    Default Water Supply Connection for House and Irrigation

    I'm installing an irrigation system and I need to replace the tee that goes into my house to use one side for my sprinklers (instead of an existing hose bib). The existing installation is 3/4" copper pipe (from the meter) to a compression fitting, then the main shutoff 1", then a galvanized union 1", then the tee into the house and hose bib. When I replace the tee, must I use galvanized again? I would prefer pvc with threaded connections, but this is above ground. If I wrap it in pipe insulation and electrical tape, will it be to code? This is PVC after the main house shutoff just outside the structure.

  2. #2
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    6,835

    Default

    You make no mention of a backflow preventer. Anytime you have a cross connection, domestic and irrigation, you must have a functioning device to prevent your domestic side from contamination. Do you really thing electrical tape is part of any plumbing code? Given your apparent complete lack of knowledge on the subject, I would suggest you get a professional lawn service to install a safe and legal connection. Hospital bills cost more than plumbers.

  3. #3
    DIY Junior Member jasontf's Avatar
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    4

    Default

    My full connection would work like this:
    3/4" copper pipe to compression fitting, then SCH 80 PVC union, then SCH 80 PVC tee to house and irrigation. On the irrigation side, then a brass strainer, PVC connection to a pressure vacuum breaker, then 1" SCH 40 PVC to irrigation valves.
    I mention the pipe insulation and electrical tape because this is what the city used to install an irrigation system near my neighborhood. Texas is hot and they have SCH 40 PVC coming up from a ground connection, then into a pressure vacuum breaker, then SCH 40 PVC back into the ground. The PVC is covered by pipe insulation and secured with electrical tape. Is this to code? Is is also acceptable for the tee into my house supply?

Similar Threads

  1. PVC repair irrigation water supply line from the street
    By themp in forum Plumbing Forum Discussion & Blog
    Replies: 4
    Last Post: 04-28-2011, 05:58 PM
  2. suspect birm filter medium getting into house water supply.
    By byo in forum Plumbing Forum Discussion & Blog
    Replies: 3
    Last Post: 01-25-2011, 09:39 PM
  3. Dishwasher supply line connection/water inlet valve
    By GregN31 in forum Plumbing Forum Discussion & Blog
    Replies: 6
    Last Post: 01-14-2011, 08:21 AM
  4. Water main, irrigation, then whole house
    By jbr383 in forum Plumbing Forum Discussion & Blog
    Replies: 3
    Last Post: 05-15-2008, 07:50 AM
  5. Cistern to supply Irrigation
    By Decanthas in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 05-13-2008, 09:32 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •