Thread: 24 V on all zones even when only one is on - No water on any

  1. #1
    DIY Junior Member andy500ny's Avatar
    Join Date
    Jun 2011
    Location
    East Meadow, NY
    Posts
    2

    Default 24 V on all zones even when only one is on - No water on any

    I just relocated my Nelson control box to a new location on other side of house. All wiring done correctly. The system worked. Recently the system stopped putting out water. I went to the control panel with my voltmeter. Transformer puts out 24 V. I tried to run an extra cycle, Zone 1 and all others are receiving 24 V at the same time. No water comes out anywhere. I tried other zones one at a time manually, but every time all the zones get 24 V at the same time and no water. When the system is off, the transformer is putting out 24 V and as expected none of the zones get any voltage. Any ideas? I just disconnected all the zone wires and re checked zone connection screws and all seems to be sending 24 V to the correct zone, however if that zone wire is connected it sends 24 V to each of the other zone wires even if they're disconnected from the control panel.
    Last edited by andy500ny; 06-13-2011 at 07:22 AM. Reason: new information from rechecking control unit

  2. #2
    irrigation tech. mike1059's Avatar
    Join Date
    Jun 2011
    Location
    Portland, OR
    Posts
    56

    Default

    First I would check for a reset button in the clock. If you can't find one try disconnecting the power and back-up battery for 0ne minute to reset the clock to factory settings. If this does not work you may have to replace the clock.

  3. #3
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by andy500ny View Post
    I just relocated my Nelson control box to a new location on other side of house. All wiring done correctly. The system worked. Recently the system stopped putting out water. I went to the control panel with my voltmeter. Transformer puts out 24 V. I tried to run an extra cycle, Zone 1 and all others are receiving 24 V at the same time. No water comes out anywhere. I tried other zones one at a time manually, but every time all the zones get 24 V at the same time and no water. When the system is off, the transformer is putting out 24 V and as expected none of the zones get any voltage. Any ideas? I just disconnected all the zone wires and re checked zone connection screws and all seems to be sending 24 V to the correct zone, however if that zone wire is connected it sends 24 V to each of the other zone wires even if they're disconnected from the control panel.
    when you say you measured 24 volts at all zones, where did you measure it? at the zone valves? did you measure at the zone valves to the common wire? that connects to one conductor of each valve solenoid? I sounds like what you are measuring is not from the common wire. I may have worked OK when you first made the change, but something happened with the common wire in the cable between the timer and the valve manifold or whatever valve arangement you have. Just my 2 cents.
    I am definitely not a pro plumber, but I am a pro crastinator

  4. #4
    DIY Junior Member andy500ny's Avatar
    Join Date
    Jun 2011
    Location
    East Meadow, NY
    Posts
    2

    Default

    I measured 24 V at the control panel from the white common to each of the other zone terminal and then also at the zone wires that I disconnected from the control panel.

  5. #5
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by andy500ny View Post
    I measured 24 V at the control panel from the white common to each of the other zone terminal and then also at the zone wires that I disconnected from the control panel.
    Check at the valves themselves for voltage from the common wire. Also, at the timer, if you disconnect all the zone wires and the white common wire from the timer, and measure the resistance with your ohm meter from the white wire to each of the wires from the valves, the resistance of each reading should be the approximately the same for each valve if the wiring is OK, and if each zone only has one valve (of the same brand). I don't know if different valve manufacturers valves are all the same, but if the are, the readings should be the same.
    I am definitely not a pro plumber, but I am a pro crastinator

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    If ALL the zones are being activated at the same time the system would not have enough power to do it, but it should also trip the internal circuit breaker. Therefore, either your voltage tests are erroneous or there is a malfunction in the board. As mentioned, removing the battery and unplugging the timer from the outlet for about 15 minutes may reset it.

Similar Threads

  1. not enough pressure in all zones
    By buikemakathy@yahoo.com in forum Irrigation / Sprinkler Forum
    Replies: 2
    Last Post: 05-10-2011, 10:45 AM
  2. 1 of 4 zones will not work
    By griffen in forum Irrigation / Sprinkler Forum
    Replies: 1
    Last Post: 06-09-2009, 07:31 AM
  3. Bleeding zones in hot water system
    By construct30 in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 12-25-2007, 09:12 PM
  4. water pressure drops when changing zones and wont come back up to normal
    By laborer90 in forum Irrigation / Sprinkler Forum
    Replies: 5
    Last Post: 07-01-2007, 06:19 PM
  5. I have 3 zones that are not working...
    By mayhem5220 in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 09-09-2006, 07:17 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •