Cycle Stop Valves

Users who are viewing this thread

Don Love

New Member
Messages
2
Reaction score
0
Points
0
Location
Lubbock,Texas
Can a cycle stop valve be put in a tee to the sprinklers (before pressure
tank) off the main line?
Also I have a 40-60 pressure switch and a 30-50 CSV,the pressure stays about a
constant 45 psi with sprinklers running.
The problem is the CSV will not let the pressure tank psi get above 52 (withot
sprinklers) psi.To shut off the well I've adjusted it.Now the working pressure
is 40-52 istead of 40-60 with sprinklers off. Thanks for your help.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Welcome to Terry's Forums Don.

Are you any relation the Terry ?

I am sure the CSV pros will have a answer for you shortly.


Have a Great Day. And Good Luck on your project.


DonL
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
40 PSI is what that valve is suppose to hold steady. 45 doesn't surprise me cause gauges are always off a few pounds. 52 might be all your pump will produce. Is it a submersible or a jet pump?

And the CSV needs to go before the tee to the tank and sprinklers.
 