Thread: Does a torn wire jacket violate California electric code?

  1. #1
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default Does a torn wire jacket violate California electric code?

    And if it does can you link to the section of the code that it violates?

    I had a mini-split AC system installed in my house by a licensed contractor and they ran a 50ft AWG14 cable through the attic to connect the outdoor compressor to the indoor blower. This cable is double insulated and has 600 V insulation. They installed the system to its own 20 amp circuit in the panel as required. The power supply is 208/230 V, phase 1, 60 Hz.

    The installers left a 1.5 tear in the outer jacket that covers the inner insulated wires. This is in the attic bundled with the lineset. I have had many problems with this system leaking so i've had other contractors out to give repair bids on getting the system fixed and in that process was told about the tear. 1 of the contractors told me that the tear is a code violation and that the cable has to be replaced (not taped) to bring it up to code. Is he correct and can you give me the section of code he's basing this on?

    BTW, yes I know about the CSLB and I'm already on it. So I'm interested in being made whole at this point and getting what I paid for the first time and having equipment that wont violate code and will pass a sales inspection in the future.

    Thanks to anyone who can help with this question!

  2. #2
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    On a 20 amp circuit the min # 12 awg wire.
    And must be 12/2 awg wg.
    Never have come across 208/230 in residental.
    Last edited by cwhyu2; 06-17-2011 at 03:24 PM. Reason: typo

  3. #3

    Default

    12/3 is NOT needed for 240 volts.

  4. #4
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default

    Thanks cwhyu2. The installation manual specifies only 14 AWG for the connection cable between the UNITS (this is what has a 1.5" tear in the outer jacket in the attic). There is small a junction/breaker box that was installed next to the outdoor unit. They probably ran a 12/2 awg POWER cable from this small junction box to the 20 amp circuit they wired in the main panel.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    As outlined in 240.4(G) Part III of 440 will be used to size the conductor and the overcurrent device for this Air Conditioner.
    Use the Minimum Circuit Ampacity to size the conductors and the Maximum Overcurrent Device to size the fuse or breaker.
    I have personally wired many AC units with 14/2 with ground Non-Metallic cable and protect the circuit with a 25 amp breaker per the nameplate on the unit.

    If the sheathing of the cable becomes damaged then replacement is the only cure for the problem unless a box in set and the damaged part is inside the box.

  6. #6
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default

    Thanks jwelectric. But that still doesnt answer my question. I've got some contractors saying that all that's necessary is to wrap some electricians tape around this jacket since the inside wires are also insulated. I've got 1 contractor stating that this damage cannot be repaired with tape as it will not meet code. SO...which section of the electrical code states you cant repair outer jackets with tape when you have a double insulated cable?

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    110.3(B) The conductors must be installed according to any listing and labeling and black tape is nowhere close to the sheathing on NM cable.

    No conductor can be installed in any manner except for in conduit or part of a cable.

    300.12 mandates that the sheathing be continuous from one box to the other.

    Ask the electrician if the manufacture of the cable will send you written permission to use tape to repair the sheathing.

    You do not have a double insulated conductor. The black and white conductor has insulation but the two and the equipment grounding conductor is incased in sheathing which has no insulating value at all.

  8. #8
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    When you say; "The installers left a 1.5 tear in the outer jacket that covers the inner insulated wires. This is in the attic bundled with the lineset."

    Is the wire damaged, or is that where the wire connections are made ?

    It sounds like the connection was not put in a proper box, and is just laying in the attic.

    Can you post a picture ?


    DonL
    Last edited by DonL; 06-17-2011 at 09:00 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  9. #9
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default

    DonL,

    The cable is a 50ft cable that runs alongside the insulated refrigerant linesets for the mini-split AC. The cable and the linesets connect to the indoor blower unit and then run all the way out of the attic to the condenser unit outside. This cable is double insulated with various wires inside. It relays power and signals from the indoor blower back and forth to the outdoor compressor. The torn section of outer jacket on the cable is about at the mid point of its length. This is inside the very hot attic. No copper is showing, just the second jacket that covers the individually jacketed wires inside.

    I need to hear from you if this is damaged beyond repair as that's what I'm trying to find out. I need to see what part of the electrical code that would say that you cant repair this tear with tape.

    I've attached a web image that will give you an idea what this cable looks like, but mine looks like it has another black jacket underneath the one that's torn.
    Attached Images Attached Images  

  10. #10
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default

    BTW the image I posted is just a manufacturer image of a new uninstalled cable. Thanks.

  11. #11
    DIY Junior Member LCroft's Avatar
    Join Date
    Jun 2011
    Location
    California
    Posts
    7

    Default

    Quote Originally Posted by jwelectric View Post
    110.3(B) The conductors must be installed according to any listing and labeling and black tape is nowhere close to the sheathing on NM cable.

    No conductor can be installed in any manner except for in conduit or part of a cable.

    300.12 mandates that the sheathing be continuous from one box to the other.
    THANK-YOU jwelectric!!! Sir/Madam you are a credit to the human race! I hope you've contributed to the gene pool

  12. #12
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    "It relays power and signals from the indoor blower back and forth to the outdoor compressor. The torn section of outer jacket on the cable is about at the mid point of its length."

    If it is a 24v control wire, then I believe the rules change.

    You could just use heat shrink tubing, if that is the case.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #13
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    Thought you you were talking high voltage wiring,not control wiring.

  14. #14
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    This is line voltage, not control wiring.


    While I definitely value JW's expertise, I disagree with him on this point. 300.12 dictates that sheathing must be continuous box to box. IMO it does NOT say that a small tear cannot be repaired with proper electrical tape. Even if it is repaired, it is STILL "continuous".

    Tape IS a legal and safe repair for a small tear in NM cable sheathing.

  15. #15
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Since underwater splices are made with rubber splicing tape and then covered with scotch 33 it sure seems that would be safe on this wire.

Similar Threads

  1. Replies: 4
    Last Post: 08-22-2010, 05:25 PM
  2. California: New closet flange code?
    By Greg98 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 01-24-2010, 05:54 PM
  3. Bath Electric Code
    By jerome8283 in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 04-21-2008, 01:31 PM
  4. California code questions - water heaters
    By mikeyvon in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-22-2008, 03:12 PM
  5. California plumbing code question
    By Kelley G in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 18
    Last Post: 06-25-2007, 08:18 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •