds. Unfortunately, sometimes the guy is just walking past the truck to some other job.
    Just thought I'd lighten up this thread with something about a plumbers problem :-) http://www.myspace.com/video/pancake...packle/6263274
    I am definitely not a pro plumber, but I am a pro crastinator

  14. #29
    DIY Junior Member Ramon Leigh's Avatar
    Join Date
    Jul 2011
    Location
    Pennsylvania
    Posts
    6

    Default

    As to AAVs - before I moved to Florida 6 years ago, I never heard of an AAV or knew anything about venting systems.
    But all the houses in this development use AAVs for all kitchen sinks and bathroom vanities. So when one of the posters
    here complains about their unreliability I have to laugh - no one in this development, according to the maintenance folks, has ever had a problem with their AAVs. That kind of thinking, he said, is obsolete - harks back to the days when they first came out and weren't so good. Their lifespan nowadays is such that even mentioning reliability concerns is bizarre.
    As to the claim that venting systems only depend upon the laws of nature and therefore last 500 years (as opposed to 60 years for AAVS) isn't a compelling argument. The house itself probably won't last 60 years. And mechanical devices can
    outlast you - buy a solar panel and see how long before it dies. Won't be before 30 years and likely will last 100 years.
    I'm going to build and am not even considering anything other than AAVS for my vanities and sinks. Based on my personal experience and those of the 750 homes around me, do you really think I am going to pay attenion to the opinion of some Joe who has a vested interest in non-AAV systems ? If so, which planet have you been living on for the past 10 years?

  15. #30
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    In new construction, I can plumb a system with vents that will cost less then I would have spent using AAV's.
    A little bit of ABS pipe may be a few bucks and the AAV costs about $30 and needs to be installed at trim. Just one more thing to bring to the job. I don't like AAVs, for many reasons.

    What planet are you on?
    Last edited by Terry; 07-26-2011 at 02:02 AM.

Similar Threads

  1. how many fixtures on a 3" stack?
    By custombuilt in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-23-2011, 06:26 AM
  2. Do you think a 3-1/2" vent stack is moronic? I do.
    By hawkeyeerik in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 16
    Last Post: 07-29-2009, 08:06 AM
  3. Replace 2 " galvenized at vent stack
    By LittleLisa in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-21-2009, 11:28 AM
  4. Tying 4"x4"x2" all-hub into existing stack
    By Ed_S in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 10-11-2007, 03:22 PM
  5. 2"main stack vent, big enough??
    By rheagle1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 03-20-2005, 06:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •